NAME

6       netxml-ups - Driver for Eaton / MGE Network Management Card / Proxy
7       (XML/HTTP Protocol) equipment
8

NOTE

10       This man page only documents the hardware-specific features of the
11       netxml-ups driver. For information about the core driver, see
12       nutupsdrv(8).
13

SUPPORTED HARDWARE

15       netxml-ups supports all recent Eaton / MGE models which use a Network
16       Management Card or Proxy (MGE XML/HTTP protocol based). This applies to
17       both Eaton (previously MGE Office Protection Systems) and to MGE UPS
18       SYSTEMS. Supported card and proxy models are:
19
20       •   NMC Minislot (Ref 66102, firmware EA or newer),
21
22       •   SNMP/Web Minislot card (Ref 66244)
23
24       •   NMC Transverse (Ref 66074),
25
26       •   NMC & Modbus/JBus (Ref 66103),
27
28       •   Network Management Proxy,
29
30       •   ePDU Monitored (newer version).
31
32       Older models, such as SNMP card (Ref 66062 and Ref 66045), use the SNMP
33       protocol and should use the snmp-ups(8) driver with the "mibs=mge"
34       parameter.
35

EXTRA ARGUMENTS

37       This driver supports the following optional settings in the
38       ups.conf(5):
39
40       timeout=value
41           The timeout for connecting to and reading from the UPS. Defaults to
42           5 seconds. Don’t change this value unless you know exactly what
43           you’re doing.
44
45       This value must never be higher than half the MAXAGE value specified in
46       upsd.conf(5), otherwise you run the risk that upsd(8) declares the
47       driver stale while it is waiting for a connection to timeout.
48
49       subscribe
50           Connect to the NMC in subscribed mode. This allows to receive
51           notifications and alarms more quickly, beside from the standard
52           polling requests.
53
54       login=value
55           Set the login value for authenticated mode. This feature also needs
56           the password argument, and allows value settings in the card. This
57           feature is not used yet.
58
59       password=value
60           Set the password value, needed with the login for authenticated
61           mode. This feature is not used yet.
62
63       shutdown_duration=value
64           Set the shutdown duration of the operating system, in seconds. This
65           represents the amount of time needed by the system to operate a
66           clean shutdown. Defaults to 120 seconds.
67
68       shutdown_timer=value
69           Set the shutdown timer, in seconds. After value seconds running on
70           battery, the local system will receive a notification to shutdown.
71           Defaults to "none" (disabled).
72
73       do_convert_deci
74           If this flag value is present, the driver assumes you have a very
75           old MGE networked UPS (or rather an old network management card
76           firmware) which serves certain measurements spelled 10x too big in
77           the XML markup. Originally such measurements were decimated by the
78           driver — but this is wrong for newer, more sane, devices — so this
79           behavior was deprecated and is now disabled by default. Enabling
80           this flag in configuration of a particular driver instance restores
81           the old behavior for those measurements.
82

IMPLEMENTATION

84       The hostname of the UPS is specified with the "port" value in ups.conf,
85       i.e.:
86
87           [mgexml]
88                   driver = netxml-ups
89                   port = http://netxml-ups.example.com:80
90
91       Specifying the method to connect to the UPS (http, https) is mandatory.
92       If the port is equal to the default for the method specified (80 for
93       http, 443 for https) it may be omitted.
94
95       In order not to overload older NMCs by polling them too frequently, it
96       is recommended to increase the "pollinterval" (see nutupsdrv(8)) and
97       ups.conf(5)) to at least 5 seconds.
98

KNOWN ISSUES

100       Don’t connect to the UPS through a proxy. Although it would be trivial
101       to add support for proxies, this is not recommended and don’t ask for
102       it. Not only because it will prevent the driver to make a persistent
103       connection to the UPS, but also it adds an additional failure mode. If
104       the proxy goes down (for whatever reason), the driver will no longer be
105       able to reach the UPS.
106

AUTHORS

108       Arjen de Korte <adkorte-guest@alioth.debian.org>
109

SEE ALSO

111   The core driver:
112       nutupsdrv(8)
113
114   Internet resources:
115       The NUT (Network UPS Tools) home page: http://www.networkupstools.org/