1BESTUPS(8) NUT Manual BESTUPS(8)
2
3
4
6 bestups - Driver for Best Power / SOLA (Phoenixtec protocol) UPS
7 equipment
8
10 This man page only documents the hardware-specific features of the
11 bestups driver. For information about the core driver, see
12 nutupsdrv(8).
13
15 Please note that this driver is deprecated and will not receive new
16 development. If it works for managing your devices — fine, but if you
17 are running it to try setting up a new device, please consider the
18 newer nutdrv_qx(8) instead, which should handle all Q* protocol
19 variants for NUT.
20
21 Please do also report if your device works with this driver, but
22 nutdrv_qx(8) would not actually support it with any subdriver!
23
25 bestups was designed to monitor Best Power UPS hardware like the
26 Fortress, Fortress Telecom, Axxium Rackmount and Patriot Pro. It also
27 recognizes and supports SOLA units such as the 325, 520 and 620. In
28 addition, the Best 610 is supported using the ‘ID’ option.
29
30 Other UPS hardware using the Phoenixtec protocol should also work, but
31 they will generate a warning since their battery information is not
32 known.
33
34 This driver does not support some older Best/SOLA units.
35
37 This driver supports the following optional settings in the
38 ups.conf(5):
39
40 nombattvolt=num
41 Override the battery float voltage which is normally determined by
42 asking the hardware. This is useful if your UPS constantly reports
43 battery.charge values just below 100% even when it’s completely
44 charged.
45
46 If you have this problem, set this to whatever battery.voltage
47 reports when the UPS is known to be completely charged with a good
48 battery.
49
50 The author’s Best Fortress 750 uses nombattvolt=27.4.
51
52 battvoltmult=num
53 Multiply the reported battery voltage by this number. Some devices
54 report only a fraction of the total battery voltage.
55
56 For example, the SOLA 610 700VA UPS (with a 24V battery) reports
57 the single cell voltage (about 2.27V when fully charged). In this
58 particular case you can set battvoltmult = 12 in ups.conf(8) to fix
59 this.
60
61 ID=string
62 Set the Identification response string. This should only be used
63 with hardware that supports the Phoenixtec protocol status inquiry
64 commands, but not the "ID" command, such as the Best/SOLA 610.
65 Format of the ID string is: AAA,BBBB,CCC,DDD,EE.E,FF.F
66
67 AAA is the three-character identification for the UPS model.
68
69 BBBB is the output power in VA (volt amperes). B is an integer
70 number ranging from 0 to 9.
71
72 CCC is the Nominal Input Voltage. C is an integer number ranging
73 from 0 to 9. The unit is Volts AC.
74
75 DDD is the Nominal Output Voltage. D is an integer number ranging
76 from 0 to 9. The unit is Volts AC.
77
78 EE.E is the Battery Voltage that will cause the UPS to shut itself
79 off. E is an integer number ranging from 0 to 9. Then unit is Volts
80 DC and a decimal point is present.
81
82 FF.F or FFF.F is the Battery Voltage at full charge. F is an
83 integer number ranging from 0 to 9. Then unit is Volts DC.
84 Typically, for 700VA, 1KVA and 1.5KVA units, the format is FF.F.
85 For 2KVA and 3KVA units, the format is FFF.F.
86
87 Example: a Best 610 1.5KVA unit would use the string
88 "610,1500,120,120,10.0,48.0".
89
91 The battery charge percentage value (in battery.charge) is derived from
92 the voltage data that the UPS returns, since the UPS doesn’t return
93 that value directly. On some hardware, the charge will remain at 100%
94 for a long time and then drops quickly shortly before the battery runs
95 out. You can confirm from the battery.voltage readings that this is a
96 problem with the UPS and not this driver.
97
98 Similarly, the float from the charger in some models forces the battery
99 charge percentage back up to 100% immediately after the UPS goes back
100 on-line, so you can’t tell when it is really recharged.
101
102 Finally, some models give one value for the battery’s nominal voltage
103 and yet actually have a nominal voltage slightly below that. This leads
104 to things such as the perpetual 98.7% charge on the author’s Fortress
105 750, even when it’s been charging for weeks. You can use nombattvolt=
106 in ups.conf(8) to fix this.