1BLAZER_SER(8) NUT Manual BLAZER_SER(8)
2
3
4
6 blazer_ser - Driver for Megatec/Q1 protocol serial based UPS equipment
7
9 This man page only documents the hardware-specific features of the
10 blazer driver. For information about the core driver, see nutupsdrv(8).
11
13 The blazer driver is known to work with various UPSes from Blazer,
14 Energy Sistem, Fenton Technologies, General Electric, Mustek and many
15 others. The NUT compatibility table lists all the known supported
16 models. Keep in mind, however, that other models not listed there may
17 also be supported, but haven’t been tested.
18
19 All devices with a serial interface (use the blazer_ser driver) and
20 many with a USB interface (use the blazer_usb driver) are supported.
21
23 You may need to override or provide defaults for some values, depending
24 on the make and model of your UPS. The following are the ones that most
25 likely will need changing (see ups.conf(5)):
26
27 default.battery.voltage.high = value
28 Maximum battery voltage that is reached after about 12 to 24 hours
29 charging. If you want the driver to report a guesstimated
30 battery.charge, you need to specify this (see BATTERY CHARGE).
31
32 default.battery.voltage.low = value
33 Minimum battery voltage just before the UPS automatically shuts
34 down. If you want the driver to report a guesstimated
35 battery.charge, you need to specify this (see BATTERY CHARGE).
36
37 default.battery.voltage.nominal = value,
38 override.battery.voltage.nominal = value
39 Some devices show a wrong nominal battery voltage (or none at all),
40 so you may need to override or set a default value.
41
42 override.battery.packs = value
43 Some devices report a part of the total battery voltage. For
44 instance, if battery.voltage.nominal is 24 V, but it reports a
45 battery.voltage of around 2 V, the number of battery.packs to
46 correct this reading would be 12. The driver will attempt to detect
47 this automatically, but if this fails somehow, you may want to
48 override this value.
49
50 ondelay = value
51 Time to wait before switching on the UPS (minutes). Note that a
52 value below 3 minutes, may cause earlier firmware versions to not
53 switch on automatically, so it defaults to 3 minutes. The
54 acceptable range is 0..9999 minutes.
55
56 offdelay = value
57 Time to wait before shutting down the UPS (seconds). This value is
58 truncated to units of 6 seconds (less than 60 seconds) or 60
59 seconds (more than 60 seconds). Defaults to 30 seconds. The
60 acceptable range is 12..600 seconds.
61
62 norating
63 Some UPSes will lock up if you attempt to read rating information
64 from them. Setting this flag will make the driver skip this step.
65
66 novendor
67 Some UPSes will lock up if you attempt to read vendor information
68 from them. Setting this flag will make the driver skip this step.
69
70 protocol = string
71 Skip autodetection of the protocol to use and only use the one
72 specified. Supported values megatec, megatec/old, mustek and zinto.
73
74 runtimecal = value,value,value,value
75 Parameter used in the (optional) runtime estimation. This takes two
76 runtimes at different loads. Typically, this uses the runtime at
77 full load and the runtime at half load. For instance, if your UPS
78 has a rated runtime of 240 seconds at full load and 720 seconds at
79 half load, you would enter
80
81 runtimecal = 240,100,720,50
82
83 The first load should always be higher than the second. If you have
84 values available for loads other than 100 and 50 % respectively,
85 you can use those too, but keep them spaced apart as far as
86 reasonably possible. Just don’t get too close to no load
87 (prediction of runtime depends more on idle load for the battery
88 then).
89
90 chargetime = value
91 The time needed to fully recharge the battery after being fully
92 discharged. If not specified, the driver defaults to 43200 seconds
93 (12 hours). Only used if runtimecal is also specified.
94
95 idleload = value
96 Minimum battery load used by the driver to estimate the runtime. If
97 not specified, the driver defaults to 10%. Only used if runtimecal
98 is also specified.
99
100 SERIAL INTERFACE ONLY
101 cablepower = string
102 By default the driver will set DTR and clear RTS (normal). If you
103 find that your UPS isn’t detected or the communication with the UPS
104 is unreliable, you may try if clear DTR and set RTS (reverse), set
105 DTR and RTS (both) or clear DTR and RTS (none) improves this
106 situation.
