1UPSMON.CONF(5)              Network UPS Tools (NUT)             UPSMON.CONF(5)
2
3
4

NAME

6       upsmon.conf - Configuration for Network UPS Tools upsmon
7
8

DESCRIPTION

10       This  file's  primary  job is to define the systems that upsmon(8) will
11       monitor and to tell it how to shut down the system when necessary.   It
12       will  contain  passwords,  so  keep it secure.  Ideally,only the upsmon
13       process should be able to read it.
14
15       Additionally, other optional configuration values can be  set  in  this
16       file.
17
18

CONFIGURATION DIRECTIVES

20       DEADTIME seconds
21
22              upsmon  allows  a UPS to go missing for this many seconds before
23              declaring it "dead".  The default is 15 seconds.
24
25              upsmon requires a UPS to provide status  information  every  few
26              seconds (see POLLFREQ and POLLFREQALERT) to keep things updated.
27              If the status fetch fails, the UPS is marked stale.  If it stays
28              stale for more than DEADTIME seconds, the UPS is marked dead.
29
30              A  dead  UPS  that was last known to be on battery is assumed to
31              have changed to a low battery condition.  This may force a shut‐
32              down  if it is providing a critical amount of power to your sys‐
33              tem.  This seems disruptive, but the  alternative  is  barreling
34              ahead into oblivion and crashing when you run out of power.
35
36              Note:  DEADTIME  should  be  a multiple of POLLFREQ and POLLFRE‐
37              QALERT.  Otherwise,  you'll have  "dead"  UPSes  simply  because
38              upsmon  isn't  polling them quickly enough.  Rule of thumb: take
39              the larger of the two POLLFREQ values, and multiply by 3.
40
41
42       FINALDELAY seconds
43
44              When running in master mode, upsmon waits this long after  send‐
45              ing  the  NOTIFY_SHUTDOWN  to  warn  the users.  After the timer
46              elapses, it then runs your SHUTDOWNCMD.  By default this is  set
47              to 5 seconds.
48
49              If  you  need  to  let  your users do something in between those
50              events, increase this number.  Remember, at this point your  UPS
51              battery is almost depleted, so don't make this too big.
52
53              Alternatively,  you  can  set  this  very  low so you don't wait
54              around when it's time to shut down.  Some UPSes don't give  much
55              warning for low battery and will require a value of 0 here for a
56              safe shutdown.
57
58              Note: If FINALDELAY on the slave is greater than HOSTSYNC on the
59              master, the master will give up waiting for the slave to discon‐
60              nect.
61
62
63       HOSTSYNC seconds
64
65              upsmon will wait up to this many seconds in master mode for  the
66              slaves  to  disconnect during a shutdown situation.  By default,
67              this is 15 seconds.
68
69              When a UPS goes critical (on battery + low battery, or  "FSD"  ‐
70              forced shutdown), the slaves are supposed to disconnect and shut
71              down right away.  The HOSTSYNC timer  keeps  the  master  upsmon
72              from sitting there forever if one of the slaves gets stuck.
73
74              This value is also used to keep slave systems from getting stuck
75              if the master fails to respond in time.   After  a  UPS  becomes
76              critical,  the  slave  will  wait up to HOSTSYNC seconds for the
77              master to set the FSD flag.  If that timer  expires,  the  slave
78              will assume that the master is broken and will shut down anyway.
79
80              This  keeps  the  slaves from shutting down during a short‐lived
81              status change to "OB LB" that the  slaves  see  but  the  master
82              misses.
83
84
85       MINSUPPLIES num
86
87              Set the number of power supplies that must be receiving power to
88              keep this system running.  Normal computers have just one  power
89              supply, so the default value of 1 is acceptable.
90
91              Large/expensive  server  type systems usually have more, and can
92              run with a few missing.  The HP NetServer LH4 can run with 2 out
93              of  4,  for  example, so you'd set it to 2.  The idea is to keep
94              the box running as long as possible, right?
95
96              Obviously you have to put the redundant  supplies  on  different
97              UPS circuits for this to make sense!  See big‐servers.txt in the
98              docs subdirectory for more information and ideas on how  to  use
99              this feature.
100
101              Also see the section on "power values" in upsmon(8).
102
103
104       MONITOR system powervalue username password type
105
106              Each UPS that you need to be monitor should have a MONITOR line.
107              Not all of these need supply power to the system that is running
108              upsmon.  You may monitor other systems if you want to be able to
109              send notifications about status changes on them.
110
111              You must have at least one MONITOR directive in this file.
112
113              system is a UPS identifier.  It is in this form:
114
