1SOLIS(8) NUT Manual SOLIS(8)
2
3
4
6 solis - Driver for Brazilian Microsol SOLIS UPS equipment
7
9 This man page only documents the hardware-specific features of the
10 solis driver. For information about the core driver, see nutupsdrv(8).
11
13 This driver has been tested with :
14
15 · Solis 1000 VA
16
17 · Solis 1500 VA
18
19 · Solis 2000 VA
20
21 · Solis 3000 VA
22
23 · Back-UPS BZ1200-BR
24
25 · Back-UPS BZ2200BI-BR
26
27 All Solis models are sinusoidal on-line.
28
29 In 2009, Schneider Electric acquired Microsol Technologies, and by
30 2012, the entire Microsol line of equipment was being sold under the
31 APC brand.
32
34 This driver support the following extra optional settings in the
35 ups.conf(5).
36
37 battext = n - (default = 0, no extra battery, where n = Ampere*hour )
38
39 prgshut = 1 - (default = 0, no programable shutdown )
40
42 · shutdown.return - Shut down in .3 minutes and restart in .3 minutes
43
44 · shutdown.stayoff - Shut down in .3 minutes and do not return
45
47 The APC version of the Microsol protocol is slightly incompatible with
48 the solis driver. As of version 0.62 of the solis driver, the driver
49 will connect to the UPS, but some values are read incorrectly.
50
52 Silvino B. Magalhães <sbm2yk@gmail.com>
53
55 The core driver:
56 nutupsdrv(8)
57
58 Internet resources:
59 The NUT (Network UPS Tools) home page: http://www.networkupstools.org/
60
61
62
63Network UPS Tools 2.7.3. 12/29/2015 SOLIS(8)