DESCRIPTION

17       upsmon is the client process that is responsible for the most important
18       part of UPS monitoring ‐ shutting down the system when the  power  goes
19       out.   It  can  call out to other helper programs for notification pur‐
20       poses during power events.
21
22       upsmon can monitor multiple systems using a single process.  Every  UPS
23       that  is defined in the upsmon.conf(5) configuration file is assigned a
24       power value and a type (slave or master).
25
26

OPTIONS

28       -h     Display the help message.
29
30
31       -c command
32              Send the command command to the existing upsmon process.   Valid
33              commands are:
34
35              fsd ‐ shutdown all master UPSes (use with caution)
36
37              stop ‐ stop monitoring and exit
38
39              reload ‐ reread upsmon.conf(5) configuration file.  See "reload‐
40              ing nuances" below if this doesn't work.
41
42
43       -D     Raise the debugging level.  upsmon will run  in  the  foreground
44              and  prints  information on stdout about the monitoring process.
45              Use this multiple times for more details.
46
47
48       -K     Test for the shutdown flag.  If it exists and contains the magic
49              string  from  upsmon,  then  upsmon will exit with EXIT_SUCCESS.
50              Any other condition will make upsmon exit with EXIT_FAILURE.
51
52              You can test for a successful exit from upsmon -K in your  shut‐
53              down  scripts to know when to call upsdrvctl(8) to shut down the
54              UPS.
55
56
57       -p     Run privileged all the time.  Normally upsmon  will  split  into
58              two processes.  The majority of the code runs as an unprivileged
59              user, and only a tiny stub runs as root.  This switch will  dis‐
60              able that mode, and run the old "all root all the time" system.
61
62              This  is  not  the recommended mode, and you should not use this
63              unless you have a very good reason.
64
65
66       -u user
67              Set the user for the unprivileged monitoring process.  This  has
68              no effect when using -p.
69
70              The  default  user  is  set  at  configure  time with 'configure
71              --with-user=...'.  Typically this is 'nobody', but other distri‐
72              butions  will probably have a specific 'nut' user for this task.
73              If your notification scripts need to run as a specific user, set
74              it here.
75
76              You  can  also  set  this  in  the  upsmon.conf(5) file with the
77              RUN_AS_USER directive.
78
79

UPS DEFINITIONS

81       In the upsmon.conf(5), you must specify at least one UPS that  will  be
82       monitored.  Use the MONITOR directive.
83
84            MONITOR system powervalue username password type
85
86       The  system  refers  to  a  upsd(8)  server,  in the form upsname@host‐
87       name[:port].  Some examples follow:
88
89        ‐ "su700@mybox" means a UPS called "su700" on a system called "mybox".
90       This is the normal form.
91
92        ‐  "fenton@bigbox:5678"  is  a  UPS called "fenton" on a system called
93       "bigbox" which runs upsd(8) on port "5678".
94
95       The powervalue refers to how many power supplies  on  this  system  are
96       being driven this UPS.  This is typically set to 1, but see the section
97       on power values below.
98
99       The username is a section in your upsd.users(5) file.   Whatever  pass‐
100       word you set in that section must match the password set in this file.
101
102       The  type set in that section must also match the type here ‐ master or
103       slave.  In general, a master process is one running on the system  with
104       the  UPS  actually  plugged  into a serial port, and a slave is drawing
105       power from the UPS but can't talk to it directly.  See the  section  on
106       UPS types for more.
107
108

NOTIFY EVENTS

110       upsmon  senses several events as it monitors each UPS.  They are called
111       notify events as they can be used to tell the users  and  admins  about
112       the change in status.  See the additional NOTIFY‐related sections below
113       for information on customizing the delivery of these messages.
114
115
116       ONLINE The UPS is back on line.
117
118
119       ONBATT The UPS is on battery.
120
121
122       LOWBATT
123              The UPS battery is low (as determined by the driver).
124
125
126       FSD    The UPS has been commanded into the "forced shutdown" mode.
127
128
129       COMMOK Communication with the UPS has been established.
130
131
132       COMMBAD
133              Communication with the UPS was just lost.
134
135
136       SHUTDOWN
137              The local system is being shut down.
138
139
140       REPLBATT
141              The UPS needs to have its battery replaced.
142
143
144       NOCOMM The UPS can't be contacted for monitoring.
145
146

