1IPMI-SENSORS(8) System Commands IPMI-SENSORS(8)
2
3
4
6 ipmi-sensors - display IPMI sensor information
7
9 ipmi-sensors [OPTION...]
10
12 Ipmi-sensors displays current readings of sensors and sensor data
13 repository (SDR) information. The default display outputs each sensor's
14 record id, sensor name, sensor type name, sensor reading (if appropri‐
15 ate), and the current sensor event. More verbose information can be
16 found using the verbose options specified below. Ipmi-sensors does not
17 inform the user if a problem exists with a particular sensor because
18 sensor readings and events are not analyzed by default. Users may wish
19 to use the --output-sensor-state option to output the analyzed sensor
20 state. Some sensors may have a sensor reading or sensor event of "N/A"
21 if the information is unavailable. This is typical of a sensor that is
22 not enabled or not owned by a BMC. Please see --bridge-sensors option
23 below to deal with sensors not owned by a BMC. Sensors may output a
24 sensor event of "Unknown" if the sensor reading cannot be read. This is
25 typical of a sensor that is busy or a reading that cannot be calcu‐
26 lated. If sensors report "Unrecognized State", it is indicative of an
27 unknown sensor type, typically an OEM sensor. If the sensor OEM inter‐
28 pretation is available, the --interpret-oem-data may be able to report
29 the appropriate sensor state. Sensors need not always report a sensor
30 event. When a sensor event is not present, "OK" is typically reported.
31
32 Listed below are general IPMI options, tool specific options, trouble
33 shooting information, workaround information, examples, and known
34 issues. For a general introduction to FreeIPMI please see freeipmi(7).
35 To perform IPMI sensor configuration, please see ipmi-config(8). To
36 perform some advanced SDR management, please see bmc-device(8).
37
39 The following options are general options for configuring IPMI communi‐
40 cation and executing general tool commands.
41
42 -D IPMIDRIVER, --driver-type=IPMIDRIVER
43 Specify the driver type to use instead of doing an auto selec‐
44 tion. The currently available outofband drivers are LAN and
45 LAN_2_0, which perform IPMI 1.5 and IPMI 2.0 respectively. The
46 currently available inband drivers are KCS, SSIF, OPENIPMI,
47 SUNBMC, and INTELDCMI.
48
49 --disable-auto-probe
50 Do not probe in-band IPMI devices for default settings.
51
52 --driver-address=DRIVER-ADDRESS
53 Specify the in-band driver address to be used instead of the
54 probed value. DRIVER-ADDRESS should be prefixed with "0x" for a
55 hex value and '0' for an octal value.
56
57 --driver-device=DEVICE
58 Specify the in-band driver device path to be used instead of the
59 probed path.
60
61 --register-spacing=REGISTER-SPACING
62 Specify the in-band driver register spacing instead of the
63 probed value. Argument is in bytes (i.e. 32bit register spacing
64 = 4)
65
66 --target-channel-number=CHANNEL-NUMBER
67 Specify the in-band driver target channel number to send IPMI
68 requests to.
69
70 --target-slave-address=SLAVE-ADDRESS
71 Specify the in-band driver target slave number to send IPMI
72 requests to.
73
74 -h IPMIHOST1,IPMIHOST2,..., --hostname=IPMIHOST1[:PORT],IPMI‐
75 HOST2[:PORT],...
76 Specify the remote host(s) to communicate with. Multiple host‐
77 names may be separated by comma or may be specified in a range
78 format; see HOSTRANGED SUPPORT below. An optional port can be
79 specified with each host, which may be useful in port forwarding
80 or similar situations. If specifying an IPv6 address and port,
81 use the format [ADDRESS]:PORT.
82
83 -u USERNAME, --username=USERNAME
84 Specify the username to use when authenticating with the remote
85 host. If not specified, a null (i.e. anonymous) username is
86 assumed. The user must have atleast OPERATOR privileges in order
87 for this tool to operate fully.
88
89 -p PASSWORD, --password=PASSWORD
90 Specify the password to use when authenticationg with the remote
91 host. If not specified, a null password is assumed. Maximum
92 password length is 16 for IPMI 1.5 and 20 for IPMI 2.0.
93
94 -P, --password-prompt
95 Prompt for password to avoid possibility of listing it in
96 process lists.
97
98 -k K_G, --k-g=K_G
99 Specify the K_g BMC key to use when authenticating with the
100 remote host for IPMI 2.0. If not specified, a null key is
101 assumed. To input the key in hexadecimal form, prefix the string
102 with '0x'. E.g., the key 'abc' can be entered with the either
103 the string 'abc' or the string '0x616263'
104
105 -K, --k-g-prompt
106 Prompt for k-g to avoid possibility of listing it in process
107 lists.
108
109 --session-timeout=MILLISECONDS
110 Specify the session timeout in milliseconds. Defaults to 20000
111 milliseconds (20 seconds) if not specified.
