1BELKINUNV(8) NUT Manual BELKINUNV(8)
2
3
4
6 belkinunv - Driver for Belkin "Universal UPS" and compatible
7
9 This man page only documents the hardware-specific features of the
10 belkin driver. For information about the core driver, see nutupsdrv(8).
11
13 The belkinunv driver is known to work with the Belkin Universal UPS
14 models F6C800-UNV and F6C120-UNV, and is expected to work with other
15 Belkin Universal UPS models. The driver only supports serial
16 communication, not USB.
17
18 The Trust UPS and older Belkin units are not supported by this driver,
19 and neither are the Belkin Home Office models (F6H500-SER and so
20 forth). However, some Belkin models, such as the Regulator Pro, are
21 supported by the belkin(8) driver, and the Home Office models are
22 supported using the genericups(8) driver with upstype=7.
23
25 One problem with the Belkin Universal UPS is that it cannot enter a
26 soft shutdown (shut down the load until AC power returns) unless the
27 batteries are completely depleted. Thus, one cannot just shut off the
28 UPS after operating system shutdown; it will not come back on when the
29 power comes back on. Therefore, the belkinunv driver should never be
30 used with the -k option. Instead, the -x wait option is provided as a
31 workaround.
32
33 When called with the -x wait option, belkinunv behaves as a standalone
34 program (i.e., it does not fork into the background). It performs one
35 simple task: it connects to the UPS, waits for AC power to return, and
36 then exits with status 0.
37
38 This is meant to be used in a shutdown script as follows: during a
39 shutdown, after all filesystems have been remounted read-only, and just
40 before the system would normally be halted: check /etc/killpower (or
41 similar) to see if this shutdown was caused by upsmon(8), and if yes,
42 call belkinunv -x wait. If AC power comes back on, belkinunv exits, and
43 things should be arranged so that the system reboots in this case. If
44 AC power does not come back on, the UPS will eventually run out of
45 batteries, kill the computer’s power supply, and go into soft shutdown
46 mode, which means everything will reboot properly when the power
47 returns. In either case, a deadlock is avoided.
48
49 In addition, if an optional integer argument is given to the -x wait
50 option, this causes belkinunv to wait not only for AC power to be
51 present, but also for the battery charge to reach the given level. I
52 use this as part of my startup scripts, to ensure that the batteries
53 are sufficiently charged before the computer continues booting. This
54 should be put very early in the startup script, before any filesystems
55 are mounted read/write, and before any filesystem checks are performed.
56
57 Several other -x options are provided to fine-tune this behavior. See
58 the options below for detailed descriptions. See the examples below for
59 examples of how to use belkinunv in shutdown and startup scripts.
60
62 See also nutupsdrv(8) for generic options. Never use the -k option with
63 this driver; it does not work properly.
64
65 -x wait[=level]
66 When this option is used, belkinunv does not fork into the
67 background, but behaves as a standalone program. It connects to the
68 UPS and waits until AC power is present. If level is specified, it
69 also waits until the battery charge reaches at least the given
70 level in percent. Then, and only then, belkinunv exits. In
71 addition, while belkinunv runs in this mode, it displays a status
72 line with information on the UPS status and battery level. This is
73 intended for use in the computer’s shutdown and startup scripts, as
74 described under Soft Shutdown Workaround above.
75
76 -x nohang
77 This option only has an effect when used in conjunction with the -x
78 wait option. It causes belkinunv to exit if a connection with the
79 UPS cannot be established or is lost, instead of retrying forever,
80 which is the default behavior. The -x nohang option should be used
81 in a startup script, to ensure the computer remains bootable even
82 if the UPS has been disconnected during the power failure (for
83 instance, you attached your computer to a generator, carried it to
84 a neighbor’s house, or whatever).
85
86 -x flash
87 This option only has an effect when used in conjunction with the -x
88 wait option. It causes the UPS load to be shut off for a short time
89 ("flashed") just after the AC power has returned and the requested
90 battery level (if any) has been attained. This is useful if slaves
91 are attached to this UPS; the flash will cause all of them to
92 reboot. Note that, due to the design of the Belkin UPS hardware,
93 the load shutdown lasts ca. 1—2 minutes; a shorter flash cannot be
94 performed reliably. Also, the computers will reboot at the
95 scheduled time, on battery power if necessary, even if AC power
96 fails again in the meantime. This should not be a problem, as your
97 startup scripts can catch this situation.
98
99 -x silent
100 This option only has an effect when used in conjunction with the -x
101 wait option. It suppresses the status line which belkinunv would
102 normally print.
103
104 -x dumbterm
105 This option only has an effect when used in conjunction with the -x
106 wait option. It changes the way in which belkinunv prints its
107 status line. Normally, terminal control sequences are used to
108 overwrite the same line with new status information, each time the
109 status is updated. This may not work on all terminals. If the -x
110 dumbterm option is given, each status update is written on a new
111 line.
112
114 battery.charge, battery.runtime
115 not supported by all hardware.
