1BLAZER(8)                         NUT Manual                         BLAZER(8)
2
3
4

NAME

6       blazer - Driver for Megatec/Q1 protocol serial (blazer_ser) and USB
7       (blazer_usb) based UPS equipment
8

NOTE

10       This man page only documents the hardware-specific features of the
11       blazer driver. For information about the core driver, see nutupsdrv(8).
12

SUPPORTED HARDWARE

14       The blazer driver is known to work with various UPSes from Blazer,
15       Energy Sistem, Fenton Technologies, Mustek and many others. The NUT
16       compatibility table lists all the known supported models. Keep in mind,
17       however, that other models not listed there may also be supported, but
18       haven’t been tested.
19
20       All devices with a serial interface (use the blazer_ser driver) and
21       many with a USB interface (use the blazer_usb driver) are supported.
22

EXTRA ARGUMENTS

24       You may need to override or provide defaults for some values, depending
25       on the make and model of your UPS. The following are the ones that most
26       likely will need changing (see ups.conf(5)):
27
28       default.battery.voltage.high = value
29           Maximum battery voltage that is reached after about 12 to 24 hours
30           charging. If you want the driver to report a guesstimated
31           battery.charge, you need to specify this (see BATTERY CHARGE).
32
33       default.battery.voltage.low = value
34           Minimum battery voltage just before the UPS automatically shuts
35           down. If you want the driver to report a guesstimated
36           battery.charge, you need to specify this (see BATTERY CHARGE).
37
38       default.battery.voltage.nominal = value,
39       override.battery.voltage.nominal = value
40           Some devices show a wrong nominal battery voltage (or none at all),
41           so you may need to override or set a default value.
42
43       override.battery.packs = value
44           Some devices report a part of the total battery voltage. For
45           instance, if battery.voltage.nominal is 24 V, but it reports a
46           battery.voltage of around 2 V, the number of battery.packs to
47           correct this reading would be 12. The driver will attempt to detect
48           this automatically, but if this fails somehow, you may want to
49           override this value.
50
51       ondelay = value
52           Time to wait before switching on the UPS (minutes). Note that a
53           value below 3 minutes, may cause earlier firmware versions to not
54           switch on automatically, so it defaults to 3 minutes.
55
56       offdelay = value
57           Time to wait before shutting down the UPS (seconds). This value is
58           truncated to units of 6 seconds (less than 60 seconds) or 60
59           seconds (more than 60 seconds). Defaults to 30 seconds.
60
61       norating
62           Some UPSes will lock up if you attempt to read rating information
63           from them. Setting this flag will make the driver skip this step.
64
65       novendor
66           Some UPSes will lock up if you attempt to read vendor information
67           from them. Setting this flag will make the driver skip this step.
68
69       protocol = string
70           Skip autodetection of the protocol to use and only use the one
71           specified. Supported values megatec, megatec/old, mustek and zinto.
72
73       runtimecal = value,value,value,value
74           Parameter used in the (optional) runtime estimation. This takes two
75           runtimes at different loads. Typically, this uses the runtime at
76           full load and the runtime at half load. For instance, if your UPS
77           has a rated runtime of 240 seconds at full load and 720 seconds at
78           half load, you would enter
79
80               runtimecal = 270,100,720,50
81
82           The first load should always be higher than the second. If you have
83           values available for loads other than 100 and 50 % respectively,
84           you can use those too, but keep them spaced apart as far as
85           reasonably possible. Just don’t get too close to no load
86           (prediction of runtime depends more on idle load for the battery
87           then).
88
89       chargetime = value
90           The time needed to fully recharge the battery after being fully
91           discharged. If not specified, the driver defaults to 43200 seconds
92           (12 hours). Only used if runtimecal is also specified.
93
94       idleload = value
95           Minimum battery load used by the driver to estimate the runtime. If
96           not specified, the driver defaults to 10%. Only used if runtimecal
97           is also specified.
98

SERIAL INTERFACE ONLY

100       cablepower = string
101           By default the driver will set DTR and clear RTS (normal). If you
102           find that your UPS isn’t detected or the communication with the UPS
103           is unreliable, you may try if clear DTR and set RTS (reverse), set
104           DTR and RTS (both) or clear DTR and RTS (none) improves this
105           situation.
106

USB INTERFACE ONLY

108       vendorid = regex, productid = regex, vendor = regex, product = regex,
109       serial = regex
110           Select a specific UPS, in case there is more than one connected via
111           USB. Each option specifies an extended regular expression (see
112           regex(7)) that must match the UPS’s entire vendor/product/serial
113           string (minus any surrounding whitespace), or the whole 4-digit
114           hexadecimal code for vendorid and productid. Try -DD for finding
115           out the strings to match.
116
117       Examples:
118
119           -x vendor="Foo.Corporation.*"
120
121           -x vendorid=051d    # (APC)
122
123           -x product=".*(Smart|Back)-?UPS.*"
124
125       bus = regex
126           Select a UPS on a specific USB bus or group of busses. The argument
127           is a regular expression that must match the bus name where the UPS
128           is connected (e.g. bus="002", bus="00[2-3]").
129
130       subdriver = string
131           Select a serial-over-USB subdriver to use. You have a choice
132           between phoenix, ippon, cypress, and krauler. When using this
133           option, it is mandatory to also specify the vendorid and productid.
134