112
113 --retransmission-timeout=MILLISECONDS
114 Specify the packet retransmission timeout in milliseconds.
115 Defaults to 1000 milliseconds (1 second) if not specified. The
116 retransmission timeout cannot be larger than the session time‐
117 out.
118
119 -a AUTHENTICATION-TYPE, --authentication-type=AUTHENTICATION-TYPE
120 Specify the IPMI 1.5 authentication type to use. The currently
121 available authentication types are NONE, STRAIGHT_PASSWORD_KEY,
122 MD2, and MD5. Defaults to MD5 if not specified.
123
124 -I CIPHER-SUITE-ID, --cipher-suite-id=CIPHER-SUITE-ID
125 Specify the IPMI 2.0 cipher suite ID to use. The Cipher Suite ID
126 identifies a set of authentication, integrity, and confidential‐
127 ity algorithms to use for IPMI 2.0 communication. The authenti‐
128 cation algorithm identifies the algorithm to use for session
129 setup, the integrity algorithm identifies the algorithm to use
130 for session packet signatures, and the confidentiality algorithm
131 identifies the algorithm to use for payload encryption. Defaults
132 to cipher suite ID 3 if not specified. The following cipher
133 suite ids are currently supported:
134
135 0 - Authentication Algorithm = None; Integrity Algorithm = None;
136 Confidentiality Algorithm = None
137
138 1 - Authentication Algorithm = HMAC-SHA1; Integrity Algorithm =
139 None; Confidentiality Algorithm = None
140
141 2 - Authentication Algorithm = HMAC-SHA1; Integrity Algorithm =
142 HMAC-SHA1-96; Confidentiality Algorithm = None
143
144 3 - Authentication Algorithm = HMAC-SHA1; Integrity Algorithm =
145 HMAC-SHA1-96; Confidentiality Algorithm = AES-CBC-128
146
147 6 - Authentication Algorithm = HMAC-MD5; Integrity Algorithm =
148 None; Confidentiality Algorithm = None
149
150 7 - Authentication Algorithm = HMAC-MD5; Integrity Algorithm =
151 HMAC-MD5-128; Confidentiality Algorithm = None
152
153 8 - Authentication Algorithm = HMAC-MD5; Integrity Algorithm =
154 HMAC-MD5-128; Confidentiality Algorithm = AES-CBC-128
155
156 11 - Authentication Algorithm = HMAC-MD5; Integrity Algorithm =
157 MD5-128; Confidentiality Algorithm = None
158
159 12 - Authentication Algorithm = HMAC-MD5; Integrity Algorithm =
160 MD5-128; Confidentiality Algorithm = AES-CBC-128
161
162 15 - Authentication Algorithm = HMAC-SHA256; Integrity Algorithm
163 = None; Confidentiality Algorithm = None
164
165 16 - Authentication Algorithm = HMAC-SHA256; Integrity Algorithm
166 = HMAC_SHA256_128; Confidentiality Algorithm = None
167
168 17 - Authentication Algorithm = HMAC-SHA256; Integrity Algorithm
169 = HMAC_SHA256_128; Confidentiality Algorithm = AES-CBC-128
170
171 -l PRIVILEGE-LEVEL, --privilege-level=PRIVILEGE-LEVEL
172 Specify the privilege level to be used. The currently available
173 privilege levels are USER, OPERATOR, and ADMIN. Defaults to
174 OPERATOR if not specified.
175
176 --config-file=FILE
177 Specify an alternate configuration file.
178
179 -W WORKAROUNDS, --workaround-flags=WORKAROUNDS
180 Specify workarounds to vendor compliance issues. Multiple work‐
181 arounds can be specified separated by commas. A special command
182 line flag of "none", will indicate no workarounds (may be useful
183 for overriding configured defaults). See WORKAROUNDS below for a
184 list of available workarounds.
185
186 --debug
187 Turn on debugging.
188
189 -?, --help
190 Output a help list and exit.
191
192 --usage
193 Output a usage message and exit.
194
195 -V, --version
196 Output the program version and exit.
197
199 The following options are specific to ipmi-sensors.
200
201 -v, --verbose
202 Output verbose sensor output. This option will output additional
203 information about sensors such as thresholds, ranges, numbers,
204 and event/reading type codes.
205
206 -vv Output very verbose sensor output. This option will output more
207 additional information than the verbose option such as informa‐
208 tion about events, other sensor types, and oem sensors.
209
210 -i, --sdr-info
211 Show sensor data repository (SDR) information
212
213 -q, --quiet-readings
214 Do not output sensor reading values by default. This option is
215 particularly useful if you want to use hostranged output across
216 a cluster and want to consolidate the output.
217
218 -r RECORD-IDS-LIST, --record-ids=RECORD-IDS-LIST
219 Specify sensors to show by record id. Multiple record ids can be
220 separated by commas or spaces. If both --record-ids and --sen‐
221 sor-types are specified, --record-ids takes precedence. A spe‐
222 cial command line record id of "all", will indicate all record
223 ids should be shown (may be useful for overriding configured
224 defaults).
