1BLAZER_USB(8) NUT Manual BLAZER_USB(8)
2
3
4
6 blazer_usb - Driver for Megatec/Q1 protocol USB based UPS equipment
7
9 This man page only documents the hardware-specific features of the
10 blazer driver. For information about the core driver, see nutupsdrv(8).
11
13 The blazer driver is known to work with various UPSes from Blazer,
14 Energy Sistem, Fenton Technologies, General Electric, Mustek and many
15 others. The NUT compatibility table lists all the known supported
16 models. Keep in mind, however, that other models not listed there may
17 also be supported, but haven’t been tested.
18
19 All devices with a serial interface (use the blazer_ser driver) and
20 many with a USB interface (use the blazer_usb driver) are supported.
21
23 You may need to override or provide defaults for some values, depending
24 on the make and model of your UPS. The following are the ones that most
25 likely will need changing (see ups.conf(5)):
26
27 default.battery.voltage.high = value
28 Maximum battery voltage that is reached after about 12 to 24 hours
29 charging. If you want the driver to report a guesstimated
30 battery.charge, you need to specify this (see BATTERY CHARGE).
31
32 default.battery.voltage.low = value
33 Minimum battery voltage just before the UPS automatically shuts
34 down. If you want the driver to report a guesstimated
35 battery.charge, you need to specify this (see BATTERY CHARGE).
36
37 default.battery.voltage.nominal = value,
38 override.battery.voltage.nominal = value
39 Some devices show a wrong nominal battery voltage (or none at all),
40 so you may need to override or set a default value.
41
42 override.battery.packs = value
43 Some devices report a part of the total battery voltage. For
44 instance, if battery.voltage.nominal is 24 V, but it reports a
45 battery.voltage of around 2 V, the number of battery.packs to
46 correct this reading would be 12. The driver will attempt to detect
47 this automatically, but if this fails somehow, you may want to
48 override this value.
49
50 ondelay = value
51 Time to wait before switching on the UPS (minutes). Note that a
52 value below 3 minutes, may cause earlier firmware versions to not
53 switch on automatically, so it defaults to 3 minutes. The
54 acceptable range is 0..9999 minutes.
55
56 offdelay = value
57 Time to wait before shutting down the UPS (seconds). This value is
58 truncated to units of 6 seconds (less than 60 seconds) or 60
59 seconds (more than 60 seconds). Defaults to 30 seconds. The
60 acceptable range is 12..600 seconds.
61
62 norating
63 Some UPSes will lock up if you attempt to read rating information
64 from them. Setting this flag will make the driver skip this step.
65
66 novendor
67 Some UPSes will lock up if you attempt to read vendor information
68 from them. Setting this flag will make the driver skip this step.
69
70 protocol = string
71 Skip autodetection of the protocol to use and only use the one
72 specified. Supported values megatec, megatec/old, mustek and zinto.
73
74 runtimecal = value,value,value,value
75 Parameter used in the (optional) runtime estimation. This takes two
76 runtimes at different loads. Typically, this uses the runtime at
77 full load and the runtime at half load. For instance, if your UPS
78 has a rated runtime of 240 seconds at full load and 720 seconds at
79 half load, you would enter
80
81 runtimecal = 240,100,720,50
82
83 The first load should always be higher than the second. If you have
84 values available for loads other than 100 and 50 % respectively,
85 you can use those too, but keep them spaced apart as far as
86 reasonably possible. Just don’t get too close to no load
87 (prediction of runtime depends more on idle load for the battery
88 then).
89
90 chargetime = value
91 The time needed to fully recharge the battery after being fully
92 discharged. If not specified, the driver defaults to 43200 seconds
93 (12 hours). Only used if runtimecal is also specified.
94
95 idleload = value
96 Minimum battery load used by the driver to estimate the runtime. If
97 not specified, the driver defaults to 10%. Only used if runtimecal
98 is also specified.
99
100 USB INTERFACE ONLY
101 vendorid = regex, productid = regex, vendor = regex, product = regex,
102 serial = regex
103 Select a specific UPS, in case there is more than one connected via
104 USB. Each option specifies an extended regular expression (see
105 regex(7)) that must match the UPS’s entire vendor/product/serial
106 string (minus any surrounding whitespace), or the whole 4-digit
107 hexadecimal code for vendorid and productid. Try -DD for finding
108 out the strings to match.
109
110 Examples:
111
112 · -x vendor="Foo.Corporation.*"
113
114 · -x vendorid=051d* (APC)
115
116 · -x product=".*(Smart|Back)-?UPS.*"
117
118 bus = regex
119 Select a UPS on a specific USB bus or group of busses. The argument
120 is a regular expression that must match the bus name where the UPS
121 is connected (e.g. bus="002", bus="00[2-3]").
