1thermal-conf.xml(5)           File Formats Manual          thermal-conf.xml(5)
2
3
4

NAME

6       thermal-conf.xml - Configuration file for thermal daemon
7

SYNOPSIS

9       $(TDCONFDIR)/etc/thermald/thermal-conf.xml
10
11

DESCRIPTION

13       thermal-conf.xml  is a configuration file for the thermal daemon. It is
14       used to configure thermal sensors, zone and cooling  devices.The  loca‐
15       tion of this file depends on the configuration option used during build
16       time.
17
18       The terminology used in this file conforms to  "Advanced  Configuration
19       and  Power  Interface  Specification".  The ACPI thermal model is based
20       around conceptual platform regions called thermal zones that physically
21       contain  devices, thermal sensors, and cooling controls. For example of
22       a thermal zone can be a CPU or a laptop cover. A zone can contain  mul‐
23       tiple  sensors  for  monitoring  temperature. A cooling device provides
24       interface to reduce the temperature of a source  device,  which  causes
25       increase in the temperature. An example of a cooling device is a FAN or
26       some Linux driver which can throttle the source device.
27
28       A thermal zone configuration includes one or more trip points.  A  trip
29       point is a temperature at which a cooling device needs to be activated.
30
31       A  cooling  device  can  be  either active or passive. An example of an
32       active device is a FAN, which will not reduce performance at  the  cost
33       of  consuming  more  power and noise. A passive device uses performance
34       throttling to control  temperature.  In  addition  to  cooling  devices
35       present  in  the thermal sysfs, the following cooling devices are built
36       into the thermald, which can be used as valid cooling device type:
37
38                   - rapl_controller
39
40                   - intel_pstate
41
42                   - cpufreq
43
44                   - LCD
45
46       The thermal sysfs under Linux (/sys/class/thermal) provides  a  way  to
47       represent  per platform ACPI configuration. The kernel thermal governor
48       uses this data to keep the platform thermals under control.  But  there
49       are some limitations, which thermald tries to resolve. For example:
50
51       -  If  the  ACPI  data is not optimized or buggy. In this case thermal-
52       conf.xml can be used to correct the behavior without change in BIOS.
53
54              - There may be thermal zones exposed by the thermal sysfs  with‐
55              out  associated  cooling  actions. In this case thermal conf.xml
56              can be used to tie the cooling devices to those zones.
57
58              - The best cooling method may not be in the  thermal  sysfs.  In
59              this  case  thermal-conf.xml  can  be  used to bind a zone to an
60              external cooling device.
61
62              - Specify thermal relationships. A zone  can  be  influenced  by
63              multiple source devices with varying degrees. In this case ther‐
64              mal-conf.xml can be used to define the  relative  influence  for
65              apply compensation.
66
67

