1GENERICUPS(8) NUT Manual GENERICUPS(8)
2
3
4
6 genericups - Driver for contact-closure UPS equipment
7
9 This man page only documents the specific features of the genericups
10 driver. For information about the core driver, see nutupsdrv(8).
11
13 This driver supports hardware from many different manufacturers as it
14 only uses the very simplest of signaling schemes. Contact closure
15 refers to a kind of interface where basic high/low signals are provided
16 to indicate status. This kind of UPS can only report line power and
17 battery status.
18
19 This means that you will only get the essentials in ups.status: OL, OB,
20 and LB. Anything else requires a smarter UPS.
21
23 Cabling is different for every kind of UPS. See the table below for
24 information on what is known to work with a given UPS type.
25
27 This driver supports the following settings in the ups.conf(5):
28
29 upstype=type
30 Required. Configures the driver for a specific kind of UPS. See the
31 UPS Types section below for more information on which entries are
32 available.
33
34 mfr=string
35 Optional. The very nature of a generic UPS driver sometimes means
36 that the stock manufacturer data has no relation to the actual
37 hardware that is attached. With the mfr setting, you can change the
38 value that is seen by clients that monitor this UPS.
39
40 model=string
41 Optional. This is like mfr above, but it overrides the model string
42 instead.
43
44 serial=string
45 Optional. This is like mfr above and intended to record the
46 identification string of the UPS. It is titled "serial" because
47 usually this string is referred to as the serial number.
48
49 sdtime=value
50 Optional. The driver will sleep for this many seconds after setting
51 the shutdown signal. This is necessary for some hardware which
52 requires a sustained level to activate the shutdown sequence.
53
54 The default behavior of the driver is to exit immediately. If this
55 doesn’t reliably trigger a shutdown in your UPS hardware, use this
56 setting to give it more time to react.
57
58 Note
59 very large values for sdtime may create warnings from upsdrvctl if
60 it gets tired of waiting for the driver to return.
61
63 You may override the values for CP, OL, LB, and SD by defining them in
64 the ups.conf(5) after the upstype setting.
65
66 For example, to set the cable power to DTR and the low battery value to
67 DCD, it would look like this:
68
69 CP = DTR
70
71 LB = DCD
72
73 Recognized values for input lines are CTS, DCD, and RNG. Recognized
74 values for output lines are DTR, RTS, and ST. See below for more about
75 what these signals mean.
76
77 These values may be negated for active low signals. That is, "LB=-DCD"
78 recognizes a low battery condition when DCD is not held high.
79
81 The essence of a UPS definition in this driver is how it uses the
82 serial lines that are available. These are the abbreviations you will
83 see below:
84
85 OL
86 On line (no power failure) (opposite of OB - on battery)
87
88 LB
89 Low battery
90
91 SD
92 Shutdown load
93
94 CP
95 Cable power (must be present for cable to have valid reading)
96
97 CTS
98 Clear to Send. Received from the UPS.
99
100 RTS
101 Ready to Send. Sent by the PC.
102
103 DCD
104 Data Carrier Detect. Received from the UPS.
105
106 RNG
107 Ring indicate. Received from the UPS.
108
109 DTR
110 Data Terminal Ready. Sent by the PC.
111
112 ST
113 Send a BREAK on the transmit data line
114
115 A "-" in front of a signal name (like -RNG) means that the indicated
116 condition is signaled with an active low signal. For example, [LB=-RNG]
117 means the battery is low when the ring indicate line goes low, and that
118 the battery is OK when that line is held high.
119
121 0 = UPSonic LAN Saver 600
122
123 [CP=DTR+RTS] [OL=-CTS] [LB=DCD] [SD=DTR]
124
125 1 = APC Back-UPS/Back-UPS Pro/Smart-UPS with 940-0095A/C cable
126
127 [CP=DTR] [OL=-RNG] [LB=DCD] [SD=RTS]
128
129 2 = APC Back-UPS/Back-UPS Pro/Smart-UPS with 940-0020B cable
130
131 [CP=RTS] [OL=-CTS] [LB=DCD] [SD=DTR+RTS]