115                   <upsname>@<hostname>[:<port>]
116
117              Some examples:
118
119               ‐ "su700@mybox" means a UPS called "su700" on a  system  called
120              "mybox".  This is the normal form.
121
122               ‐  "fenton@bigbox:5678"  is  a  UPS called "fenton" on a system
123              called "bigbox" which runs upsd(8) on port "5678".
124
125              powervalue is an integer representing the number of  power  sup‐
126              plies  that the UPS feeds on this system.  Most normal computers
127              have one power supply, and the UPS feeds it, so this value  will
128              be  1.  You need a very large or special system to have anything
129              higher here.
130
131              You can set the powervalue to 0 if you want  to  monitor  a  UPS
132              that doesn't actually supply power to this system.  This is use‐
133              ful when you want to have upsmon do notifications  about  status
134              changes on a UPS without shutting down when it goes critical.
135
136              The  username  and  password on this line must match an entry in
137              that system's upsd.users(5).  If your  username  is  "monmaster"
138              and  your  password  is "blah", the MONITOR line might look like
139              this:
140
141              MONITOR myups@bigserver 1 monmaster blah master
142
143              Meanwhile, the upsd.users on 'bigserver' would look like this:
144
145                   [monmaster]
146
147                        password  = blah
148
149                        allowfrom = (ACLs from upsd.conf(5))
150
151                        upsmon master   (or slave)
152
153              The type refers to the relationship with  upsd(8).   It  can  be
154              either  "master" or "slave".  See upsmon(8) for more information
155              on the meaning of these modes.  The mode you pick here also goes
156              in the upsd.users file, as seen in the example above.
157
158
159       NOCOMMWARNTIME seconds
160
161              upsmon  will  trigger a NOTIFY_NOCOMM after this many seconds if
162              it can't reach any of the  UPS  entries  in  this  configuration
163              file.   It  keeps  warning you until the situation is fixed.  By
164              default this is 300 seconds.
165
166
167       NOTIFYCMD command
168
169              upsmon calls this to send messages when things happen.
170
171              This command is called with the full text of the message as  one
172              argument.   The  environment  string NOTIFYTYPE will contain the
173              type string of whatever caused this event to happen.
174
175              If you need to use upssched(8), then you must make it your NOTI‐
176              FYCMD by listing it here.
177
178              Note  that  this is only called for NOTIFY events that have EXEC
179              set with NOTIFYFLAG.  See NOTIFYFLAG below for more details.
180
181              Making this some sort of shell script might not be a  bad  idea.
182              For more information and ideas, see pager.txt in the docs direc‐
183              tory.
184
185              Remember, this also needs to be one element in the configuration
186              file, so if your command has spaces, then wrap it in quotes.
187
188                   NOTIFYCMD "/path/to/script --foo --bar"
189
190              This  script  is  run  in the background ‐ that is, upsmon forks
191              before it calls out to start it.  This means that your NOTIFYCMD
192              may  have  multiple instances running simultaneously if a lot of
193              stuff happens all at once.  Keep this  in  mind  when  designing
194              complicated notifiers.
195
196
197       NOTIFYMSG type message
198
199              upsmon  comes  with  a set of stock messages for various events.
200              You can change them if you like.
201
202                   NOTIFYMSG ONLINE "UPS %s is getting line power"
203
204                   NOTIFYMSG ONBATT "Someone pulled the plug on %s"
205
206              Note that %s is replaced with the identifier of the UPS in ques‐
207              tion.
208
209              Possible values for type:
210
211                   ONLINE ‐ UPS is back online
212
213                   ONBATT ‐ UPS is on battery
214
215                   LOWBATT ‐ UPS is on battery and has a low battery (is crit‐
216              ical)
217
218                   FSD ‐ UPS is being shutdown by the master  (FSD  =  "Forced
219              Shutdown")
220
221                   COMMOK ‐ Communications established with the UPS
222
223                   COMMBAD ‐ Communications lost to the UPS
224
225                   SHUTDOWN ‐ The system is being shutdown
226
227                   REPLBATT ‐ The UPS battery is bad and needs to be replaced
228
229                   NOCOMM ‐ A UPS is unavailable (can't be contacted for moni‐
230              toring)
231
232              The message must be one element in the configuration file, so if
233              it contains spaces, you must wrap it in quotes.
234
235                   NOTIFYMSG NOCOMM "Someone stole UPS %s"
236
237
238       NOTIFYFLAG type flag[+flag][+flag]...
239
240              By  default, upsmon sends walls global messages to all logged in
241              users) via /bin/wall and writes to the syslog when  things  hap‐
