11
12 This driver only supports serial connections. If your UPS has a USB
13 port, please consult the Hardware Compatibility List (HCL) to see which
14 of the USB drivers you should use.
15
17 The belkinunv driver is known to work with the Belkin Universal UPS
18 models F6C800-UNV and F6C120-UNV, and is expected to work with other
19 Belkin Universal UPS models. The driver only supports serial
20 communication, not USB.
21
22 The Trust UPS and older Belkin units are not supported by this driver,
23 and neither are the Belkin Home Office models (F6H500-SER and so
24 forth). However, some Belkin models, such as the Regulator Pro, are
25 supported by the belkin(8) driver, and the Home Office models are
26 supported using the genericups(8) driver with upstype=7.
27
29 One problem with the Belkin Universal UPS is that it cannot enter a
30 soft shutdown (shut down the load until AC power returns) unless the
31 batteries are completely depleted. Thus, one cannot just shut off the
32 UPS after operating system shutdown; it will not come back on when the
33 power comes back on. Therefore, the belkinunv driver should never be
34 used with the -k option. Instead, the -x wait option is provided as a
35 workaround.
36
37 When called with the -x wait option, belkinunv behaves as a standalone
38 program (i.e., it does not fork into the background). It performs one
39 simple task: it connects to the UPS, waits for AC power to return, and
40 then exits with status 0.
41
42 This is meant to be used in a shutdown script as follows: during a
43 shutdown, after all filesystems have been remounted read-only, and just
44 before the system would normally be halted: check /etc/killpower (or
45 similar) to see if this shutdown was caused by upsmon(8), and if yes,
46 call belkinunv -x wait. If AC power comes back on, belkinunv exits, and
47 things should be arranged so that the system reboots in this case. If
48 AC power does not come back on, the UPS will eventually run out of
49 batteries, kill the computer’s power supply, and go into soft shutdown
50 mode, which means everything will reboot properly when the power
51 returns. In either case, a deadlock is avoided.
52
53 In addition, if an optional integer argument is given to the -x wait
54 option, this causes belkinunv to wait not only for AC power to be
55 present, but also for the battery charge to reach the given level. I
56 use this as part of my startup scripts, to ensure that the batteries
57 are sufficiently charged before the computer continues booting. This
58 should be put very early in the startup script, before any filesystems
59 are mounted read/write, and before any filesystem checks are performed.
60
61 Several other -x options are provided to fine-tune this behavior. See
62 the options below for detailed descriptions. See the examples below for
63 examples of how to use belkinunv in shutdown and startup scripts.
64
66 See also nutupsdrv(8) for generic options. Never use the -k option with
67 this driver; it does not work properly.
68
69 -x wait[=level]
70 When this option is used, belkinunv does not fork into the
71 background, but behaves as a standalone program. It connects to the
72 UPS and waits until AC power is present. If level is specified, it
73 also waits until the battery charge reaches at least the given
74 level in percent. Then, and only then, belkinunv exits. In
75 addition, while belkinunv runs in this mode, it displays a status
76 line with information on the UPS status and battery level. This is
77 intended for use in the computer’s shutdown and startup scripts, as
78 described under Soft Shutdown Workaround above.
79
80 -x nohang
81 This option only has an effect when used in conjunction with the -x
82 wait option. It causes belkinunv to exit if a connection with the
83 UPS cannot be established or is lost, instead of retrying forever,
84 which is the default behavior. The -x nohang option should be used
85 in a startup script, to ensure the computer remains bootable even
86 if the UPS has been disconnected during the power failure (for
87 instance, you attached your computer to a generator, carried it to
88 a neighbor’s house, or whatever).
89
90 -x flash
91 This option only has an effect when used in conjunction with the -x
92 wait option. It causes the UPS load to be shut off for a short time
93 ("flashed") just after the AC power has returned and the requested
94 battery level (if any) has been attained. This is useful if slaves
95 are attached to this UPS; the flash will cause all of them to
96 reboot. Note that, due to the design of the Belkin UPS hardware,
97 the load shutdown lasts ca. 1—2 minutes; a shorter flash cannot be
98 performed reliably. Also, the computers will reboot at the
99 scheduled time, on battery power if necessary, even if AC power
100 fails again in the meantime. This should not be a problem, as your
101 startup scripts can catch this situation.
102
103 -x silent
104 This option only has an effect when used in conjunction with the -x
105 wait option. It suppresses the status line which belkinunv would
106 normally print.
107
108 -x dumbterm
109 This option only has an effect when used in conjunction with the -x
110 wait option. It changes the way in which belkinunv prints its
111 status line. Normally, terminal control sequences are used to
112 overwrite the same line with new status information, each time the
113 status is updated. This may not work on all terminals. If the -x
114 dumbterm option is given, each status update is written on a new
115 line.
116
118 battery.charge, battery.runtime
119 not supported by all hardware.