225
226 -R RECORD-IDS-LIST, --exclude-record-ids=RECORD-IDS-LIST
227 Specify sensors to not show by record id. Multiple record ids
228 can be separated by commas or spaces. A special command line
229 record id of "none", will indicate no record ids should be
230 excluded (may be useful for overriding configured defaults).
231
232 -t SENSOR-TYPE-LIST, --sensor-types=SENSOR-TYPE-LIST
233 Specify sensor types to show outputs for. Multiple types can be
234 separated by commas or spaces. If both --record-ids and --sen‐
235 sor-types are specified, --record-ids takes precedence. A spe‐
236 cial command line type of "all", will indicate all types should
237 be shown (may be useful for overriding configured defaults).
238 Users may specify sensor types by string (see --list-sen‐
239 sor-types below) or by number (decimal or hex).
240
241 -T SENSOR-TYPE-LIST, --exclude-sensor-types=SENSOR-TYPE-LIST
242 Specify sensor types to not show outputs for. Multiple types can
243 be eparated by commas or spaces. A special command line type of
244 "none", will indicate no types should be excluded (may be useful
245 for overriding configured defaults). Users may specify sensor
246 types by string (see --list-sensor-types below) or by number
247 (decimal or hex).
248
249 -L, --list-sensor-types
250 List sensor types.
251
252 -b, --bridge-sensors
253 By default, sensors readings are not attempted for sensors on
254 non-BMC owners. By setting this option, sensor requests can be
255 bridged to non-BMC owners to obtain sensor readings. Bridging
256 may not work on some interfaces/driver types.
257
258 --shared-sensors
259 Some sensors share the same sensor data record (SDR). This is
260 typically utilized for system event log (SEL) entries and not
261 for sensor readings. However, there may be some motherboards in
262 which this format is utilized for multiple active sensors, or
263 the user simply has interest in seeing the permutation of
264 entries shared by a SDR entry. By setting this option, each sen‐
265 sor number shared by a record will be iterated over and output.
266
267 --interpret-oem-data
268 Attempt to interpret OEM data, such as event data, sensor read‐
269 ings, or general extra info, etc. If an OEM interpretation is
270 not available, the default output will be generated. Correctness
271 of OEM interpretations cannot be guaranteed due to potential
272 changes OEM vendors may make in products, firmware, etc. See OEM
273 INTERPRETATION below for confirmed supported motherboard inter‐
274 pretations.
275
276 --ignore-not-available-sensors
277 Ignore not-available (i.e. N/A) sensors in output.
278
279 --ignore-unrecognized-events
280 Ignore unrecognized sensor events. This will suppress output of
281 unrecognized events, typically shown as 'Unrecognized Event =
282 XXXXh' in output. In addition, unrecognized events will be
283 ignored when calculating sensor state with --output-sensor-state
284 below.
285
286 --output-event-bitmask
287 Output event bitmask value instead of the string representation.
288
289 --output-sensor-state
290 Output sensor state in output. This will add an additional out‐
291 put reporting if a sensor is in a NOMINAL, WARNING, or CRITICAL
292 state. The sensor state is an interpreted value based on the
293 current sensor event. The sensor state interpretations are
294 determined by the configuration file
295 /etc/freeipmi//freeipmi_interpret_sensor.conf. See
296 freeipmi_interpret_sensor.conf(5) for more information. This
297 option gives identical output to the sensor state previously
298 output by ipmimonitoring(8).
299
300 --sensor-state-config-file=FILE
301 Specify an alternate sensor state configuration file. Option
302 ignored if --output-sensor-state not specified.
303
304 --entity-sensor-names
305 Output sensor names prefixed with their entity id and instance
306 number when appropriate. This may be necessary on some mother‐
307 boards to help identify what sensors are referencing. For exam‐
308 ple, a motherboard may have multiple sensors named 'TEMP'. The
309 entity id and instance number may help clarify which sensor
310 refers to "Processor 1" vs. "Processor 2".
311
312 --output-sensor-thresholds
313 Output sensor thresholds in output. This will add columns to the
314 default output for lower non-recoverable, lower critical, lower
315 non-critical, upper non-critical, upper critical, and upper non-
316 recoverable thresholds.
317
318 --no-sensor-type-output
319 Do not show sensor type output for each entry. On many systems,
320 the sensor type is redundant to the name of the sensor. This can
321 especially be true if --entity-sensor-names is specified. If
322 the sensor name is sufficient, or if the sensor type is of no
323 interest to the user, this option can be specified to condense
324 output.
325
326 --comma-separated-output
327 Output fields in comma separated format.
328
329 --no-header-output
330 Do not output column headers. May be useful in scripting.
331
332 --non-abbreviated-units
333 Output non-abbreviated units (e.g. 'Amps' instead of 'A'). May
334 aid in disambiguation of units (e.g. 'C' for Celsius or
335 Coulombs).
336
337 --legacy-output
338 Output in legacy format. Newer options may not be applicable to
339 legacy output.
