1APCSMART(8)                       NUT Manual                       APCSMART(8)
2
3
4

NAME

6       apcsmart - Driver for American Power Conversion Smart Protocol UPS
7       equipment
8

SYNOPSIS

10       apcsmart -h
11
12       apcsmart -a UPS_NAME [-x option=value ...]
13
14           Note
15           This man page only documents the hardware-specific features of the
16           apcsmart driver. For information about the core driver, see
17           nutupsdrv(8).
18

SUPPORTED HARDWARE

20       The apcsmart driver should recognize (or at the very least, work with)
21       the majority of Smart-UPS models - which includes Smart-UPS, Matrix-UPS
22       and Back-UPS lineups, among few other ones.
23
24       Currently, we can roughly divide APC hardware into four groups (note
25       that the division isn’t strict by any means, and the borders between
26       those are pretty fuzzy):
27
28       [very] "old" models
29           These models usually have old APC logo, white color and no
30           programmable EEPROM; you won’t find them listed anywhere on APC’s
31           site either. The support for those will be usually based on
32           driver’s compatibility tables, or if the model (firmware) is not
33           listed in those - the driver will try to follow the very basic
34           subset of features, while still trying to remain useful. Despite
35           "smart" tagname, they often tend to behave in pretty dumb way (see
36           the section below about shutdown behaviour).
37
38           Example models:
39
40           ·   Smart-UPS 2000I
41
42           ·   Smart-UPS 900I
43
44       "new" models
45           These models usually come from late 1990s / pre-2009 times. They
46           are often referred as "3rd. gen". For the most part, they have
47           programmable EEPROM, report supported commands and capabilites, and
48           should work just fine with the apcsmart driver.
49
50       "microlink" models
51           WARNING: these are not natively supported by apcsmart (or apcupsd,
52           for that matter, if you’re wondering). Around 2007, APC (now APC
53           Schneider) decided to go back to its proprietry roots, and all the
54           new models (SMT, SMX, SURTD) use completely different protocol and
55           cables. If you purchased a new APC UPS - that uses cable with RJ45
56           on the one end, and DB-9 on the other - then you have such model.
57           Your only option to support it through NUT is to purchase a "legacy
58           communications card" - part #AP9620 (google 'AP9620' for more
59           details). Or if that’s not an option, rely on official software.
60
61       Microsol models
62           Several Microsol serial models sold in Brazil have been rebranded
63           as APC Back-UPS, and the model numbers tend to start with "BZ". If
64           you have one of these "Nobreaks", they will not work with the
65           apcsmart driver - please see the solis(8) driver instead.
66
67           Example models:
68
69           ·   Back-UPS BZ1200-BR
70
71           ·   Back-UPS BZ2200BI-BR
72
73       Another thing to remember is that Smart protocol is not USB protocol.
74       If you have UPS with both USB and serial ports, then depending on how
75       you connect it, you will need either apcsmart or usbhid-ups driver.
76

CABLING

78       This driver expects to see a 940-0024C cable or a clone by default. You
79       can switch to the 940-0095B dual-mode cable support with the 'cable='
80       definition described below.
81
82       If your 940-xx24X cable is broken or missing, use this diagram to build
83       a clone:
84
85       http://www.networkupstools.org/cables.html#_940_0024c_clone
86
87           Note
88           The "xx" is either "00" for a short cable, or the number of feet of
89           a longer cable. The "X" is a letter representing the minor revision
90           of the physical cable and its connectors ("C" and "E" are commonly
91           found revisions). All minor revisions should use the same pin-outs
92           and wiring.
93
94       You can specify alternate cable in ups.conf(5):
95
96       cable=940-0095B
97
98       Alternatively, you can also provide it on the command line using:
99
100       -x cable=940-0095B
101

TTY MODES

103       By default the driver works in canonical mode, but it proved to be a
104       problem in Windows systems. Furthermore there’s a possibility of some
105       obscure serial cards or serial-USB converters that could cause problems
106       as well. You can use 'ttymode=' option to force non-canonical
107       discipline in ups.conf(5):
108
109       ttymode=raw
110
111       Alternatively, you can also provide it on the command line using:
112
113       -x ttymode=raw
114
115           Note
116           Any other value will make the driver work in the canonical mode.
117