120
121 battery.voltage, battery.voltage.nominal, input.frequency,
122 input.frequency.nominal
123 e.g. 60 for 60Hz
124
125 input.sensitivity
126 writable: normal/medium/low
127
128 input.transfer.high
129 writable: high transfer voltage point in V
130
131 input.transfer.low
132 writable: low transfer voltage point in V
133
134 input.voltage, input.voltage.maximum, input.voltage.minimum,
135 input.voltage.nominal, output.frequency, output.voltage,
136 ups.beeper.status
137 writable. Values: enabled/disabled/muted. This variable controls
138 the state of the panel beeper. Enabled means sound when the alarm
139 is present, disabled means never sound, and muted means the sound
140 is temporarily disabled until the alarm would normally stop
141 sounding. In the muted state, the beeper is automatically turned
142 back on at the next event (AC failure, battery test, etc). Also,
143 the beeper can’t be turned off during a critical event (low
144 battery). Note that not all UPS models support the "disabled"
145 state.
146
147 ups.firmware, ups.load, ups.model, ups.power.nominal
148 e.g. 800 for an 800VA system
149
150 ups.status
151 a list of flags; see the status flags below.
152
153 ups.temperature
154 not supported by all hardware.
155
156 ups.test.result, ups.delay.restart
157 time to restart (read only)
158
159 ups.delay.shutdown
160 time to shutdown (read only). This is always a multiple of 60
161 seconds.
162
163 ups.type
164 ONLINE/OFFLINE/LINEINT. This describes the basic layout of this UPS
165 (for GUI clients which want to draw an animated picture of power
166 flow). An offline UPS has a direct connection from AC input to AC
167 output, and also a connection from AC input to the battery, and
168 from the battery to AC output. An online UPS lacks the direct
169 connection from AC input to AC output, whereas a line interactive
170 UPS lacks the connection from AC input to the battery.
171
173 beeper.enable, beeper.disable, beeper.mute
174 Enable, disable or mute the panel beeper. Note that if the beeper
175 is muted, it is automatically turned back on at the next event (AC
176 failure, battery test, etc). Also, the beeper can’t be turned muted
177 during a critical event (low battery).
178
179 reset.input.minmax
180 Reset the variables input.voltage.minimum and
181 input.voltage.maximum.
182
183 shutdown.reboot
184 Shut down load immediately for about 1—2 minutes.
185
186 shutdown.reboot.graceful
187 After 40 second delay, shut down load for about 1—2 minutes.
188
189 shutdown.stayoff
190 Shut down load immediately and stay off. The only way it can be
191 turned back on is by manually pressing the front panel button.
192
193 test.battery.start, test.battery.stop
194 Start/stop 10 second battery test.
195
196 test.failure.start, test.failure.stop
197 Start/stop "deep" battery test.
198
200 OB
201 load is on battery, including during tests
202
203 OFF
204 load is off
205
206 OL
207 load is online
208
209 ACFAIL
210 AC failure. Note that this refers to the AC input, and thus it is
211 not the same as "OB". An AC failure can occur at any time, for
212 instance, during a battery test, or when the UPS load is off.
213
214 OVER
215 overload
216
217 OVERHEAT
218 overheat
219
220 COMMFAULT
221 UPS fault
222
223 LB
224 low battery
225
226 CHRG
227 charging
228
229 DEPLETED
230 the battery is depleted. When the UPS raises this flag, it
231 simultaneously switches off the load.
232
233 RB
234 replace battery
235
237 Here is an example for how belkinunv should be used in a computer’s
238 shutdown script. These commands should go in the very last part of the
239 shutdown script, after all file systems have been mounted read-only,
240 and just before the computer halts. Note that belkinunv must be
241 installed in a directory which is still readable at that point.
242
243 # NEAR END OF SHUTDOWN SCRIPT:
244 # if shutdown was caused by UPS, perform Belkin UPS workaround.
245 if [ -f /etc/killpower ] ; then
246 echo "Waiting for AC power, or for UPS batteries to run out..."
247 /usr/bin/belkinunv -x wait /dev/ttyS1
248
249 # we get here if the power came back on. Reboot.
250 echo "Power is back. Rebooting..."
251 reboot
252 fi
253
254 And here is an example of how to use belkinunv in the startup script.
255 These commands should go near the beginning of the startup script,
256 before any file systems are mounted read/write, and before any file
257 system integrity checks are done.
258
259 # NEAR BEGINNING OF STARTUP SCRIPT:
260 # if we are recovering from a power failure, wait for the UPS to
261 # charge to a comfortable level before writing anything to disk
262 if [ -f /etc/killpower ] ; then
263 echo "Waiting for UPS battery charge to reach 60%..."
264 /usr/bin/belkinunv -x wait=60 -x nohang /dev/ttyS1
265 fi
266
268 When used normally, belkinunv forks into the background and its
269 diagnostics are the same as for all NUT drivers, see nutupsdrv(8).
270
271 When used with the -x wait option, the exit status is normally 0. If
272 the -x nohang option has also been specified, an exit status of 1
273 indicates that communication with the UPS was lost. If the -x flash
274 option has been specified, an exit status of 2 indicates that the timed
275 shutdown has failed.
276
278 This driver does not support any extra settings in ups.conf(5).
279
281 Peter Selinger <selinger@users.sourceforge.net>
282
284 The core driver:
285 nutupsdrv(8)
286
287 Other Belkin drivers:
288 belkinunv(8), blazer_ser(8), blazer_usb(8), usbhid-ups(8)
289
290 Internet resources:
291 • The NUT (Network UPS Tools) home page:
292 http://www.networkupstools.org/
293
294 • The documentation for the protocol used by this UPS:
295 belkin-universal-ups.html (replica on NUT site)