NOTIFY COMMAND

148       In upsmon.conf(5), you can configure a  program  called  the  NOTIFYCMD
149       that will handle events that occur.
150
151            NOTIFYCMD "path to program"
152
153            NOTIFYCMD "/usr/local/bin/notifyme"
154
155       Remember to wrap the path in "quotes" if it contains any spaces.
156
157       The program you run as your NOTIFYCMD can use the environment variables
158       NOTIFYTYPE and UPSNAME to know what has happened and on which UPS.   It
159       also  receives  the  notification message (see below) as the first (and
160       only) argument, so you can deliver a preformatted message too.
161
162       Note that the NOTIFYCMD will only be called for a given event when  you
163       set the EXEC flag by using the notify flags, below:
164
165

NOTIFY FLAGS

167       By  default,  all  notify  events (see above) generate a global message
168       (wall) to all users, plus they are logged  via  the  syslog.   You  can
169       change this with the NOTIFYFLAG directive in the configuration file:
170
171            NOTIFYFLAG notifytype flags
172
173            Examples:
174
175            NOTIFYFLAG ONLINE SYSLOG
176
177            NOTIFYFLAG ONBATT SYSLOG+WALL
178
179            NOTIFYFLAG LOWBATT SYSLOG+WALL+EXEC
180
181       The flags that can be set on a given notify event are:
182
183
184       SYSLOG Write this message to the syslog.
185
186
187       WALL   Send this message to all users on the system via 'wall'.
188
189
190       EXEC   Execute the NOTIFYCMD.
191
192
193       IGNORE Don't  do anything.  If you use this, don't use any of the other
194              flags.
195
196       You can mix these flags.  "SYSLOG+WALL+EXEC" does all three for a given
197       event.
198
199

NOTIFY MESSAGES

201       upsmon  comes  with  default  messages  for  each of the NOTIFY events.
202       These can be changed with the NOTIFYMSG directive.
203
204            NOTIFYMSG type "message"
205
206            Examples:
207
208            NOTIFYMSG ONLINE "UPS %s is getting line power"
209
210            NOTIFYMSG ONBATT "Someone pulled the plug on %s"
211
212       The first instance of %s is replaced with the  identifier  of  the  UPS
213       that  generated  the event.  These messages are used when sending walls
214       to the users directly from upsmon, and are also passed to  the  NOTIFY‐
215       CMD.
216
217

POWER VALUES

219       The "current overall power value" is the sum of all UPSes that are cur‐
220       rently able to supply power to the system hosting upsmon.  Any UPS that
221       is  either on line or just on battery contributes to this number.  If a
222       UPS is critical (on battery and low  battery)  or  has  been  put  into
223       "forced shutdown" mode, it no longer contributes.
224
225       A  "power  value" on a MONITOR line in the config file is the number of
226       power supplies that the UPS runs on the current system.
227
228            MONITOR upsname powervalue username password type
229
230       Normally, you only have one power supply, so it will be set to 1.
231
232            MONITOR myups@myhost 1 username mypassword master
233
234       On a large server with redundant power supplies, the power value for  a
235       UPS  may  be  greater  than 1.  You may also have more than one of them
236       defined.
237
238            MONITOR ups-alpha@myhost 2 username mypassword master
239
240            MONITOR ups-beta@myhost 2 username mypassword master
241
242       You can also set the power value for a UPS to 0 if it does  not  supply
243       any  power to that system.  This is generally used when you want to use
244       the upsmon notification features for a UPS even though it's  not  actu‐
245       ally  running the system that hosts upsmon.  Don't set this to "master"
246       unless you really want to power this UPS  off  when  this  instance  of
247       upsmon needs to shut down for its own reasons.
248
249            MONITOR faraway@anotherbox 0 username mypassword slave
250
251       The  "minimum power value" is the number of power supplies that must be
252       receiving power in order to keep the computer running.
253
254            MINSUPPLIES value
255
256       Typical PCs only have 1, so most users will leave this at the default.
257
258            MINSUPPLIES 1
259
260       If you have a server or similar system with redundant power, then  this
261       value  will  usually be set higher.  One that requires three power sup‐
262       plies to be running at all times would simply set it to 3.
263
264            MINSUPPLIES 3
265
266       When the current overall power value  drops  below  the  minimum  power
267       value,  upsmon starts the shutdown sequence.  This design allows you to
268       lose some of your power supplies in a redundant power environment with‐
269       out  bringing  down  the entire system while still working properly for
270       smaller systems.
271
272

