1GENERICUPS(8)               Network UPS Tools (NUT)              GENERICUPS(8)
2
3
4

NAME

6       genericups - Driver for contact‐closure UPS equipment
7
8

NOTE

10       This  man  page  only documents the specific features of the genericups
11       driver.  For information about the core driver, see nutupsdrv(8).
12
13

SUPPORTED HARDWARE

15       This driver supports hardware from many different manufacturers  as  it
16       only  uses  the  very  simplest  of signaling schemes.  Contact closure
17       refers to a kind of interface where basic high/low signals are provided
18       to  indicate  status.   This kind of UPS can only report line power and
19       battery status.
20
21       This means that you will only get the essentials in ups.status: OL, OB,
22       and LB.  Anything else requires a smarter UPS.
23
24

CABLING

26       Cabling  is  different  for every kind of UPS.  See the table below for
27       information on what is known to work with a given UPS type.
28
29

EXTRA ARGUMENTS

31       This driver supports the following settings in the ups.conf(5):
32
33
34       upstype=type
35
36              Required.  Configures the driver for a  specific  kind  of  UPS.
37              See  the  UPS  Types section below for more information on which
38              entries are available.
39
40
41       mfr=string
42
43              Optional.  The very nature of a  generic  UPS  driver  sometimes
44              means  that  the  stock manufacturer data has no relation to the
45              actual hardware that is attached.  With the mfr setting, you can
46              change the value that is seen by clients that monitor this UPS.
47
48
49       model=string
50
51              Optional.   This  is  like mfr above, but it overrides the model
52              string instead.
53
54
55       serial=string
56
57              Optional.  This is like mfr above and  intended  to  record  the
58              identification  string  of  the UPS. It is titled serial because
59              usually this string is referred to as the serial number.
60
61
62       sdtime=value
63
64              Optional.  The driver will sleep for  this  many  seconds  after
65              setting  the  shutdown signal.  This is necessary for some hard‐
66              ware which requires a sustained level to activate  the  shutdown
67              sequence.
68
69              The  default  behavior of the driver is to exit immediately.  If
70              this doesn't reliably trigger a shutdown in your  UPS  hardware,
71              use this setting to give it more time to react.
72
73              Note: very large values for sdtime may create warnings from ups‐
74              drvctl if it gets tired of waiting for the driver to return.
75
76

CUSTOM CONFIGURATIONS

78       You may override the values for CP, OL, LB, and SD by defining them  in
79       the ups.conf after the upstype setting.
80
81       For example, to set the cable power to DTR and the low battery value to
82       DCD, it would look like this:
83
84            CP = DTR
85
86            LB = DCD
87
88       Recognized values for input lines are CTS, DCD,  and  RNG.   Recognized
89       values for output lines are DTR, RTS, and ST.  See below for more about
90       what these signals mean.
91
92       These values may be negated for active low signals.  That is, "LB=-DCD"
93       recognizes a low battery condition when DCD is not held high.
94
95

TYPE INFORMATION

97       The  essence  of  a  UPS  definition  in this driver is how it uses the
98       serial lines that are available.  These are the abbreviations you  will
99       see below:
100
101            OL ‐ On line (no power failure) (opposite of OB ‐ on battery)
102
103            LB ‐ Low battery
104
105            SD ‐ Shutdown load
106
107            CP ‐ Cable power (must be present for cable to have valid reading)
108
109            CTS ‐ Clear to Send.  Received from the UPS.
110
111            RTS ‐ Ready to Send.  Sent by the PC.
112
113            DCD ‐ Data Carrier Detect.  Received from the UPS.
114
115            RNG ‐ Ring indicate.  Received from the UPS.
116
117            DTR ‐ Data Terminal Ready.  Sent by the PC.
118
119            ST ‐ Send a BREAK on the transmit data line
120
121       A - in front of a signal name (like -RNG) means that the indicated con‐
122       dition is signaled with an active low signal.  For  example,  [LB=-RNG]
123       means the battery is low when the ring indicate line goes low, and that
124       the battery is OK when that line is held high.
125
126

