4

NAME

6       usbhid-ups - Driver for USB/HID UPS equipment
7

NOTE

9       This man page only documents the hardware-specific features of the
10       usbhid-ups driver. For information about the core driver, see
11       nutupsdrv(8).
12

SUPPORTED HARDWARE

14       usbhid-ups brings USB/HID UPS monitoring to NUT on all platforms
15       supporting USB through libusb. It should detect any UPS that uses the
16       HID Power Device Class, but the amount of data will vary depending on
17       the manufacturer and model.
18
19       At the present time, usbhid-ups supports:
20
21       •   the newer Eaton USB models,
22
23       •   all MGE USB models,
24
25       •   all Dell USB models,
26
27       •   all AMETEK Powervar UPM models,
28
29       •   some APC models,
30
31       •   some Belkin models,
32
33       •   some Cyber Power Systems models,
34
35       •   some Powercom models,
36
37       •   some PowerWalker models,
38
39       •   some TrippLite models.
40
41       For a more complete list, refer to the NUT hardware compatibility list,
42       available in the source distribution as data/driver.list, or on the NUT
43       website. You may use the "explore" driver option to gather information
44       from HID UPSes which are not yet supported; see below for details.
45
46       This driver is known to work on:
47
48       •   most Linux systems,
49
50       •   FreeBSD (beta stage) and maybe other *BSD,
51
52       •   Darwin / Mac OS X,
53
54       •   Solaris 10.
55

EXTRA ARGUMENTS

57       This driver also supports the following optional settings:
58
59       offdelay=num
60           Set the timer before the UPS is turned off after the kill power
61           command is sent (via the -k switch).
62
63           The default value is 20 (in seconds). Usually this must be lower
64           than ondelay, but the driver will not warn you upon startup if it
65           isn’t.
66
67           Note that many Cyber Power Systems (CPS) models tend to divide this
68           delay by 60 and round down, so the minimum advisable value is 60 to
69           avoid powering off immediately after NUT sends the shutdown command
70           to the UPS.
71
72       ondelay=num
73           Set the timer for the UPS to switch on in case the power returns
74           after the kill power command had been sent, but before the actual
75           switch off. This ensures the machines connected to the UPS are, in
76           all cases, rebooted after a power failure.
77
78           The default value is 30 (in seconds). Usually this must be greater
79           than offdelay, but the driver will not warn you upon startup if it
80           isn’t. Some UPSes will restart no matter what, even if the power is
81           (still) out at the moment this timer elapses. In that case, you
82           could see whether setting ondelay = -1 in ups.conf helps.
83
84           Note that many CPS models tend to divide this delay by 60 and round
85           down, so the minimum advisable value is 120 to allow a short delay
86           between when the UPS shuts down, and when the power returns.
87
88       pollfreq=num
89           Set polling frequency for full updates, in seconds. Compared to the
90           quick updates performed every "pollinterval" (the latter option is
91           described in ups.conf(5)), the "pollfreq" interval is for polling
92           the less-critical variables. The default value is 30 (in seconds).
93
94       pollonly
95           If this flag is set, the driver will not use Interrupt In transfers
96           during the shorter "pollinterval" cycles (not recommended, but
97           needed if these reports are broken on your UPS).
98
99       onlinedischarge
100           If this flag is set, the driver will treat OL+DISCHRG status as
101           offline. For most devices this combination means calibration or
102           similar maintenance; however some UPS models (e.g. CyberPower UT
103           series) emit OL+DISCHRG when wall power is lost — and need this
104           option to handle shutdowns.
105
106       vendor=regex, product=regex, serial=regex, vendorid=regex,
107       productid=regex
108           Select a specific UPS, in case there is more than one connected via
109           USB. Each option specifies an extended regular expression (see
110           regex(7)) that must match the UPS’s entire vendor/product/serial
111           string (minus any surrounding whitespace), or the whole 4-digit
112           hexadecimal code for vendorid and productid. Try -DD for finding
113           out the strings to match.
114
115           Examples:
116
117           •   -x vendor="Foo.Corporation.*"
118
119           •   -x vendorid=051d* (APC)
120
121           •   -x product=".*(Smart|Back)-?UPS.*"
122
123       bus=regex
124           Select a UPS on a specific USB bus or group of buses. The argument
125           is a regular expression that must match the bus name where the UPS
126           is connected (e.g. bus="002", bus="00[2-3]").
127
128       device = regex
129           Select a UPS on a specific USB device or group of devices. The
130           argument is a regular expression that must match the device name
131           where the UPS is connected (e.g. device="001", device="00[1-2]").
132           Note that device numbers are not guaranteed by the OS to be stable
133           across re-boots or device re-plugging.
134
135       explore
136           With this option, the driver will connect to any device, including
137           ones that are not yet supported. This must always be combined with
138           the "vendorid" option. In this mode, the driver will not do
139           anything useful except for printing debugging information
140           (typically used with -DD).
141
142       maxreport
143           With this option, the driver activates a tweak to workaround buggy
144           firmware returning invalid HID report length. Some APC Back-UPS
145           units are known to have this bug.
146
147       interruptonly
148           If this flag is set, the driver will not poll UPS. This also
149           implies using of INPUT flagged objects. Some Powercom units need
150           this option.
151
152       interruptsize=num
153           Limit the number of bytes to read from interrupt pipe. For some
154           Powercom units this option should be equal to 8.
155