EXPLANATION OF SHUTDOWN METHODS SUPPORTED BY APC UPSES

119       APC hardware supports a lot of shutdown methods, that themselves can
120       differ in behaviour quite a bit, depending on the model.
121
122       S (soft hibernate)
123           This is most basic command present in probably all APC models. It
124           will hibernate the UPS, and subsequently wake it up when the mains
125           supply returns.  The command doesn’t work if the UPS is running on
126           mains.
127
128           "old" models
129               The behaviour here is unfortunately pretty primitive - when the
130               power returns, the UPS just wakes up. No grace periods, no min.
131               battery charge condition, etc. This is probably not what you
132               want.
133
134           "new" models
135               The behaviour here is as expected - the power is cut off after
136               the EEPROM defined grace period. The UPS will wake up when the
137               power returns, after the EEPROM defined delay AND if the EEPROM
138               defined min. battery charge level is met. The delay is counted
139               from the power's return.
140
141       CS (aka "force OB hack")
142           This is a trick to make UPS power down even if it's running on
143           mains. Immediately before issuing S, "simulate power failure" is
144           issued. The remaining behaviour is as in S case.
145
146           The name came from APC CS models, where such trick was used to
147           power down UPSes in consistent fashion using only S. It's better to
148           use @nnn command if your UPS supports it (and is not too old, see
149           below).
150
151       @nnn (hard hibernate)
152           This is basic command used to hibernate UPS regardless if it's
153           running on batteries or on mains. The option takes 3 digits
154           argument which can be used to specify additional wakeup delay (in 6
155           minute units).
156
157           "old" models
158               The behaviour is - unfortunately - similary primitive to S. The
159               UPS unconditionally wakes up after nnn*6 minutes - it doesn't
160               care if the power returned !  If nnn = 000, then UPS will do
161               precisely nothing. On those models you're better specifying nnn
162               > 0, if you can estimate the kind of power problems that might
163               be happening in your environment. Another thing to consider
164               with "old" models - you might lose the connection with the UPS,
165               until it wakes up (with S, the serial connection is kept
166               alive).
167
168           "new" models
169               All the usual variables defined in EEPROM are respected (see
170               S). Additionally, if nnn > 0, the nnn*6 minutes are added to
171               EEPROM defined delay. UPS will not power up if it's running on
172               batteries, contrary to what "old" models used to do - the
173               combined delay is counted from the moment of power return.
174
175           Supposedly there exist models that take 2 digits instead of 3. Just
176           in case, NUT also supports such variation. You have to provide
177           exactly 2 digits to trigger it (awd option, or argument to one of
178           the supported instant commands).
179
180       K (delayed poweroff)
181           This is permanent poweroff - the UPS will not wake up
182           automatically. On newer units, it will respect applicable EEPROM
183           variables.
184
185       Z (instant poweroff)
186           This is also permanent poweroff - the UPS will not wake up
187           automatically. The poweroff is executed immediately.
188

SHUTDOWN CONTROL BY NUT

190       There are three options used to control the shutdown behaviour.
191
192       sdtype=[0-5]
193           This option takes a single digit (0-5) as an argument. See below
194           for details.
195
196       advorder=no|[0-4]+
197           This option takes string of digits as an argument. Methods listed
198           are tried in turn until one of them succeedes. Note that the
199           meaning of digits is different from sdtype. See below for details.
200
201       awd=[0-9]{1,3}
202           This option lets you specify additional wakeup delay used by @. If
203           you provide exactly 2 digits, the driver will try 2 digits
204           variation (see previous section for more info). Otherwise standard
205           3 digits variation is used.  Note: the time unit is 6 minutes !
206
207       Keep in mind that sdtype and advorder are mutually exclusive. If
208       advorder is provided, sdtype is ignored. If advorder is set to 'no',
209       sdtype is used instead.
210
211       If nothing is provided, NUT will assume sdtype=0 - which is generally
212       fine for anything not too ancient or not too quirky.
213
214   SDTYPE
215       The values permitted are from 0 to 5. Only one can be specified.
216       Anything else will cause apcsmart to exit.
217
218       0
219           issue soft hibernate (S) if the UPS is running on batteries,
220           otherwise issue hard hibernate (@)
221
222       1
223           issue soft hibernate (S) (if on batteries), and if it fails (or on
224           mains) - try hard hibernate (@)
225
226       2
227           issue instant poweroff (Z)
228
229       3
230           issue delayed poweroff (K)
231
232       4
233           issue "force OB hack" (CS)
234
235       5
236           issue hard hibernate (@)
237
238           Note
239           Hard hibernate's additional wakeup delay can be provided by awd.
240
241   ADVORDER
242       The argument is either a word 'no', or a string of 1 - 5 digits in [0 -
243       4] range. Each digit maps to the one of shutdown methods supported by
244       APC UPSes. Methods listed in this way are tried in order, until one of
245       them succedes.
246
247       If advorder is undefined or set to 'no', sdtype is used instead.
248
249       The mapping is as follows:
250
251
252       0   soft hibernate (S)
253
254       1   hard hibernate (@)
255
256       2   delayed poweroff (K)
257
258       3   instant poweroff (Z)
259
260       4   "force OB hack" (CS)
261
262
263           Note
264           Hard hibernate's additional wakeup delay can be provided by awd.
265