122
123 subdriver = string
124 Select a serial-over-USB subdriver to use. You have a choice
125 between phoenix, ippon, cypress, and krauler. When using this
126 option, it is mandatory to also specify the vendorid and productid.
127
128 langid_fix = value
129 Apply the language ID workaround to the krauler subdriver. This is
130 mandatory for some devices to work (LDLC, Dynamix and others). You
131 must to provide value (0x409 or 0x4095), according to your device
132 entry in NUT hardware compatibility list (HCL).
133
135 This driver supports some instant commands (see upscmd(8)):
136
137 beeper.toggle
138 Toggle the UPS beeper. (Not available on some hardware.)
139
140 load.on
141 Turn on the load immediately.
142
143 load.off
144 Turn off the load immediately (see KNOWN PROBLEMS).
145
146 shutdown.return
147 Turn off the load and return when power is back. Uses the timers
148 defined by ondelay and offdelay.
149
150 shutdown.stayoff
151 Turn off the load and remain off (see KNOWN PROBLEMS). Uses the
152 timer defined by offdelay.
153
154 shutdown.stop
155 Stop a shutdown in progress.
156
157 test.battery.start.deep
158 Perform a long battery test (Not available on some hardware.)
159
160 test.battery.start.quick
161 Perform a (10 second) battery test.
162
163 test.battery.start value
164 Perform a battery test for the duration of value minutes.
165
166 test.battery.stop
167 Stop a running battery test (not available on some hardware.)
168
170 Due to popular demand, this driver will report a guesstimated
171 battery.charge and optionally battery.runtime, provided you specified a
172 couple of the EXTRA ARGUMENTS listed above.
173
174 If you specify both battery.voltage.high and battery.voltage.low in
175 ups.conf(5), but don’t enter runtimecal, it will guesstimate the state
176 of charge by looking at the battery voltage alone. This is not reliable
177 under load, as this only gives reasonably accurate readings if you
178 disconnect the load, let the battery rest for a couple of minutes and
179 then measure the open cell voltage. This just isn’t practical if the
180 power went out and the UPS is providing power for your systems.
181
182 battery.voltage - battery.voltage.low
183 battery.charge = ------------------------------------------ x 100 %
184 battery.voltage.high - battery.voltage.low
185
186 There is a way to get better readings without disconnecting the load
187 but this requires one to keep track on how much (and how fast) current
188 is going in- and out of the battery. If you specified the runtimecal,
189 the driver will attempt to do this. Note however, that this heavily
190 relies on the values you enter and that the UPS must be able to report
191 the load as well. There are quite a couple of devices that report 0 %
192 (or any other fixed value) at all times, in which case this obviously
193 doesn’t work.
194
195 The driver also has no way of determining the degradation of the
196 battery capacity over time, so you’ll have to deal with this yourself
197 (by adjusting the values in runtimecal). Also note that the driver
198 guesses the initial state of charge based on the battery voltage, so
199 this may be less than 100 %, even when you are certain that they are
200 full. There is just no way to reliably measure this between 0 and 100 %
201 full charge.
202
203 This is better than nothing (but not by much). If any of the above
204 calculations is giving you incorrect readings, you are the one that put
205 in the values in ups.conf(5), so don’t complain with the author. If you
206 need something better, buy a UPS that reports battery.charge and
207 battery.runtime all by itself without the help of a NUT driver.
208
210 The blazer drivers having replaced the megatec ones, some configuration
211 changes may be required by users switching to blazer.
212
213 Part of this, the following megatec options, in ups.conf, have to be
214 changed:
215
216 battvolts
217 You need to use default.battery.voltage.high and
218 default.battery.voltage.low
219
220 dtr and rts
221 You need to use cablepower
222
223 ignoreoff
224 This parameter can simply be discarded, since it was a wrong
225 understanding of the specification.
226
228 Some UPS commands aren’t supported by all models. In most cases, the
229 driver will send a message to the system log when the user tries to
230 execute an unsupported command. Unfortunately, some models don’t even
231 provide a way for the driver to check for this, so the unsupported
232 commands will silently fail.
233
234 Both the load.off and shutdown.stayoff instant commands are meant to
235 turn the load off indefinitely. However, some UPS models don’t allow
236 this.
237
238 Some models report a bogus value for the beeper status (will always be
239 enabled or disabled). So, the beeper.toggle command may appear to have
240 no effect in the status reported by the driver when, in fact, it is
241 working fine.
242
243 The temperature and load value is known to be bogus in some models.
244
246 Arjen de Korte <adkorte-guest at alioth.debian.org>, Alexander Gordeev
247 <lasaine at lvk.cs.msu.su>
248
250 blazer_ser(8), nutupsdrv(8), upsc(8), upscmd(8), upsrw(8)
251
252 Internet Resources:
253 The NUT (Network UPS Tools) home page: http://www.networkupstools.org/
254
255 The NUT HCL: http://www.networkupstools.org/stable-hcl.html
256
257
258