116
117 battery.voltage, battery.voltage.nominal, input.frequency,
118 input.frequency.nominal
119 e.g. 60 for 60Hz
120
121 input.sensitivity
122 writable: normal/medium/low
123
124 input.transfer.high
125 writable: high transfer voltage point in V
126
127 input.transfer.low
128 writable: low transfer voltage point in V
129
130 input.voltage, input.voltage.maximum, input.voltage.minimum,
131 input.voltage.nominal, output.frequency, output.voltage,
132 ups.beeper.status
133 writable. Values: enabled/disabled/muted. This variable controls
134 the state of the panel beeper. Enabled means sound when the alarm
135 is present, disabled means never sound, and muted means the sound
136 is temporarily disabled until the alarm would normally stop
137 sounding. In the muted state, the beeper is automatically turned
138 back on at the next event (AC failure, battery test, etc). Also,
139 the beeper can’t be turned off during a critical event (low
140 battery). Note that not all UPS models support the "disabled"
141 state.
142
143 ups.firmware, ups.load, ups.model, ups.power.nominal
144 e.g. 800 for an 800VA system
145
146 ups.status
147 a list of flags; see the status flags below.
148
149 ups.temperature
150 not supported by all hardware.
151
152 ups.test.result, ups.delay.restart
153 time to restart (read only)
154
155 ups.delay.shutdown
156 time to shutdown (read only). This is always a multiple of 60
157 seconds.
158
159 ups.type
160 ONLINE/OFFLINE/LINEINT. This describes the basic layout of this UPS
161 (for GUI clients which want to draw an animated picture of power
162 flow). An offline UPS has a direct connection from AC input to AC
163 output, and also a connection from AC input to the battery, and
164 from the battery to AC output. An online UPS lacks the direct
165 connection from AC input to AC output, whereas a line interactive
166 UPS lacks the connection from AC input to the battery.
167
169 beeper.enable, beeper.disable, beeper.mute
170 Enable, disable or mute the panel beeper. Note that if the beeper
171 is muted, it is automatically turned back on at the next event (AC
172 failure, battery test, etc). Also, the beeper can’t be turned muted
173 during a critical event (low battery).
174
175 reset.input.minmax
176 Reset the variables input.voltage.minimum and
177 input.voltage.maximum.
178
179 shutdown.reboot
180 Shut down load immediately for about 1—2 minutes.
181
182 shutdown.reboot.graceful
183 After 40 second delay, shut down load for about 1—2 minutes.
184
185 shutdown.stayoff
186 Shut down load immediately and stay off. The only way it can be
187 turned back on is by manually pressing the front panel button.
188
189 test.battery.start, test.battery.stop
190 Start/stop 10 second battery test.
191
192 test.failure.start, test.failure.stop
193 Start/stop "deep" battery test.
194
196 OB
197 load is on battery, including during tests
198
199 OFF
200 load is off
201
202 OL
203 load is online
204
205 ACFAIL
206 AC failure. Note that this refers to the AC input, and thus it is
207 not the same as "OB". An AC failure can occur at any time, for
208 instance, during a battery test, or when the UPS load is off.
209
210 OVER
211 overload
212
213 OVERHEAT
214 overheat
215
216 COMMFAULT
217 UPS fault
218
219 LB
220 low battery
221
222 CHRG
223 charging
224
225 DEPLETED
226 the battery is depleted. When the UPS raises this flag, it
227 simultaneously switches off the load.
228
229 RB
230 replace battery
231
233 Here is an example for how belkinunv should be used in a computer’s
234 shutdown script. These commands should go in the very last part of the
235 shutdown script, after all file systems have been mounted read-only,
236 and just before the computer halts. Note that belkinunv must be
237 installed in a directory which is still readable at that point.
238
239 # NEAR END OF SHUTDOWN SCRIPT:
240 # if shutdown was caused by UPS, perform Belkin UPS workaround.
241 if [ -f /etc/killpower ] ; then
242 echo "Waiting for AC power, or for UPS batteries to run out..."
243 /usr/bin/belkinunv -x wait /dev/ttyS1
244
245 # we get here if the power came back on. Reboot.
246 echo "Power is back. Rebooting..."
247 reboot
248 fi
249
250 And here is an example of how to use belkinunv in the startup script.
251 These commands should go near the beginning of the startup script,
252 before any file systems are mounted read/write, and before any file
253 system integrity checks are done.
254
255 # NEAR BEGINNING OF STARTUP SCRIPT:
256 # if we are recovering from a power failure, wait for the UPS to
257 # charge to a comfortable level before writing anything to disk
258 if [ -f /etc/killpower ] ; then
259 echo "Waiting for UPS battery charge to reach 60%..."
260 /usr/bin/belkinunv -x wait=60 -x nohang /dev/ttyS1
261 fi
262
264 When used normally, belkinunv forks into the background and its
265 diagnostics are the same as for all NUT drivers, see nutupsdrv(8).
266
267 When used with the -x wait option, the exit status is normally 0. If
268 the -x nohang option has also been specified, an exit status of 1
269 indicates that communication with the UPS was lost. If the -x flash
270 option has been specified, an exit status of 2 indicates that the timed
271 shutdown has failed.
272
274 This driver does not support any extra settings in ups.conf(5).
275
277 The core driver:
278 nutupsdrv(8)
279
280 Internet resources:
281 · The NUT (Network UPS Tools) home page:
282 http://www.networkupstools.org/
283
284 · The documentation for the protocol used by this UPS:
285 belkin-universal-ups.html
286
288 Peter Selinger <selinger@users.sourceforge.net>
289
290
291
292Network UPS Tools 2.7.3. 12/29/2015 BELKINUNV(8)