IGNORING LB STATE

267       APC units - even if they report LB mode - will not go into shutdown
268       automatically. This gives us even more control with reference to "when
269       to actually shutdown PSU". Since version 2.6.2, NUT supports ignorelb
270       option in driver’s section of ups.conf(5). When such option is in
271       effect, the core driver will ignore LB state as reported by specific
272       driver and start shutdown basing the decision only on two conditions:
273
274       battery.charge < battery.charge.low
275
276       OR
277
278       battery.runtime < battery.runtime.low
279
280       Of course - if any of the variables are not available, the appropriate
281       condition is not checked. If you want to explicitly disable one of the
282       conditions, simply override the right hand variable causing the
283       condition to always evaluate to false (you can even provide negative
284       numbers).
285
286       APC UPSes don’t have battery.charge.low - you will have to define it if
287       you want to use such condition (prefix the variable with override. or
288       default.).
289
290       "New" units have battery.runtime.low, but depending on battery quality,
291       firmware version, calibration and UPS load - this variable can be
292       underestimated quite a bit - especially right after going into OB
293       state. This in turn can cause LB to be asserted, which under normal
294       conditions will cause NUT to initiate the shutdown. You might want to
295       disable this condition entirely, when relying on ignorelb option (this
296       was actually the main motivation behind introduction of such feature).
297
298       Simple example:
299
300           [apc]
301               ignorelb
302               override.battery.charge.low = 15
303               override.battery.runtime.low = -1
304
305       This would cause apcsmart to go into shutdown only if detected battery
306       charge < 15%. Runtime condition is always false in this example.
307
308       You could ask - why bother ? Well, the reason is already hinted above.
309       APC units can be very picky about the batteries, and their firmware can
310       underestimate the remaining runtime (especially right after going into
311       OB state). ignorelb option and override.* let you remain in control of
312       the UPS, not UPS in control of you.
313
314       Furthermore, this allows to specify conditions similary to how it’s
315       done in apcupsd daemon, so it should be welcome by people used to that
316       software.
317

SUPPORTED INSTANT COMMANDS

319       The apcsmart driver exposes following instant commands:
320
321       shutdown.return
322           executes soft hibernate
323
324       shutdown.return cs
325           executes "force OB hack"
326
327       shutdown.return at:<nbr>
328           executes "hard hibernate" with <nbr>*6 minutes additional wakeup
329           delay (<nbr> format is the same as of awd option)
330
331       shutdown.stayoff
332           executes "delayed poweroff"
333
334       load.off
335           executes "instant poweroff"
336
337       All the above commands must be issued 2nd time to have any effect (no
338       less than 3 seconds, and no more than 15 seconds after the initial
339       call). Those commands are mostly useful for manual testing, when your
340       machine is not powered by the UPS you're testing.
341
342       Other supported commands:
343
344       ·   load.on
345
346       ·   test.panel.start
347
348       ·   test.failure.start
349
350       ·   test.battery.start
351
352       ·   test.battery.stop
353
354       ·   bypass.start
355
356       ·   bypass.stop
357
358       ·   calibrate.start
359
360       ·   calibrate.stop
361

PREVIOUS DRIVER VERSION

363       Previous driver is still available as apcsmart-old, should there be any
364       need to use earlier version (bugs, incompatiblities with new
365       functionality, etc.). In due time, apcsmart-old will be phased out
366       completely, but this won’t happen until the new version gets solid
367       exposure with no pending issues.
368

BUGS

370       Some older APC UPS models return bogus data in the status register
371       during a front panel test. This is usually detected and discarded, but
372       some other unexpected values have occasionally slipped through.
373
374       APC UPS models with both USB and serial ports require a power cycle
375       when switching from USB communication to serial, and perhaps vice
376       versa.
377

AUTHOR

379       Nigel Metheringham <Nigel.Metheringham@Intechnology.co.uk> (drawing
380       heavily on the original apcsmart driver by Russell Kroll). This driver
381       was called newapc for a time and was renamed in the 1.5 series. In
382       2.6.2 it was renamed to apcsmart-old, being superseded by updated
383       version with new features, which is maintained by Michal Soltys
384       <soltys@ziu.info>
385

SEE ALSO

387       nutupsdrv(8), ups.conf(5), usbhid-ups(8), solis(8)
388
389   Internet resources:
390       The NUT (Network UPS Tools) home page: http://www.networkupstools.org/
391
392
393
394Network UPS Tools 2.7.3.          12/29/2015                       APCSMART(8)