132
133 Type 2 has also been reported to work with the 940-0020C cable.
134
135 3 = PowerTech Comp1000 with DTR cable power
136
137 [CP=DTR] [OL=CTS] [LB=DCD] [SD=DTR+RTS]
138
139 4 = Generic RUPS Model
140
141 [CP=RTS] [OL=CTS] [LB=-DCD] [SD=-RTS]
142
143 5 = Tripp Lite UPS with Lan2.2 interface (black 73-0844 cable)
144
145 [CP=DTR] [OL=CTS] [LB=-DCD] [SD=DTR+RTS]
146
147 6 = Best Patriot with INT51 cable
148
149 [CP=DTR] [OL=CTS] [LB=-DCD] [SD=RTS]
150
151 7 = CyberPower Power99 Also Upsonic Power Guardian PG-500, Belkin
152 Belkin Home Office, F6H350-SER, F6H500-SER, F6H650-SER, Eaton
153 Management Card Contact - Config3 with cable 66033 (shutdown does not
154 work)
155
156 [CP=RTS] [OL=CTS] [LB=-DCD] [SD=DTR]
157
158 8 = Nitram Elite 500
159
160 [CP=DTR] [OL=CTS] [LB=-DCD] [SD=???]
161
162 9 = APC Back-UPS/Back-UPS Pro/Smart-UPS with 940-0023A cable
163
164 [CP=none] [OL=-DCD] [LB=CTS] [SD=RTS]
165
166 10 = Victron Lite with crack cable
167
168 [CP=RTS] [OL=CTS] [LB=-DCD] [SD=DTR]
169
170 11 = Powerware 3115
171
172 [CP=DTR] [OL=-CTS] [LB=-DCD] [SD=ST]
173
174 12 = APC Back-UPS Office with 940-0119A cable
175
176 [CP=RTS] [OL=-CTS] [LB=DCD] [SD=DTR]
177
178 13 = RPT Repoteck RPT-800A/RPT-162A
179
180 [CP=DTR+RTS] [OL=DCD] [LB=-CTS] [SD=ST]
181
182 14 = Online P-series
183
184 [CP=DTR] [OL=DCD] [LB=-CTS] [SD=RTS]
185
186 15 = Powerware 5119, 5125
187
188 [CP=DTR] [OL=CTS] [LB=-DCD] [SD=ST]
189
190 16 = Nitram Elite 2002
191
192 [CP=DTR+RTS] [OL=CTS] [LB=-DCD] [SD=???]
193
194 17 = PowerKinetics 9001
195
196 [CP=DTR] [OL=CTS] [LB=-DCD] [SD=???]
197
198 18 = TrippLite Omni 450LAN with Martin’s cabling
199
200 [CP=DTR] [OL=CTS] [LB=DCD] [SD=none]
201
202 19 = Fideltronic Ares Series
203
204 [CP=DTR] [OL=CTS] [LB=-DCD] [SD=RTS]
205
206 20 = Powerware 5119 RM
207
208 [CP=DTR] [OL=-CTS] [LB=DCD] [SD=ST]
209
210 Check docs/cables/powerware.txt
211
212 21 = Generic RUPS 2000 (Megatec M2501 cable)
213
214 [CP=RTS] [OL=CTS] [LB=-DCD] [SD=RTS+DTR]
215
216 22 = Gamatronic All models with alarm interface (also CyberPower SL
217 series)
218
219 [CP=RTS] [OL=CTS] [LB=-DCD] [SD=DTR]
220
222 Many different UPS companies make models with similar interfaces. The
223 RUPS cable seems to be especially popular in the "power strip" variety
224 of UPS found in office supply stores. If your UPS works with an entry
225 in the table above, but the model or manufacturer information don’t
226 match, don’t despair. You can fix that easily by using the mfr and
227 model variables documented above in your ups.conf(5).
228
230 If your UPS isn’t listed above, you can try going through the list
231 until you find one that works. There is a lot of cable and interface
232 reuse in the UPS world, and you may find a match.
233
234 To do this, first make sure nothing important is plugged into the
235 outlets on the UPS, as you may inadvertently switch it off. Definitely
236 make sure that the computer you’re using is not plugged into that UPS.
237 Plug in something small like a lamp so you know when power is being
238 supplied to the outlets.
239
240 Now, you can either attempt to make an educated guess based on the
241 documentation your manufacturer has provided (if any), or just start
242 going down the list.