340
341 --ipmimonitoring-legacy-output
342 Output legacy format of legacy ipmimonitoring tool. Newer
343 options may not be applicable to legacy output.
344
346 This tool requires access to the sensor data repository (SDR) cache for
347 general operation. By default, SDR data will be downloaded and cached
348 on the local machine. The following options apply to the SDR cache.
349
350 --flush-cache
351 Flush a cached version of the sensor data repository (SDR)
352 cache. The SDR is typically cached for faster subsequent access.
353 However, it may need to be flushed and re-generated if the SDR
354 has been updated on a system.
355
356 --quiet-cache
357 Do not output information about cache creation/deletion. May be
358 useful in scripting.
359
360 --sdr-cache-recreate
361 If the SDR cache is out of date or invalid, automatically recre‐
362 ate the sensor data repository (SDR) cache. This option may be
363 useful for scripting purposes.
364
365 --sdr-cache-file=FILE
366 Specify a specific sensor data repository (SDR) cache file to be
367 stored or read from. If this option is used when multiple hosts
368 are specified, the same SDR cache file will be used for all
369 hosts.
370
371 --sdr-cache-directory=DIRECTORY
372 Specify an alternate directory for sensor data repository (SDR)
373 caches to be stored or read from. Defaults to the home directory
374 if not specified.
375
377 By IPMI definition, all IPMI times and timestamps are stored in local‐
378 time. However, in many situations, the timestamps will not be stored in
379 localtime. Whether or not a system truly stored the timestamps in
380 localtime varies on many factors, such as the vendor, BIOS, and operat‐
381 ing system. The following options will allow the user to adjust the
382 interpretation of the stored timestamps and how they should be output.
383
384 --utc-to-localtime
385 Assume all times are reported in UTC time and convert the time
386 to localtime before being output.
387
388 --localtime-to-utc
389 Convert all localtime timestamps to UTC before being output.
390
391 --utc-offset=SECONDS
392 Specify a specific UTC offset in seconds to be added to time‐
393 stamps. Value can range from -86400 to 86400 seconds. Defaults
394 to 0.
395
397 The following options manipulate hostranged output. See HOSTRANGED SUP‐
398 PORT below for additional information on hostranges.
399
400 -B, --buffer-output
401 Buffer hostranged output. For each node, buffer standard output
402 until the node has completed its IPMI operation. When specifying
403 this option, data may appear to output slower to the user since
404 the the entire IPMI operation must complete before any data can
405 be output. See HOSTRANGED SUPPORT below for additional informa‐
406 tion.
407
408 -C, --consolidate-output
409 Consolidate hostranged output. The complete standard output from
410 every node specified will be consolidated so that nodes with
411 identical output are not output twice. A header will list those
412 nodes with the consolidated output. When this option is speci‐
413 fied, no output can be seen until the IPMI operations to all
414 nodes has completed. If the user breaks out of the program
415 early, all currently consolidated output will be dumped. See
416 HOSTRANGED SUPPORT below for additional information.
417
418 -F NUM, --fanout=NUM
419 Specify multiple host fanout. A "sliding window" (or fanout)
420 algorithm is used for parallel IPMI communication so that slower
421 nodes or timed out nodes will not impede parallel communication.
422 The maximum number of threads available at the same time is lim‐
423 ited by the fanout. The default is 64.
424
425 -E, --eliminate
426 Eliminate hosts determined as undetected by ipmidetect. This
427 attempts to remove the common issue of hostranged execution tim‐
428 ing out due to several nodes being removed from service in a
429 large cluster. The ipmidetectd daemon must be running on the
430 node executing the command.
431
432 --always-prefix
433 Always prefix output, even if only one host is specified or com‐
434 municating in-band. This option is primarily useful for script‐
435 ing purposes. Option will be ignored if specified with the -C
436 option.
437
439 Multiple hosts can be input either as an explicit comma separated lists
440 of hosts or a range of hostnames in the general form: prefix[n-m,l-
441 k,...], where n < m and l < k, etc. The later form should not be con‐
442 fused with regular expression character classes (also denoted by []).
443 For example, foo[19] does not represent foo1 or foo9, but rather repre‐
444 sents a degenerate range: foo19.
445
446 This range syntax is meant only as a convenience on clusters with a
447 prefixNN naming convention and specification of ranges should not be
448 considered necessary -- the list foo1,foo9 could be specified as such,
449 or by the range foo[1,9].
450
451 Some examples of range usage follow:
452 foo[01-05] instead of foo01,foo02,foo03,foo04,foo05
453 foo[7,9-10] instead of foo7,foo9,foo10
454 foo[0-3] instead of foo0,foo1,foo2,foo3
455
456 As a reminder to the reader, some shells will interpret brackets ([ and
457 ]) for pattern matching. Depending on your shell, it may be necessary
458 to enclose ranged lists within quotes.
459
460 When multiple hosts are specified by the user, a thread will be exe‐
461 cuted for each host in parallel up to the configured fanout (which can
462 be adjusted via the -F option). This will allow communication to large
463 numbers of nodes far more quickly than if done in serial.