UPS COMMANDS

136       This driver supports some instant commands (see upscmd(8)):
137
138       beeper.toggle
139           Toggle the UPS beeper. (Not available on some hardware.)
140
141       load.on
142           Turn on the load immediately.
143
144       load.off
145           Turn off the load immediately (see KNOWN PROBLEMS).
146
147       shutdown.return [value]
148           Turn off the load and return when power is back. Uses the timers
149           defined by ondelay and offdelay.
150
151       shutdown.stayoff [value]
152           Turn off the load and remain off (see KNOWN PROBLEMS). Uses the
153           timer defined by offdelay.
154
155       shutdown.stop
156           Stop a shutdown in progress.
157
158       test.battery.start.deep
159           Perform a long battery test (Not available on some hardware.)
160
161       test.battery.start.quick
162           Perform a (10 second) battery test.
163
164       test.battery.start value
165           Perform a battery test for the duration of value seconds (truncated
166           to units of 60 seconds).
167
168       test.battery.stop
169           Stop a running battery test (not available on some hardware.)
170

BATTERY CHARGE

172       Due to popular demand, this driver will report a guesstimated
173       battery.charge and optionally battery.runtime, provided you specified a
174       couple of the EXTRA ARGUMENTS listed above.
175
176       If you specify both battery.voltage.high and battery.voltage.low in
177       ups.conf(5), but don’t enter runtimecal, it will guesstimate the state
178       of charge by looking at the battery voltage alone. This is not reliable
179       under load, as this only gives reasonably accurate readings if you
180       disconnect the load, let the battery rest for a couple of minutes and
181       then measure the open cell voltage. This just isn’t practical if the
182       power went out and the UPS is providing power for your systems.
183
184                                battery.voltage - battery.voltage.low
185           battery.charge =  ------------------------------------------ x 100 %
186                             battery.voltage.high - battery.voltage.low
187
188       There is a way to get better readings without disconnecting the load
189       but this requires to keep track on how much (and how fast) current is
190       going in- and out of the battery. If you specified the runtimecal, the
191       driver will attempt to do this. Note however, that this heavily relies
192       on the values you enter and that the UPS must be able to report the
193       load as well. There are quite a couple of devices that report 0 % (or
194       any other fixed value) at all times, in which case this obviously
195       doesn’t work.
196
197       The driver also has no way of determining the degradation of the
198       battery capacity over time, so you’ll have to deal with this yourself
199       (by adjusting the values in runtimecal). Also note that the driver
200       guesses the initial state of charge based on the battery voltage, so
201       this may be less than 100 %, even when you are certain that they are
202       full. There is just no way to reliably measure this between 0 and 100 %
203       full charge.
204
205       This is better than nothing (but not by much). If any of the above
206       calculations is giving you incorrect readings, you are the one that put
207       in the values in ups.conf(5), so don’t complain with the author. If you
208       need something better, buy a UPS that reports battery.charge and
209       battery.runtime all by itself without the help of a NUT driver.
210

NOTES FOR THE PREVIOUS USER OF MEGATEC DRIVERS

212       The blazer drivers having replaced the megatec ones, some configuration
213       changes may be required by users switching to blazer.
214
215       Part of this, the following megatec options, in ups.conf, have to be
216       changed:
217
218       battvolts
219           You need to use default.battery.voltage.high and
220           default.battery.voltage.low
221
222       dtr and rts
223           You need to use cablepower
224
225       ignoreoff
226           This parameter can simply be discarded, since it was a wrong
227           understanding of the specification.
228

KNOWN PROBLEMS

230       Some UPS commands aren’t supported by all models. In most cases, the
231       driver will send a message to the system log when the user tries to
232       execute an unsupported command. Unfortunately, some models don’t even
233       provide a way for the driver to check for this, so the unsupported
234       commands will silently fail.
235
236       Both the load.off and shutdown.stayoff instant commands are meant to
237       turn the load off indefinitely. However, some UPS models don’t allow
238       this.
239
240       Some models report a bogus value for the beeper status (will always be
241       enabled or disabled). So, the beeper.toggle command may appear to have
242       no effect in the status reported by the driver when, in fact, it is
243       working fine.
244
245       The temperature and load value is known to be bogus in some models.
246

AUTHORS

248       Arjen de Korte <adkorte-guest at alioth.debian.org>, Alexander Gordeev
249       <lasaine at lvk.cs.msu.su>
250

SEE ALSO

252       nutupsdrv(8), upsc(8), upscmd(8), upsrw(8)
253
254   Internet Resources:
255       The NUT (Network UPS Tools) home page: http://www.networkupstools.org/