1MODBUS_GET_FLOAT_CDA(3)        libmodbus Manual        MODBUS_GET_FLOAT_CDA(3)
2
3
4

NAME

6       modbus_get_float_cdab - get a float value from 2 registers in CDAB byte
7       order
8

SYNOPSIS

10       float modbus_get_float_cdab(const uint16_t *src);
11

DESCRIPTION

13       The modbus_get_float_cdab() function shall get a float from 4 bytes
14       with swapped words (CDAB order instead of ABCD). The src array must be
15       a pointer on two 16 bits values, for example, if the first word is set
16       to F147 and the second to 0x0020, the float value will be read as
17       123456.0.
18

RETURN VALUE

20       The function shall return a float.
21

SEE ALSO

23       modbus_set_float_cdab(3) modbus_get_float_abcd(3)
24       modbus_get_float_badc(3) modbus_get_float_dcba(3)
25

AUTHORS

27       The libmodbus documentation was written by Stéphane Raimbault
28       <stephane.raimbault@gmail.com>
29
30
31
32libmodbus v3.1.6                  02/04/2022           MODBUS_GET_FLOAT_CDA(3)
Impressum