464
465 By default, standard output from each node specified will be output
466 with the hostname prepended to each line. Although this output is read‐
467 able in many situations, it may be difficult to read in other situa‐
468 tions. For example, output from multiple nodes may be mixed together.
469 The -B and -C options can be used to change this default.
470
471 In-band IPMI Communication will be used when the host "localhost" is
472 specified. This allows the user to add the localhost into the hos‐
473 tranged output.
474
476 Most often, IPMI problems are due to configuration problems.
477
478 IPMI over LAN problems involve a misconfiguration of the remote
479 machine's BMC. Double check to make sure the following are configured
480 properly in the remote machine's BMC: IP address, MAC address, subnet
481 mask, username, user enablement, user privilege, password, LAN privi‐
482 lege, LAN enablement, and allowed authentication type(s). For IPMI 2.0
483 connections, double check to make sure the cipher suite privilege(s)
484 and K_g key are configured properly. The ipmi-config(8) tool can be
485 used to check and/or change these configuration settings.
486
487 Inband IPMI problems are typically caused by improperly configured
488 drivers or non-standard BMCs.
489
490 In addition to the troubleshooting tips below, please see WORKAROUNDS
491 below to also if there are any vendor specific bugs that have been dis‐
492 covered and worked around.
493
494 Listed below are many of the common issues for error messages. For
495 additional support, please e-mail the <freeipmi-users@gnu.org> mailing
496 list.
497
498 "username invalid" - The username entered (or a NULL username if none
499 was entered) is not available on the remote machine. It may also be
500 possible the remote BMC's username configuration is incorrect.
501
502 "password invalid" - The password entered (or a NULL password if none
503 was entered) is not correct. It may also be possible the password for
504 the user is not correctly configured on the remote BMC.
505
506 "password verification timeout" - Password verification has timed out.
507 A "password invalid" error (described above) or a generic "session
508 timeout" (described below) occurred. During this point in the protocol
509 it cannot be differentiated which occurred.
510
511 "k_g invalid" - The K_g key entered (or a NULL K_g key if none was
512 entered) is not correct. It may also be possible the K_g key is not
513 correctly configured on the remote BMC.
514
515 "privilege level insufficient" - An IPMI command requires a higher user
516 privilege than the one authenticated with. Please try to authenticate
517 with a higher privilege. This may require authenticating to a different
518 user which has a higher maximum privilege.
519
520 "privilege level cannot be obtained for this user" - The privilege
521 level you are attempting to authenticate with is higher than the maxi‐
522 mum allowed for this user. Please try again with a lower privilege. It
523 may also be possible the maximum privilege level allowed for a user is
524 not configured properly on the remote BMC.
525
526 "authentication type unavailable for attempted privilege level" - The
527 authentication type you wish to authenticate with is not available for
528 this privilege level. Please try again with an alternate authentication
529 type or alternate privilege level. It may also be possible the avail‐
530 able authentication types you can authenticate with are not correctly
531 configured on the remote BMC.
532
533 "cipher suite id unavailable" - The cipher suite id you wish to authen‐
534 ticate with is not available on the remote BMC. Please try again with
535 an alternate cipher suite id. It may also be possible the available
536 cipher suite ids are not correctly configured on the remote BMC.
537
538 "ipmi 2.0 unavailable" - IPMI 2.0 was not discovered on the remote
539 machine. Please try to use IPMI 1.5 instead.
540
541 "connection timeout" - Initial IPMI communication failed. A number of
542 potential errors are possible, including an invalid hostname specified,
543 an IPMI IP address cannot be resolved, IPMI is not enabled on the
544 remote server, the network connection is bad, etc. Please verify con‐
545 figuration and connectivity.
546
547 "session timeout" - The IPMI session has timed out. Please reconnect.
548 If this error occurs often, you may wish to increase the retransmission
549 timeout. Some remote BMCs are considerably slower than others.
550
551 "device not found" - The specified device could not be found. Please
552 check configuration or inputs and try again.
553
554 "driver timeout" - Communication with the driver or device has timed
555 out. Please try again.
556
557 "message timeout" - Communication with the driver or device has timed
558 out. Please try again.
559
560 "BMC busy" - The BMC is currently busy. It may be processing informa‐
561 tion or have too many simultaneous sessions to manage. Please wait and
562 try again.
563
564 "could not find inband device" - An inband device could not be found.
565 Please check configuration or specify specific device or driver on the
566 command line.
567
568 "driver timeout" - The inband driver has timed out communicating to the
569 local BMC or service processor. The BMC or service processor may be
570 busy or (worst case) possibly non-functioning.
571
572 "internal IPMI error" - An IPMI error has occurred that FreeIPMI does
573 not know how to handle. Please e-mail <freeipmi-users@gnu.org> to
574 report the issue.
575
576 "sensor config file parse error" - A parse error was found in the sen‐
577 sor interpretation configuration file. Please see freeipmi_inter‐
578 pret_sensor.conf(5).