UPS TYPES

128       0 = UPSonic LAN Saver 600
129           [CP=DTR+RTS] [OL=-CTS] [LB=DCD] [SD=DTR]
130
131       1 = APC Back‐UPS/Back‐UPS Pro/Smart‐UPS with 940-0095A/C cable
132           [CP=DTR] [OL=-RNG] [LB=DCD] [SD=RTS]
133
134       2 = APC Back‐UPS/Back‐UPS Pro/Smart‐UPS with 940-0020B cable
135           [CP=RTS] [OL=-CTS] [LB=DCD] [SD=DTR+RTS]
136
137           Type 2 has also been reported to work with the 940-0020C cable.
138
139       3 = PowerTech Comp1000 with DTR cable power
140           [CP=DTR] [OL=CTS] [LB=DCD] [SD=DTR+RTS]
141
142       4 = Generic RUPS Model
143           [CP=RTS] [OL=CTS] [LB=-DCD] [SD=-RTS]
144
145       5 = Tripp Lite UPS with Lan2.2 interface (black 73-0844 cable)
146           [CP=DTR] [OL=CTS] [LB=-DCD] [SD=DTR+RTS]
147
148       6 = Best Patriot with INT51 cable
149           [CP=DTR] [OL=CTS] [LB=-DCD] [SD=RTS]
150
151       7 = CyberPower Power99
152           also Upsonic Power Guardian PG-500
153
154           Also Belkin Belkin Home Office
155           F6H350-SER, F6H500-SER, F6H650-SER
156
157           [CP=RTS] [OL=CTS] [LB=-DCD] [SD=DTR]
158
159       8 = Nitram Elite 500
160           [CP=DTR] [OL=CTS] [LB=-DCD] [SD=???]
161
162       9 = APC Back‐UPS/Back‐UPS Pro/Smart‐UPS with 940-0023A cable
163           [CP=none] [OL=-DCD] [LB=CTS] [SD=RTS]
164
165       10 = Victron Lite with crack cable
166            [CP=RTS] [OL=CTS] [LB=-DCD] [SD=DTR]
167
168       11 = Powerware 3115
169            [CP=DTR] [OL=-CTS] [LB=-DCD] [SD=ST]
170
171       12 = APC Back-UPS Office with 940-0119A cable
172            [CP=RTS] [OL=-CTS] [LB=DCD] [SD=DTR]
173
174       13 = RPT Repoteck RPT-800A/RPT-162A
175            [CP=DTR+RTS] [OL=DCD] [LB=-CTS] [SD=ST]
176
177       14 = Online P-series
178            [CP=DTR] [OL=DCD] [LB=-CTS] [SD=RTS]
179
180       15 = Powerware 5119, 5125
181            [CP=DTR] [OL=CTS] [LB=-DCD] [SD=ST]
182
183       16 = Nitram Elite 2002
184            [CP=DTR+RTS] [OL=CTS] [LB=-DCD] [SD=???]
185
186       17 = PowerKinetics 9001
187            [CP=DTR] [OL=CTS] [LB=DCD] [SD=???]
188
189       18 = TrippLite Omni 450LAN with Martin's cabling
190            [CP=DTR] [OL=CTS] [LB=DCD] [SD=none]
191
192            http://lists.exploits.org/upsdev/Jul2002/00012.html
193
194       19 = Fideltronic Ares Series
195            [CP=DTR] [OL=CTS] [LB=-DCD] [SD=RTS]
196
197       20 = Powerware 5119 RM
198            [CP=DTR] [OL=-CTS] [LB=DCD] [SD=ST]
199
200            Check docs/cables/powerware.txt
201
202       21 = Generic RUPS 2000 (Megatec M2501 cable)
203            [CP=RTS] [OL=CTS] [LB=-DCD] [SD=RTS+DTR]
204
205            http://lists.exploits.org/upsdev/Oct2004/00004.html
206
207       22 = Gamatronic All models with alarm interface
208            also CyberPower SL series
209
210            [CP=RTS] [OL=CTS] [LB=-DCD] [SD=DTR]
211
212

SIMILAR MODELS

214       Many different UPS companies make models with similar interfaces.   The
215       RUPS  cable seems to be especially popular in the "power strip" variety
216       of UPS found in office supply stores.  If your UPS works with an  entry
217       in  the  table  above,  but the model or manufacturer information don't
218       match, don't despair.  You can fix that easily by  using  the  mfr  and
219       model variables documented above in your ups.conf(5).
220
221