243
244 Step 1
245 Pick a driver to try from the list (genericups -h) and go to step 2.
246
247 Step 2
248 Start the driver with the type you want to try -
249
250 genericups -x upstype=n /dev/port
251
252 Let upsd sync up (watch the syslog), and then run upsc to see what it
253 found. If the STATUS is right (should be OL for on line), continue to
254 Step 3, otherwise go back to step 1.
255
256 Alternatively, you can run genericups in debug mode -
257
258 genericups -DDDDD -x upstype=n /dev/port
259
260 In this mode it will be running in the foreground and continuously
261 display the line and battery status of the UPS.
262
263 Step 3
264 Disconnect the UPS from the wall/mains power. This is easiest if you
265 have a switched outlet in between it and the wall, but you can also
266 just pull the plug to test. The lamp should stay lit, and the status
267 should switch to "OB". If the lamp went out or the status didn’t go to
268 "OB" within about 15 seconds, go to Step 1. Otherwise, continue to Step
269 4.
270
271 Step 4
272 At this point, we know that OL and OB work. If nothing else beyond this
273 point works, you at least know what your OL/OB value should be.
274
275 Wait for the UPS to start complaining about a low battery. Depending on
276 the size of your UPS battery and the lamp’s bulb, this could take
277 awhile. It should start complaining audibly at some point. When this
278 happens, STATUS should show "OB LB" within 15 seconds. If not, go to
279 Step 1, otherwise continue to Step 5.
280
281 Step 5
282 So far: OL works, OB works, and LB works.
283
284 With the UPS running on battery, run the genericups driver with the -k
285 switch to shut it down.
286
287 genericups -x upstype=n -k /dev/port
288
289 If the UPS turns off the lamp, you’re done. At this point, you have
290 verified that the shutdown sequence actually does what you want. You
291 can start using the genericups driver with this type number for normal
292 operations.
293
294 You should use your findings to add a section to your ups.conf. Here is
295 a quick example:
296
297 [myups]
298 driver = genericups
299 port = /dev/ttyS0
300 upstype = 1
301
302 Change the port and upstype values to match your system.
303
305 If the above testing sequence fails, you will probably need to create a
306 new entry to support your hardware. All UPS types are determined from
307 the table in the genericups.h file in the source tree.
308
309 On a standard 9 pin serial port, there are 6 lines that are used as the
310 standard "high/low" signal levels. 4 of them are incoming (to the PC,
311 from the UPS), and the other 2 are outgoing (to the UPS, from the PC).
312 The other 3 are the receive/transmit lines and the ground.
313
314 Be aware that many manufacturers remap pins within the cable. If you
315 have any doubts, a quick check with a multimeter should confirm whether
316 the cable is straight-through or not. Another thing to keep in mind is
317 that some cables have electronics in them to do special things. Some
318 have resistors and transistors on board to change behavior depending on
319 what’s being supplied by the PC.
320
322 These have been contributed by users of this driver.
323
324 The Centralion CL series may power down the load if the driver starts
325 up with the UPS running on battery as the default line settings contain
326 the shutdown sequence. - Neil Muller
327
328 The Tripp-Lite Internet Office 700 must be used with the black 73-0844
329 cable instead of the gray 73-0743 cable. This entry should work with
330 any of their models with the Lan 2.2 interface - see the sticker by the
331 DB9 connector on the UPS. - Stephen Brown
332
333 Type 5 should work with the Tripp-Lite Lan 2.1 interface and the
334 73-0724 cable. This was tested with the OmniSmart 675 PNP on Red Hat
335 7.2. - Q Giese
336
337 Types 7 and 10 should both work with the PhoenixTec A1000.
338
340 There is no way to reliably detect a contact-closure UPS. This means
341 the driver will start up happily even if no UPS is detected. It also
342 means that if the connection between the UPS and computer is
343 interrupted, you may not be able to sense this in software.
344
345 Most contact-closure UPSes will not power down the load if the line
346 power is present. This can create a race when using slave upsmon(8)
347 systems. See the upsmon(8) man page for more information.
348
349 The solution to both of these problems is to upgrade to a smart
350 protocol UPS of some kind that allows detection and proper load cycling
351 on command.
352
354 The core driver
355 nutupsdrv(8)
356
357 Internet resources
358 The NUT (Network UPS Tools) home page: http://www.networkupstools.org/
359
360
361