579
581 With so many different vendors implementing their own IPMI solutions,
582 different vendors may implement their IPMI protocols incorrectly. The
583 following describes a number of workarounds currently available to han‐
584 dle discovered compliance issues. When possible, workarounds have been
585 implemented so they will be transparent to the user. However, some will
586 require the user to specify a workaround be used via the -W option.
587
588 The hardware listed below may only indicate the hardware that a problem
589 was discovered on. Newer versions of hardware may fix the problems
590 indicated below. Similar machines from vendors may or may not exhibit
591 the same problems. Different vendors may license their firmware from
592 the same IPMI firmware developer, so it may be worthwhile to try work‐
593 arounds listed below even if your motherboard is not listed.
594
595 If you believe your hardware has an additional compliance issue that
596 needs a workaround to be implemented, please contact the FreeIPMI main‐
597 tainers on <freeipmi-users@gnu.org> or <freeipmi-devel@gnu.org>.
598
599 assumeio - This workaround flag will assume inband interfaces communi‐
600 cate with system I/O rather than being memory-mapped. This will work
601 around systems that report invalid base addresses. Those hitting this
602 issue may see "device not supported" or "could not find inband device"
603 errors. Issue observed on HP ProLiant DL145 G1.
604
605 spinpoll - This workaround flag will inform some inband drivers (most
606 notably the KCS driver) to spin while polling rather than putting the
607 process to sleep. This may significantly improve the wall clock running
608 time of tools because an operating system scheduler's granularity may
609 be much larger than the time it takes to perform a single IPMI message
610 transaction. However, by spinning, your system may be performing less
611 useful work by not contexting out the tool for a more useful task.
612
613 authcap - This workaround flag will skip early checks for username
614 capabilities, authentication capabilities, and K_g support and allow
615 IPMI authentication to succeed. It works around multiple issues in
616 which the remote system does not properly report username capabilities,
617 authentication capabilities, or K_g status. Those hitting this issue
618 may see "username invalid", "authentication type unavailable for
619 attempted privilege level", or "k_g invalid" errors. Issue observed on
620 Asus P5M2/P5MT-R/RS162-E4/RX4, Intel SR1520ML/X38ML, and Sun Fire
621 2200/4150/4450 with ELOM.
622
623 nochecksumcheck - This workaround flag will tell FreeIPMI to not check
624 the checksums returned from IPMI command responses. It works around
625 systems that return invalid checksums due to implementation errors, but
626 the packet is otherwise valid. Users are cautioned on the use of this
627 option, as it removes validation of packet integrity in a number of
628 circumstances. However, it is unlikely to be an issue in most situa‐
629 tions. Those hitting this issue may see "connection timeout", "session
630 timeout", or "password verification timeout" errors. On IPMI 1.5 con‐
631 nections, the "noauthcodecheck" workaround may also needed too. Issue
632 observed on Supermicro X9SCM-iiF, Supermicro X9DRi-F, and Supermicro
633 X9DRFR.
634
635 idzero - This workaround flag will allow empty session IDs to be
636 accepted by the client. It works around IPMI sessions that report empty
637 session IDs to the client. Those hitting this issue may see "session
638 timeout" errors. Issue observed on Tyan S2882 with M3289 BMC.
639
640 unexpectedauth - This workaround flag will allow unexpected non-null
641 authcodes to be checked as though they were expected. It works around
642 an issue when packets contain non-null authentication data when they
643 should be null due to disabled per-message authentication. Those hit‐
644 ting this issue may see "session timeout" errors. Issue observed on
645 Dell PowerEdge 2850,SC1425. Confirmed fixed on newer firmware.
646
647 forcepermsg - This workaround flag will force per-message authentica‐
648 tion to be used no matter what is advertised by the remote system. It
649 works around an issue when per-message authentication is advertised as
650 disabled on the remote system, but it is actually required for the pro‐
651 tocol. Those hitting this issue may see "session timeout" errors.
652 Issue observed on IBM eServer 325.
653
654 endianseq - This workaround flag will flip the endian of the session
655 sequence numbers to allow the session to continue properly. It works
656 around IPMI 1.5 session sequence numbers that are the wrong endian.
657 Those hitting this issue may see "session timeout" errors. Issue
658 observed on some Sun ILOM 1.0/2.0 (depends on service processor
659 endian).
660
661 noauthcodecheck - This workaround flag will tell FreeIPMI to not check
662 the authentication codes returned from IPMI 1.5 command responses. It
663 works around systems that return invalid authentication codes due to
664 hashing or implementation errors. Users are cautioned on the use of
665 this option, as it removes an authentication check verifying the valid‐
666 ity of a packet. However, in most organizations, this is unlikely to be
667 a security issue. Those hitting this issue may see "connection time‐
668 out", "session timeout", or "password verification timeout" errors.
669 Issue observed on Xyratex FB-H8-SRAY, Intel Windmill, Quanta Winter‐
670 fell, and Wiwynn Windmill.