UPS TYPES

274       upsmon and upsd(8) don't always run on the same system.  When they  do,
275       any UPSes that are directly attached to the upsmon host should be moni‐
276       tored in "master" mode.  This makes upsmon take charge of  that  equip‐
277       ment,  and  it  will wait for slaves to disconnect before shutting down
278       the local system.  This allows the distant systems (monitoring over the
279       network)  to shut down cleanly before upsdrvctl shutdown runs and turns
280       them all off.
281
282       When upsmon runs as a slave, it is relying on  the  distant  system  to
283       tell  it  about  the state of the UPS.  When that UPS goes critical (on
284       battery and low battery), it immediately  invokes  the  local  shutdown
285       command.   This  needs to happen quickly.  Once it disconnects from the
286       distant upsd(8) server, the master upsmon will start its  own  shutdown
287       process.   Your  slaves  must all shut down before the master turns off
288       the power or filesystem damage may result.
289
290       upsmon deals with slaves that get wedged, hang, or  otherwise  fail  to
291       disconnect  from  upsd(8)  in  a timely manner with the HOSTSYNC timer.
292       During a shutdown situation, the master upsmon will give up after  this
293       interval and it will shut down anyway.  This keeps the master from sit‐
294       ting there forever (which would endanger that host) if a  slave  should
295       break somehow.  This defaults to 15 seconds.
296
297       If  your master system is shutting down too quickly, set the FINALDELAY
298       interval to something greater than the default 15 seconds.   Don't  set
299       this too high, or your UPS battery may run out of power before the mas‐
300       ter upsmon process shuts down that system.
301
302

TIMED SHUTDOWNS

304       For those rare situations where the shutdown process can't be completed
305       between  the  time  that  low battery is signalled and the UPS actually
306       powers off the load, use the upssched(8) helper program.  You  can  use
307       it  along  with upsmon to schedule a shutdown based on the "on battery"
308       event.  upssched can then come back to upsmon to initiate the  shutdown
309       once it's run on battery too long.
310
311       This can be complicated and messy, so stick to the default critical UPS
312       handling if you can.
313
314

REDUNDANT POWER SUPPLIES

316       If you have more than one power supply for  redundant  power,  you  may
317       also  have  more than one UPS feeding your computer.  upsmon can handle
318       this.  Be sure to set the UPS power values appropriately and  the  MIN‐
319       SUPPLIES  value  high  enough  so that it keeps running until it really
320       does need to shut down.
321
322       For example, the HP NetServer LH4  by  default  has  3  power  supplies
323       installed, with one bay empty.  It has two power cords, one per side of
324       the box.  This means that one power cord powers two power supply  bays,
325       and that you can only have two UPSes supplying power.
326
327       Connect  UPS  "alpha"  to  the cord feeding two power supplies, and UPS
328       "beta" to the cord that feeds the third and  the  empty  slot.   Define
329       alpha  as  a  powervalue  of 2, and beta as a powervalue of 1.  Set the
330       MINSUPPLIES to 2.
331
332       When alpha goes on battery, your current overall power value will  stay
333       at  3,  as  it's still supplying power.  However, once it goes critical
334       (on battery and low battery), it will stop contributing to the  current
335       overall  power  value.   That  means  the value will be 1 (beta alone),
336       which is less than 2.  That is insufficient  to  run  the  system,  and
337       upsmon will invoke the shutdown sequence.
338
339       However,  if beta goes critical, subtracting its contribution will take
340       the current overall value from 3 to 2.  This is  just  high  enough  to
341       satisfy the minimum, so the system will continue running as before.  If
342       beta returns later, it will be re‐added and the current value  will  go
343       back  to 3.  This allows you to swap out UPSes, change a power configu‐
344       ration, or whatever, as long as you maintain the minimum power value at
345       all times.
346
347

