6 megatec - Driver for Megatec protocol based UPS equipment
7
9 This man page only documents the hardware‐specific features of the
10 megatec driver. For information about the core driver, see nutups‐
11 drv(8).
12
13
15 The megatec driver is known to work with the following UPSes:
16
17 Maxxtro UPS 600VA
18 Mustek PowerMust 400VA Plus
19 Mustek PowerMust 600VA Plus
20 Mustek PowerMust 800VA Pro
21 Mustek PowerMust 1000VA Plus
22 Mustek PowerMust 1400VA Plus
23 Mustek PowerMust 2000VA USB
24 OnLite AQUA 50
25 Soyntec Sekury C 500
26 Soyntec Sekury C 800
27 Square One Power QP 1000
28 Tecnoware Easy Power 1200
29 Trust UPS 1000 Management PW-4105
30
31 It is also known to work with various models from Blazer, Energy Sistem
32 and Fenton Technologies. It may also work with similar models from
33 other manufacturers, but they haven't been tested.
34
35 On models with both a serial port (RS-232) and an USB port, only the
36 serial port is supported.
37
38
40 mfr=string
41
42 Optional. Specify the UPS manufacturer name.
43
44
45 model=string
46
47 Optional. Specify the UPS model name.
48
49
50 serial=string
51
52 Optional. Specify the UPS serial number.
53
54
55 lowbatt=float
56
57 Optional. Low battery level (%). Overrides the hardware default
58 level.
59
60
61 ondelay=int
62
63 Optional. Delay before the UPS is turned back on (minutes).
64
65
66 offdelay=int
67
68 Optional. Delay before the UPS is turned off (minutes).
69
70
72 This driver supports some extra commands (see upscmd(8)):
73
74
75 beeper.toggle
76 Toggle the UPS beeper. (Not available on some hardware.)
77
78
79 load.on
80 Turn on the load immediately.
81
82
83 load.off
84 Turn off the load immediately.
85
86
87 reset.input.minmax
88 Reset minimum and maximum input voltage status.
89
90
91 reset.watchdog
92 Restarts the UPS watchdog timeout. The watchdog is started if it
93 isn't running, which means the UPS shuts down one minute after
94 this command is executed for the last time, restarting one
95 minute afterwards. To cancel the watchdog, run the "shut‐
96 down.stop" command.
97
98
99 shutdown.return
100 Turn off the load and return when power is back.
101
102
103 shutdown.stayoff
104 Turn off the load and remain off.
105
106
107 shutdown.stop
108 Stop a shutdown in progress.
109
110
111 test.battery.start.deep
112 Perform a long battery test (Not available on some hardware.)
113
114
115 test.battery.start
116 Perform a (10 second) battery test.
117
118
119 test.battery.stop
120 Stop a running battery test. (Not available on some hardware.)
121
122
124 The behavior of the driver can be controlled by some user definable
125 variables (see upsrw(8)):
126
127
128 ups.delay.shutdown
129 Interval to wait after shutdown with delay command (seconds)
130
131
132 ups.delay.start
133 Interval to wait before (re)starting the load (seconds)
134
135
137 The battery charge (%) value is only a best-effort calculation and may
138 be incorrect, or non-existant, for some UPS models.
139
140 Some UPS commands aren't supported by all models. In most cases, the
141 driver will send a message to the system log when the user tries to
142 execute an unsupported command. Unfortunately, some models don't even
143 provide a way for the driver to check for this, so the unsupported com‐
144 mands will silently fail.
145
146 Some models report a bogus value for the beeper status (will always be
147 "enabled" or "disabled"). So, the "beeper.toggle" command may appear to
148 have no effect in the status reported by the driver when, in fact, it
149 is working fine.
150
151 The temperature value is also known to be bogus in some models.
152
153
155 Carlos Rodrigues <carlos.efr at mail.telepac.pt>
156
157
159 nutupsdrv(8), upsc(8), upscmd(8), upsrw(8)