FILE FORMAT

69       The  configuration file format conforms to XML specifications. A set of
70       tags defined to define platform, sensors, zones,  cooling  devices  and
71       trip points.
72
73       <ThermalConfiguration>
74         <Platform>
75           <Name>Example Platform Name</Name>
76           <!-- UUID is optional, if present this will be matched. Both product
77                name and UUID can contain wild card "*", which matches any
78                platform. -->
79           <UUID>Example UUID</UUID>
80           <!-- configuration file format conforms to XML specifications. A
81                set of tags defined to define platform, sensors, zones, cooling
82                devices and trip points. -->
83           <ProductName>Example Product Name</ProductName>
84           <Preference>QUIET|PERFORMANCE</Preference>
85           <!-- Quiet mode will only use passive cooling device. "PERFORMANCE"
86                will only select active devices. -->
87           <ThermalSensors>
88             <ThermalSensor>
89               <!-- New Sensor with a type and path -->
90               <Type>example_sensor_1</Type>
91               <Path>/some_path</Path>
92               <AsyncCapable>0</AsyncCapable>
93             </ThermalSensor>
94             <ThermalSensor>
95               <!-- Already present in thermal sysfs, enable this or
96                    add/change config For example, here we are indicating
97                    that sensor can do async events to avoid polling. -->
98               <Type>example_thermal_sysfs_sensor</Type>
99               <!-- If async capable, then we don't need to poll. -->
100               <AsyncCapable>1</AsyncCapable>
101             </ThermalSensor>
102           </ThermalSensors>
103           <ThermalZones>
104             <ThermalZone>
105               <Type>Example Zone type</Type>
106               <TripPoints>
107                 <TripPoint>
108                   <SensorType>example_sensor_1</SensorType>
109                   <!-- Temperature at which to take action. -->
110                   <Temperature> 75000 </Temperature>
111                   <!-- max/passive/active If a MAX type is specified, then
112                        daemon will use PID control to aggressively throttle
113                        to avoid reaching this temp. -->
114                   <type>max</type>
115                   <!-- SEQUENTIAL | PARALLEL. When a trip point temp is
116                        violated, then number of cooling devices can be
117                        activated. If control type is SEQUENTIAL then, it
118                        will exhaust first cooling device
119                        before trying next. -->
120                   <ControlType>SEQUENTIAL</ControlType>
121                   <CoolingDevice>
122                     <index>1</index>
123                     <type>example_cooling_device</type>
124                     <!-- Influence will be used order cooling devices. First
125                          cooling device will be used, which has highest
126                          influence. -->
127                     <influence> 100 </influence>
128                     <!-- Delay in using this cdev, this takes some time too
129                          actually cool a zone. -->
130                     <SamplingPeriod> 12 </SamplingPeriod>
131                     <!-- Set a specific state of this cooling device when this
132                          trip is violated. -->
133                     <TargetState> 6 </TargetState>
134                   </CoolingDevice>
135                 </TripPoint>
136               </TripPoints>
137             </ThermalZone>
138           </ThermalZones>
139           <CoolingDevices>
140             <CoolingDevice>
141               <!-- Cooling device can be specified by a type and optionally
142                    a sysfs path. If the type is already present in thermal
143                    sysfs, there is no need of a path. Compensation can use
144                    min/max and step size to increasing cool the system.
145                    Debounce period can be used to force a waiting period
146                    for action. -->
147               <Type>example_cooling_device</Type>
148               <MinState>0</MinState>
149               <IncDecStep>10</IncDecStep>
150               <ReadBack> 0 </ReadBack>
151               <MaxState>50</MaxState>
152               <DebouncePeriod>5000</DebouncePeriod>
153               <!-- If there are no PID parameters, compensation increase step
154                    wise and exponentially (if single step is not able to
155                    change trend).
156                    Alternatively a PID parameters can be specified then next
157                    step will use PID calculation using provided PID
158                    constants. -->
159               <PidControl>
160                 <kp>0.001</kp>
161                 <kd>0.0001</kd>
162                 <ki>0.0001</ki>
163               </PidControl>
164               <!-- Write some prefix attached to state value, like below the
165                    prefix is "level ". It will preserve spaces as entered
166                    when writing to sysfs. -->
167               <WritePrefix>level </WritePrefix>
168             </CoolingDevice>
169           </CoolingDevices>
170         </Platform>
171       </ThermalConfiguration>
172