MIXED OPERATIONS

349       Besides  being  able to monitor multiple UPSes, upsmon can also monitor
350       them as different roles.  If you have a system with multiple power sup‐
351       plies  serviced by separate UPS batteries, it's possible to be a master
352       on one and a slave on the other.  This usually happens when you run out
353       of  serial  ports  and need to do the monitoring through another system
354       nearby.
355
356       This is also complicated, especially when it comes time to power down a
357       UPS  that  has  gone critical but doesn't supply the local system.  You
358       can do this with some scripting magic in your  notify  command  script,
359       but it's beyond the scope of this manual.
360
361

FORCED SHUTDOWNS

363       When upsmon is forced to bring down the local system, it sets the "FSD"
364       (forced shutdown) flag on any UPSes that it is running in master  mode.
365       This  is used to synchronize slaves in the event that a master UPS that
366       is otherwise OK needs to be brought down due to some pressing event  on
367       the master.
368
369       You  can  manually  invoke  this  mode on the master upsmon by starting
370       another copy with '-c fsd'.  This is useful when you want to initiate a
371       shutdown before the critical stage through some external means, such as
372       upssched(8).
373
374

DEAD UPSES

376       In the event that upsmon can't reach  upsd(8),  it  declares  that  UPS
377       "dead"   after   some   interval   controlled   by   DEADTIME   in  the
378       upsmon.conf(5).  If this happens while that UPS was last known to be on
379       battery,  it is assumed to have gone critical and no longer contributes
380       to the overall power value.
381
382       upsmon will alert you to a UPS that can't be contacted  for  monitoring
383       with  a  "NOCOMM"  notifier  by default every 300 seconds.  This can be
384       changed with the NOCOMMWARNTIME setting.
385
386

RELOADING NUANCES

388       upsmon usually gives up root powers for the process that does  most  of
389       the work, including handling signals like SIGHUP to reload the configu‐
390       ration file.  This means your upsmon.conf(8) file must be  readable  by
391       the non‐root account that upsmon switches to.
392
393       If you want reloads to work, upsmon must run as some user that has per‐
394       missions to read the configuration file.  I recommend making a new user
395       just  for  this  purpose,  as making the file readable by "nobody" (the
396       default user) would be a bad idea.
397
398       See the RUN_AS_USER section in upsmon.conf(8) for more on this topic.
399
400       Additionally, you can't change the SHUTDOWNCMD or POWERDOWNFLAG defini‐
401       tions  with  a  reload  due  to the split‐process model.  If you change
402       those values, you must stop upsmon and start it back up.   upsmon  will
403       warn  you  in  the syslog if you make changes to either of those values
404       during a reload.
405
406

SIMULATING POWER FAILURES

408       To test a synchronized  shutdown  without  pulling  the  plug  on  your
409       UPS(es), you need only set the forced shutdown (FSD) flag on them.  You
410       can do this by calling upsmon again to set the flag ‐ i.e.:
411
412            upsmon -c fsd
413
414       After that, the master and the slaves  will  do  their  usual  shutdown
415       sequence  as  if the battery had gone critical.  This is much easier on
416       your UPS equipment, and it beats crawling under  a  desk  to  find  the
417       plug.
418
419

FILES

421       upsmon.conf(5)
422
423

SEE ALSO

425   Server:
426       upsd(8)
427
428
429   Clients:
430       upsc(8), upscmd(8), upsrw(8), upsmon(8)
431
432
433   CGI programs:
434       upsset.cgi(8), upsstats.cgi(8), upsimage.cgi(8)
435
436
437   Internet resources:
438       The NUT (Network UPS Tools) home page: http://www.networkupstools.org/
439
440
441
442                                Wed Nov 26 2003                      UPSMON(8)
Impressum