242              pen.  You can change this.
243
244              Examples:
245
246                   NOTIFYFLAG ONLINE SYSLOG
247
248                   NOTIFYFLAG ONBATT SYSLOG+WALL+EXEC
249
250              Possible values for the flags:
251
252                   SYSLOG ‐ Write the message to the syslog
253
254                   WALL ‐ Write the message to all users with /bin/wall
255
256                   EXEC ‐ Execute NOTIFYCMD (see above) with the message
257
258                   IGNORE ‐ Don't do anything
259
260              If you use IGNORE, don't use any other flags on the same line.
261
262
263       POLLFREQ seconds
264
265              Normally  upsmon  polls  the upsd(8) server every 5 seconds.  If
266              this is flooding your network with activity,  you  can  make  it
267              higher.   You  can  also  make it lower to get faster updates in
268              some cases.
269
270              There are some catches.  First, if  you  set  the  POLLFREQ  too
271              high,  you may miss short‐lived power events entirely.  You also
272              risk triggering the DEADTIME (see above) if you use a very large
273              number.
274
275              Second,  there  is  a point of diminishing returns if you set it
276              too low.  While upsd normally has all of the data  available  to
277              it  instantly,  most  drivers  only  refresh the UPS status once
278              every 2 seconds.  Polling any more than that usually doesn't get
279              you the information any faster.
280
281
282       POLLFREQALERT seconds
283
284              This  is  the interval that upsmon waits between polls if any of
285              its UPSes are on battery.  You can use this along with  POLLFREQ
286              above to slow down polls during normal behavior, but get quicker
287              updates when something bad happens.
288
289              This should always be equal to or lower than the POLLFREQ value.
290              By default it is also set 5 seconds.
291
292              The  warnings from the POLLFREQ entry about too‐high and too‐low
293              values also apply here.
294
295
296       POWERDOWNFLAG filename
297
298              upsmon creates this file when running in master  mode  when  the
299              UPS  needs to be powered off.  You should check for this file in
300              your shutdown scripts and call upsdrvctl shutdown if it exists.
301
302              This is done to forcibly reset the slaves,  so  they  don't  get
303              stuck at the "halted" stage even if the power returns during the
304              shutdown process.  This usually does not work well  on  contact‐
305              closure UPSes that use the genericups driver.
306
307              See  the  shutdown.txt  file  in  the docs subdirectory for more
308              information.
309
310
311       RBWARNTIME seconds
312
313              When a UPS says that it needs  to  have  its  battery  replaced,
314              upsmon  will  generate a NOTIFY_REPLBATT event.  By default this
315              happens every 43200 seconds ‐ 12 hours.
316
317              If you need another value, set it here.
318
319
320       RUN_AS_USER username
321
322              upsmon normally runs the bulk of  the  monitoring  duties  under
323              another user ID after dropping root privileges.  On most systems
324              this means it runs as "nobody", since that's  the  default  from
325              compile‐time.
326
327              The catch is that "nobody" can't read your upsmon.conf, since by
328              default it is installed so that only root  can  open  it.   This
329              means  you won't be able to reload the configuration file, since
330              it will be unavailable.
331
332              The solution is to create a new user just for upsmon, then  make
333              it  run  as that user.  I suggest "nutmon", but you can use any‐
334              thing that isn't already taken on your system.   Just  create  a
335              regular  user with no special privileges and an impossible pass‐
336              word.
337
338              Then, tell upsmon to run as  that  user,  and  make  upsmon.conf
339              readable  by  it.   Your reloads will work, and your config file
340              will stay secure.
341
342              This file should not be writable by the upsmon user, as it would
343              be  possible  to exploit a hole, change the SHUTDOWNCMD to some‐
344              thing malicious, then wait for upsmon to be restarted.
345
346
347       SHUTDOWNCMD command
348
349              upsmon runs this command when the system  needs  to  be  brought
350              down.   If  it  is a slave, it will do that immediately whenever
351              the current overall power  value  drops  below  the  MINSUPPLIES
352              value above.
353
354              When  upsmon  is  a  master, it will allow any slaves to log out
355              before starting the local shutdown procedure.
356
357              Note that the command needs to be  one  element  in  the  config
358              file.   If your shutdown command includes spaces, then put it in
359              quotes to keep it together, i.e.:
360
361                   SHUTDOWNCMD "/sbin/shutdown -h +0"
362
363

SEE ALSO

365       upsmon(8), upsd(8), nutupsdrv(8).
366
367