671
672 intel20 - This workaround flag will work around several Intel IPMI 2.0
673 authentication issues. The issues covered include padding of usernames,
674 and password truncation if the authentication algorithm is HMAC-
675 MD5-128. Those hitting this issue may see "username invalid", "password
676 invalid", or "k_g invalid" errors. Issue observed on Intel SE7520AF2
677 with Intel Server Management Module (Professional Edition).
678
679 supermicro20 - This workaround flag will work around several Supermicro
680 IPMI 2.0 authentication issues on motherboards w/ Peppercon IPMI
681 firmware. The issues covered include handling invalid length authenti‐
682 cation codes. Those hitting this issue may see "password invalid"
683 errors. Issue observed on Supermicro H8QME with SIMSO daughter card.
684 Confirmed fixed on newerver firmware.
685
686 sun20 - This workaround flag will work work around several Sun IPMI 2.0
687 authentication issues. The issues covered include invalid lengthed hash
688 keys, improperly hashed keys, and invalid cipher suite records. Those
689 hitting this issue may see "password invalid" or "bmc error" errors.
690 Issue observed on Sun Fire 4100/4200/4500 with ILOM. This workaround
691 automatically includes the "opensesspriv" workaround.
692
693 opensesspriv - This workaround flag will slightly alter FreeIPMI's IPMI
694 2.0 connection protocol to workaround an invalid hashing algorithm used
695 by the remote system. The privilege level sent during the Open Session
696 stage of an IPMI 2.0 connection is used for hashing keys instead of the
697 privilege level sent during the RAKP1 connection stage. Those hitting
698 this issue may see "password invalid", "k_g invalid", or "bad rmcpplus
699 status code" errors. Issue observed on Sun Fire 4100/4200/4500 with
700 ILOM, Inventec 5441/Dell Xanadu II, Supermicro X8DTH, Supermicro X8DTG,
701 Intel S5500WBV/Penguin Relion 700, Intel S2600JF/Appro 512X, Quanta
702 QSSC-S4R/Appro GB812X-CN, and Dell C5220. This workaround is automati‐
703 cally triggered with the "sun20" workaround.
704
705 integritycheckvalue - This workaround flag will work around an invalid
706 integrity check value during an IPMI 2.0 session establishment when
707 using Cipher Suite ID 0. The integrity check value should be 0 length,
708 however the remote motherboard responds with a non-empty field. Those
709 hitting this issue may see "k_g invalid" errors. Issue observed on
710 Supermicro X8DTG, Supermicro X8DTU, and Intel S5500WBV/Penguin Relion
711 700, and Intel S2600JF/Appro 512X.
712
713 assumemaxsdrrecordcount - This workaround will inform SDR reading to
714 stop reading after a known maximum number of SDR records have been
715 read. This will work around systems that have mis-implemented SDR read‐
716 ing functions. Those hitting this issue may see "SDR record count
717 invalid" errors. Issue observed on unspecified Inspur motherboard.
718
719 discretereading - This workaround option will allow analog sensor read‐
720 ings (i.e. rpm, degrees, etc.) to be read even if the event/reading
721 type code for the sensor is for a discrete sensor (i.e. assert vs.
722 deassert). This option works around poorly defined (and arguably ille‐
723 gal) SDR records that expect analog sensor readings to be read along‐
724 side discrete sensors. This option is confirmed to work around issues
725 on HP Proliant DL380 G7 and HP ProLiant ML310 G5 motherboards.
726
727 ignorescanningdisabled - This workaround option will allow sensor read‐
728 ings to be read even if the sensor scanning bit indicates a sensor is
729 disabled. This option works around motherboards that incorrectly indi‐
730 cate sensors as disabled. This may problem may exist on your mother‐
731 board if sensors are listed as "N/A" even if they should be available.
732 This option is confirmed to work around issues on Dell Poweredge 2900,
733 Dell Poweredge 2950, Dell Poweredge R410, Dell Poweredge R610, and HP
734 Integrity rx3600 motherboards.
735
736 assumebmcowner - This workaround option will allow sensor readings to
737 be read if the sensor owner is the BMC, but the reported sensor owner
738 is not the BMC. Typically, sensors owned by a non-BMC sensor owner must
739 be bridged (e.g. with the --bridge-sensors option), however if the non-
740 BMC sensor owner is invalid, bridging fails. This option works around
741 motherboards that incorrectly report an non-BMC sensor owner by always
742 assuming the sensor owner is the BMC. This problem may exist on your
743 motherboard if sensors are listed as "N/A" even if they should be
744 available. This option is confirmed to work around issues on Fujitsu
745 RX300 and Fujitsu RX300S2 motherboards.
746
747 ignoreauthcode - This workaround option will allow sensor readings to
748 be read if the remote machine is invalidly calculating authentication
749 codes (i.e. authentication hashes) when communicating over LAN. This
750 problem may exist on your system if the error "session timeout" errors
751 or there is an appearance of a hang. Users are cautioned on the use of
752 this option, as it removes an authentication check verifying the valid‐
753 ity of a packet. However, in most organizations, this is unlikely to be
754 a security issue. The ignoring of authentication packets is only lim‐
755 ited to the period in which sensor readings are done, and not for any
756 portion of the session authentication or session teardown. This option
757 is confirmed to work on Inventec 5441/Dell Xanadu II and Inventec
758 5442/Dell Xanadu III. (Note: On the above systems, this issue has only
759 been observed when the --bridge-sensors is used.)