INSTALLATION

157       This driver is not built by default. You can build it by using
158       "configure --with-usb=yes". Note that it will also install other USB
159       drivers.
160
161       You also need to install manually the legacy hotplug files (libhidups
162       and libhid.usermap, generally in /etc/hotplug/usb/), or the udev file
163       (nut-usbups.rules, generally in /etc/udev/rules.d/) to address the
164       permission settings problem. For more information, refer to the README
165       file in nut/scripts/hotplug or nut/scripts/udev.
166

IMPLEMENTATION

168   Selecting a specific UPS
169       The driver ignores the "port" value in ups.conf. Unlike previous
170       versions of this driver, it is now possible to control multiple UPS
171       units simultaneously with this driver, provided they can be
172       distinguished by setting some combination of the "vendor", "product",
173       "serial", "vendorid", and "productid" options. For instance:
174
175           [mge]
176                   driver = usbhid-ups
177                   port = auto
178                   vendorid = 0463
179           [tripplite]
180                   driver = usbhid-ups
181                   port = auto
182                   vendorid = 09ae
183
184   USB Polling and Interrupt Transfers
185       The usbhid-ups driver has two polling intervals. The "pollinterval"
186       configuration option controls what can be considered the "inner loop",
187       where the driver polls and waits briefly for "interrupt" reports. The
188       "pollfreq" option is for less frequent updates of a larger set of
189       values, and as such, we recommend setting that interval to several
190       times the value of "pollinterval".
191
192       Many UPSes will respond to a USB Interrupt In transfer with HID reports
193       corresponding to values which have changed. This saves the driver from
194       having to poll each value individually with USB Control transfers.
195       Since the OB and LB status flags are important for a clean shutdown,
196       the driver also explicitly polls the HID paths corresponding to those
197       status bits during the inner "pollinterval" time period. The "pollonly"
198       option can be used to skip the Interrupt In transfers if they are known
199       not to work.
200

KNOWN ISSUES AND BUGS

202   Repetitive timeout and staleness
203       Some models tends to be unresponsive with the default polling
204       frequency. The result is that your system log will have lots of
205       messages like:
206
207           usb 2-1: control timeout on ep0in
208           usb 2-1: usbfs: USBDEVFS_CONTROL failed cmd usbhid-ups rqt 128 rq 6 len 256
209           ret -110
210
211       In this case, simply modify the general parameter "pollinterval" to a
212       higher value (such as 10 seconds). This should solve the issue.
213
214       Note that if you increase "pollinterval" beyond 10 or 15 seconds, you
215       might also want to increase "pollfreq" by the same factor.
216
217   Got EPERM: Operation not permitted upon driver startup
218       You have forgotten to install the hotplug files, as explained in the
219       INSTALLATION section above. Don’t forget to restart hotplug so that it
220       applies these changes.
221
222   Unattended shutdowns
223       The hardware which was used for development of this driver is almost
224       certainly different from what you have, and not all manufacturers
225       follow the USB HID Power Device Class specifications to the letter. You
226       don’t want to find out that yours has issues here when a power failure
227       hits your server room and you’re not around to manually restart your
228       servers.
229
230       If you rely on the UPS to shutdown your systems in case of mains
231       failure and to restart them when the power returns, you must test this.
232       You can do so by running upsmon -c fsd. With the mains present, this
233       should bring your systems down and then cycle the power to restart them
234       again. If you do the same without mains present, it should do the same,
235       but in this case, the outputs shall remain off until mains power is
236       applied again.
237
238   UPS cuts power too soon
239       Note that many Cyber Power Systems (CPS) models tend to divide offdelay
240       by 60 and round down, so the minimum advisable value is 60 (seconds) to
241       avoid powering off immediately after NUT sends the shutdown command to
242       the UPS.
243
244   UPS does not set battery.charge.low but says OK
245       Note that many Cyber Power Systems (CPS) models tend to allow only
246       certain values for battery.charge.low and anything outside of the set
247       of allowed values are rounded or ignored.
248
249       A shell loop like this can help you map out the allowed values:
250
251           for i in `seq 90 -1 0`; do echo "set to $i"; \
252               upsrw -s battery.charge.low=$i -u * -p * cps-big; \
253               sleep 1; upsc cps-big battery.charge.low; echo ""; \
254           done
255
256       For example, for CPS PR1000LCDRTXL2U model, the only allowed values are
257       [60,55,50,45,40,35,30,25,20] and in some cases, your UPS may
258       effectively not support a value of 10 for the battery.charge.low
259       setting.
260

HISTORY

262       This driver, formerly called newhidups, replaces the legacy hidups
263       driver, which only supported Linux systems.
264

AUTHORS

266       Originally sponsored by MGE UPS SYSTEMS.
267
268       Now sponsored by Eaton http://opensource.eaton.com
269
270       •   Arnaud Quette
271
272       •   Peter Selinger
273
274       •   Arjen de Korte
275

SEE ALSO

277   The core driver
278       nutupsdrv(8)
279
280   Internet resources
281       The NUT (Network UPS Tools) home page: http://www.networkupstools.org/
282