EXAMPLE CONFIGURATIONS

174       Example  1:  This is a very simple configuration, to change the passive
175       limit on the CPU. Instead of default, this new temperature 86C  in  the
176       configuration  is  used.  This will start cooling, once the temperature
177       reaches 86C.
178
179       <?xml version="1.0"?>
180       <ThermalConfiguration>
181         <Platform>
182           <Name>Override CPU default passive</Name>
183           <ProductName>*</ProductName>
184           <Preference>QUIET</Preference>
185           <ThermalZones>
186             <ThermalZone>
187               <Type>cpu</Type>
188               <TripPoints>
189                 <TripPoint>
190                   <Temperature>86000</Temperature>
191                   <type>passive</type>
192                 </TripPoint>
193               </TripPoints>
194             </ThermalZone>
195           </ThermalZones>
196         </Platform>
197       </ThermalConfiguration>
198
199       Example 2: In this configuration, we  are  controlling  backlight  when
200       some  sensor  "SEN2"  reaches  60C.  Here  "LCD"  is a standard cooling
201       device, which uses Linux backlight sysfs  interface.  "LCD_Zone"  is  a
202       valid  thermal  zone in Linux thermal sysfs on the test platform, hence
203       we don't need to provide path for sysfs for "LCD_Zone". The Linux ther‐
204       mal sysfs is already parsed and loaded by thermald program.
205
206       <?xml version="1.0"?>
207       <ThermalConfiguration>
208         <Platform>
209           <Name>Change Backlight</Name>
210           <ProductName>*</ProductName>
211           <Preference>QUIET</Preference>
212           <ThermalZones>
213             <ThermalZone>
214               <Type>LCD_Zone</Type>
215               <TripPoints>
216                 <TripPoint>
217                   <SensorType>SEN2</SensorType>
218                   <Temperature>60000</Temperature>
219                   <type>passive</type>
220                   <CoolingDevice>
221                     <Type>LCD</Type>
222                   </CoolingDevice>
223                 </TripPoint>
224               </TripPoints>
225             </ThermalZone>
226           </ThermalZones>
227         </Platform>
228       </ThermalConfiguration>
229
230       Example  3:  In this example Lenovo Thinkpad X220 and fan speed is con‐
231       trolled. Here a cooling device "_Fan",  can  be  controlled  via  sysfs
232       /sys/devices/platform/thinkpad_hwmon/pwm1.    When   the   x86_pkg_temp
233       reaches 45C, Fan is started with increasing speeds, if the  temperature
234       can't be controlled at 45C.
235
236       <?xml version="1.0"?>
237       <ThermalConfiguration>
238         <Platform>
239           <Name>Lenovo ThinkPad X220</Name>
240           <ProductName>*</ProductName>
241           <Preference>QUIET</Preference>
242           <ThermalZones>
243             <ThermalZone>
244               <Type>x86_pkg_temp</Type>
245               <TripPoints>
246                 <TripPoint>
247                   <SensorType>x86_pkg_temp</SensorType>
248                   <Temperature>45000</Temperature>
249                   <type>passive</type>
250                   <ControlType>SEQUENTIAL</ControlType>
251                   <CoolingDevice>
252                     <index>1</index>
253                     <type>_Fan</type>
254                     <influence> 100 </influence>
255                     <SamplingPeriod> 12 </SamplingPeriod>
256                   </CoolingDevice>
257                 </TripPoint>
258               </TripPoints>
259             </ThermalZone>
260           </ThermalZones>
261           <CoolingDevices>
262             <CoolingDevice>
263               <Type>_Fan</Type>
264               <Path>/sys/devices/platform/thinkpad_hwmon/pwm1</Path>
265               <MinState>0</MinState>
266               <IncDecStep>30</IncDecStep>
267               <ReadBack> 0 </ReadBack>
268               <MaxState>255</MaxState>
269               <DebouncePeriod>5</DebouncePeriod>
270             </CoolingDevice>
271           </CoolingDevices>
272         </Platform>
273       </ThermalConfiguration>
274
275       Example  4:  The following example shows how PID can be used. Here once
276       temperature exceeds 80C, compensation is calculated using PID using 80C
277       as  set  point  of  PID. The compensation depends on error from the set
278       point. Here the default built in processor cooling device is used  with
279       min state as 0 and max state as 10.
280
281       <?xml version="1.0"?>
282       <ThermalConfiguration>