760
761 No IPMI 1.5 Support - Some motherboards that support IPMI 2.0 have been
762 found to not support IPMI 1.5. Those hitting this issue may see "ipmi
763 2.0 unavailable" or "connection timeout" errors. This issue can be
764 worked around by using IPMI 2.0 instead of IPMI 1.5 by specifying
765 --driver-type=LAN_2_0. Issue observed on a number of HP and Supermicro
766 motherboards.
767
769 The following motherboards are confirmed to have atleast some support
770 by the --interpret-oem-data option. While highly probable the OEM data
771 interpretations would work across other motherboards by the same manu‐
772 facturer, there are no guarantees. Some of the motherboards below may
773 be rebranded by vendors/distributors.
774
775 Dell Poweredge R210, Dell Poweredge R610, Dell Poweredge R710, Dell
776 Poweredge R720, Fujitsu iRMC S1 and iRMC S2 systems, HP Proliant DL160
777 G8, Intel S5500WB/Penguin Computing Relion 700, Intel S2600JF/Appro
778 512X, Intel S2600GZ, Intel S2600WP, Intel S5000PAL, Intel Windmill,
779 Quanta Winterfell, Supermicro X7DBR-3, Supermicro X7DB8, Supermicro
780 X8DTN, Supermicro X7SBI-LN4, Supermicro X8DTH, Supermicro X8DTG, Super‐
781 micro X8DTU, Supermicro X8DT3-LN4F, Supermicro X8DTU-6+, Supermicro
782 X8DTL, Supermicro X8DTL-3F, Supermicro X8SIL-F, Supermicro X9SCL,
783 Supermicro X9SCM, Supermicro X8DTN+-F, Supermicro X8SIE, Supermicro
784 X9SCA-F-O, Supermicro H8DGU-F, Supermicro X9DRi-F, Supermicro X9DRI-
785 LN4F+, Supermicro X9SPU-F-O, Supermicro X9SCM-iiF, Wiwynn Windmill,
786 Wistron/Dell Poweredge C6220.
787
789 # ipmi-sensors
790
791 Show all sensors and readings on the local machine.
792
793 # ipmi-sensors --verbose
794
795 Show verbose sensors and readings on the local machine.
796
797 # ipmi-sensors --record-ids="7,11,102"
798
799 Show sensor record ids 7, 11, and 102 on the local machine.
800
801 # ipmi-sensors --sensor-types=fan
802
803 Show all sensors of type fan on the local machine.
804
805 # ipmi-sensors -h ahost -u myusername -p mypassword
806
807 Show all sensors on a remote machine using IPMI over LAN.
808
809 # ipmi-sensors -h mycluster[0-127] -u myusername -p mypassword
810
811 Show all sensors across a cluster using IPMI over LAN.
812
814 Upon successful execution, exit status is 0. On error, exit status is
815 1.
816
817 If multiple hosts are specified for communication, the exit status is 0
818 if and only if all targets successfully execute. Otherwise the exit
819 status is 1.
820
822 On older operating systems, if you input your username, password, and
823 other potentially security relevant information on the command line,
824 this information may be discovered by other users when using tools like
825 the ps(1) command or looking in the /proc file system. It is generally
826 more secure to input password information with options like the -P or
827 -K options. Configuring security relevant information in the FreeIPMI
828 configuration file would also be an appropriate way to hide this infor‐
829 mation.
830
831 In order to prevent brute force attacks, some BMCs will temporarily
832 "lock up" after a number of remote authentication errors. You may need
833 to wait awhile in order to this temporary "lock up" to pass before you
834 may authenticate again.
835
836 Some sensors may be output as not available (i.e. N/A) because the
837 owner of the sensor is not the BMC. To attempt to bridge sensors and
838 access sensors not on the BMC, users may wish to try the -b or
839 --bridge-sensors options.
840
842 Report bugs to <freeipmi-users@gnu.org> or <freeipmi-devel@gnu.org>.
843
845 Copyright © 2003-2015 FreeIPMI Core Team.
846
847 This program is free software; you can redistribute it and/or modify it
848 under the terms of the GNU General Public License as published by the
849 Free Software Foundation; either version 3 of the License, or (at your
850 option) any later version.
851
853 freeipmi(7), bmc-device(8), ipmi-config(8), freeipmi_interpret_sen‐
854 sor.conf(5)
855
856 http://www.gnu.org/software/freeipmi/
857
858
859
860IPMI Sensors version 1.6.7 2021-02-12 IPMI-SENSORS(8)