107
109 This driver supports some instant commands (see upscmd(8)):
110
111 beeper.toggle
112 Toggle the UPS beeper. (Not available on some hardware.)
113
114 load.on
115 Turn on the load immediately.
116
117 load.off
118 Turn off the load immediately (see KNOWN PROBLEMS).
119
120 shutdown.return
121 Turn off the load and return when power is back. Uses the timers
122 defined by ondelay and offdelay.
123
124 shutdown.stayoff
125 Turn off the load and remain off (see KNOWN PROBLEMS). Uses the
126 timer defined by offdelay.
127
128 shutdown.stop
129 Stop a shutdown in progress.
130
131 test.battery.start.deep
132 Perform a long battery test (Not available on some hardware.)
133
134 test.battery.start.quick
135 Perform a (10 second) battery test.
136
137 test.battery.start value
138 Perform a battery test for the duration of value minutes.
139
140 test.battery.stop
141 Stop a running battery test (not available on some hardware.)
142
144 Due to popular demand, this driver will report a guesstimated
145 battery.charge and optionally battery.runtime, provided you specified a
146 couple of the EXTRA ARGUMENTS listed above.
147
148 If you specify both battery.voltage.high and battery.voltage.low in
149 ups.conf(5), but don’t enter runtimecal, it will guesstimate the state
150 of charge by looking at the battery voltage alone. This is not reliable
151 under load, as this only gives reasonably accurate readings if you
152 disconnect the load, let the battery rest for a couple of minutes and
153 then measure the open cell voltage. This just isn’t practical if the
154 power went out and the UPS is providing power for your systems.
155
156 battery.voltage - battery.voltage.low
157 battery.charge = ------------------------------------------ x 100 %
158 battery.voltage.high - battery.voltage.low
159
160 There is a way to get better readings without disconnecting the load
161 but this requires one to keep track on how much (and how fast) current
162 is going in- and out of the battery. If you specified the runtimecal,
163 the driver will attempt to do this. Note however, that this heavily
164 relies on the values you enter and that the UPS must be able to report
165 the load as well. There are quite a couple of devices that report 0 %
166 (or any other fixed value) at all times, in which case this obviously
167 doesn’t work.
168
169 The driver also has no way of determining the degradation of the
170 battery capacity over time, so you’ll have to deal with this yourself
171 (by adjusting the values in runtimecal). Also note that the driver
172 guesses the initial state of charge based on the battery voltage, so
173 this may be less than 100 %, even when you are certain that they are
174 full. There is just no way to reliably measure this between 0 and 100 %
175 full charge.
176
177 This is better than nothing (but not by much). If any of the above
178 calculations is giving you incorrect readings, you are the one that put
179 in the values in ups.conf(5), so don’t complain with the author. If you
180 need something better, buy a UPS that reports battery.charge and
181 battery.runtime all by itself without the help of a NUT driver.
182
184 The blazer drivers having replaced the megatec ones, some configuration
185 changes may be required by users switching to blazer.
186
187 Part of this, the following megatec options, in ups.conf, have to be
188 changed:
189
190 battvolts
191 You need to use default.battery.voltage.high and
192 default.battery.voltage.low
193
194 dtr and rts
195 You need to use cablepower
196
197 ignoreoff
198 This parameter can simply be discarded, since it was a wrong
199 understanding of the specification.
200
202 Some UPS commands aren’t supported by all models. In most cases, the
203 driver will send a message to the system log when the user tries to
204 execute an unsupported command. Unfortunately, some models don’t even
205 provide a way for the driver to check for this, so the unsupported
206 commands will silently fail.
207
208 Both the load.off and shutdown.stayoff instant commands are meant to
209 turn the load off indefinitely. However, some UPS models don’t allow
210 this.
211
212 Some models report a bogus value for the beeper status (will always be
213 enabled or disabled). So, the beeper.toggle command may appear to have
214 no effect in the status reported by the driver when, in fact, it is
215 working fine.
216
217 The temperature and load value is known to be bogus in some models.
218
220 Arjen de Korte <adkorte-guest at alioth.debian.org>, Alexander Gordeev
221 <lasaine at lvk.cs.msu.su>
222
224 blazer_usb(8), nutupsdrv(8), upsc(8), upscmd(8), upsrw(8)
225
226 Internet Resources:
227 The NUT (Network UPS Tools) home page: http://www.networkupstools.org/
228
229 The NUT HCL: http://www.networkupstools.org/stable-hcl.html
230
231
232
233Network UPS Tools 2.7.3. 12/29/2015 BLAZER_SER(8)