283         <Platform>
284           <Name>Use PID param </Name>
285           <ProductName>*</ProductName>
286           <Preference>QUIET</Preference>
287           <ThermalZones>
288             <ThermalZone>
289               <Type>x86_pkg_temp</Type>
290               <TripPoints>
291                 <TripPoint>
292                   <SensorType>x86_pkg_temp</SensorType>
293                   <Temperature>80000</Temperature>
294                   <type>passive</type>
295                   <ControlType>SEQUENTIAL</ControlType>
296                   <CoolingDevice>
297                     <type>Processor</type>
298                   </CoolingDevice>
299                 </TripPoint>
300               </TripPoints>
301             </ThermalZone>
302           </ThermalZones>
303           <CoolingDevices>
304             <CoolingDevice>
305               <Type>Processor</Type>
306               <PidControl>
307                 <kp>0.0002</kp>
308                 <kd>0</kd>
309                 <ki>0</ki>
310               </PidControl>
311             </CoolingDevice>
312           </CoolingDevices>
313         </Platform>
314       </ThermalConfiguration>
315
316       Example  5:  The  following  example  shows how to control Fan when the
317       sysfs expects some string prefix. For example instead of just  write  a
318       number  to  fan control sysfs, the interface requires "level " in front
319       of the speed index value.
320
321       <?xml version="1.0"?>
322       <ThermalConfiguration>
323         <Platform>
324           <Name>Use Fan control first then CPU throttle </Name>
325           <ProductName>*</ProductName>
326           <Preference>QUIET</Preference>
327           <ThermalZones>
328             <ThermalZone>
329               <Type>x86_pkg_temp</Type>
330               <TripPoints>
331                 <TripPoint>
332                   <SensorType>x86_pkg_temp</SensorType>
333                   <Temperature>80000</Temperature>
334                   <type>passive</type>
335                   <ControlType>SEQUENTIAL</ControlType>
336                   <CoolingDevice>
337                     <type>_fan_</type>
338                   </CoolingDevice>
339                 </TripPoint>
340               </TripPoints>
341             </ThermalZone>
342           </ThermalZones>
343           <CoolingDevices>
344             <CoolingDevice>
345               <Type>_fan_</Type>
346               <Path>/proc/acpi/ibm/fan</Path>
347               <WritePrefix>level </WritePrefix>
348               <MinState>0</MinState>
349               <MaxState>5</MaxState>
350               <DebouncePeriod>10</DebouncePeriod>
351             </CoolingDevice>
352           </CoolingDevices>
353         </Platform>
354       </ThermalConfiguration>
355
356       Example 6: Similar to example 5, but write different speeds at  differ‐
357       ent temperatures.
358
359       <?xml version="1.0"?>
360       <ThermalConfiguration>
361         <Platform>
362           <Name>Use Fan control first then CPU throttle </Name>
363           <ProductName>*</ProductName>
364           <Preference>QUIET</Preference>
365           <ThermalZones>
366             <ThermalZone>
367               <Type>x86_pkg_temp</Type>
368               <TripPoints>
369                 <TripPoint>
370                   <SensorType>x86_pkg_temp</SensorType>
371                   <Temperature>80000</Temperature>
372                   <type>passive</type>
373                   <CoolingDevice>
374                     <type>_fan_</type>
375                     <TargetState>1</TargetState>
376                   </CoolingDevice>
377                 </TripPoint>
378                 <TripPoint>
379                   <SensorType>x86_pkg_temp</SensorType>
380                   <Temperature>85000</Temperature>
381                   <type>passive</type>
382                   <CoolingDevice>
383                     <type>_fan_</type>
384                     <TargetState>2</TargetState>
385                   </CoolingDevice>
386                 </TripPoint>
387               </TripPoints>
388             </ThermalZone>
389           </ThermalZones>
390           <CoolingDevices>
391             <CoolingDevice>
392               <Type>_fan_</Type>
393               <Path>/proc/acpi/ibm/fan</Path>
394               <WritePrefix>level </WritePrefix>
395               <MinState>0</MinState>
396               <MaxState>5</MaxState>
397               <DebouncePeriod>10</DebouncePeriod>
398             </CoolingDevice>
399           </CoolingDevices>
400         </Platform>
401       </ThermalConfiguration>