TESTING COMPATIBILITY

223       If  your  UPS  isn't  listed  above, you can try going through the list
224       until you find one that works.  There is a lot of cable  and  interface
225       reuse in the UPS world, and you may find a match.
226
227       To  do this, first make sure nothing important is plugged into the out‐
228       lets on the UPS, as you may inadvertently switch  it  off.   Definitely
229       make  sure that the computer you're using is not plugged into that UPS.
230       Plug in something small like a lamp so you know  when  power  is  being
231       supplied to the outlets.
232
233       Now, you can either attempt to make an educated guess based on the doc‐
234       umentation your manufacturer has provided (if any), or just start going
235       down the list.
236
237       Step 1
238
239       Pick a driver to try from the list (genericups -h) and go to step 2.
240
241       Step 2
242
243       Start the driver with the type you want to try ‐
244
245               genericups -x upstype=n /dev/port
246
247       Let  upsd  sync up (watch the syslog), and then run upsc to see what it
248       found.  If the STATUS is right (should be OL for on line), go  to  step
249       3, otherwise go back to step 1.
250
251       Step 3
252
253       Disconnect  the  UPS from the wall/mains power.  This is easiest if you
254       have a switched outlet in between it and the wall,  but  you  can  also
255       just  pull  the plug to test.  The lamp should stay lit, and the status
256       should switch to "OB".  If the lamp went out or the status didn't go to
257       "OB"  within  about  15  seconds, go to step 1.  Otherwise, continue to
258       step 4.
259
260       Step 4
261
262       At this point, we know that OL and OB work.   If  nothing  else  beyond
263       this point works, you at least know what your OL/OB value should be.
264
265       Wait  for  the UPS to start complaining about a low battery.  Depending
266       on the size of your UPS battery and the lamp's bulb,  this  could  take
267       awhile.   It should start complaining audibly at some point.  When this
268       happens, STATUS should show "OB LB" within 15 seconds.  If not,  go  to
269       step 1, otherwise continue to step 5.
270
271       Step 5
272
273       So far: OL works, OB works, and LB works.
274
275       With  the UPS running on battery, run the genericups driver with the -k
276       switch to shut it down.
277
278               genericups -x upstype=n -k /dev/port
279
280       If the UPS turns off the lamp, you're done.  At this  point,  you  have
281       verified  that  the shutdown sequence actually does what you want.  You
282       can start using the genericups driver with this type number for  normal
283       operations.
284
285       You  should  use your findings to add a section to your ups.conf.  Here
286       is a quick example:
287
288               [myups]
289                       driver = genericups
290                       port = /dev/ttyS0
291                       upstype = 1
292
293       Change the port and upstype values to match your system.
294
295

NEW SUPPORT

297       If the above testing sequence fails, you will probably need to create a
298       new  entry to support your hardware.  All UPS types are determined from
299       the table in the genericups.h file in the source tree.
300
301       On a standard 9 pin serial port, there are 6 lines that are used as the
302       standard  "high/low" signal levels.  4 of them are incoming (to the PC,
303       from the UPS), and the other 2 are outgoing (to the UPS, from the  PC).
304       The other 3 are the receive/transmit lines and the ground.
305
306       Be  aware  that many manufacturers remap pins within the cable.  If you
307       have any doubts, a quick check with a multimeter should confirm whether
308       the cable is straight‐through or not.  Another thing to keep in mind is
309       that some cables have electronics in them to do special  things.   Some
310       have resistors and transistors on board to change behavior depending on
311       what's being supplied by the PC.
312
313

SPECIFIC MODEL NOTES

315       These have been contributed by users of this driver.
316
317       The Centralion CL series may power down the load if the  driver  starts
318       up with the UPS running on battery as the default line settings contain
319       the shutdown sequence.  ‐ Neil Muller
320
321       The Tripp‐Lite Internet Office 700 must be used with the black  73‐0844
322       cable  instead  of the gray 73‐0743 cable.  This entry should work with
323       any of their models with the Lan 2.2 interface ‐ see the sticker by the
324       DB9 connector on the UPS.  ‐ Stephen Brown
325
326       Type  5  should  work  with  the  Tripp‐Lite  Lan 2.1 interface and the
327       73‐0724 cable.  This was tested with the OmniSmart 675 PNP on  Red  Hat
328       7.2.  ‐ Q Giese
329
330       Types 7 and 10 should both work with the PhoenixTec A1000.
331
332

BUGS

334       There  is  no way to reliably detect a contact‐closure UPS.  This means
335       the driver will start up happily even if no UPS is detected.   It  also
336       means  that  if  the  connection between the UPS and computer is inter‐
337       rupted, you may not be able to sense this in software.
338
339       Most contact‐closure UPSes will not power down the  load  if  the  line
340       power  is  present.   This can create a race when using slave upsmon(8)
341       systems.  See the upsmon(8) man page for more information.
342
343       The solution to both of these problems is to upgrade to a smart  proto‐
344       col  UPS  of some kind that allows detection and proper load cycling on
345       command.
346
347

SEE ALSO

349   The core driver:
350       nutupsdrv(8)
351
352
353   Internet resources:
354       The NUT (Network UPS Tools) home page: http://www.networkupstools.org/
355
356
357
358                                Thu Aug 11 2005                  GENERICUPS(8)