6 powerpanel - Driver for serial PowerPanel Plus compatible UPS equipment
7
9 This man page only documents the hardware-specific features of the
10 powerpanel driver. For information about the core driver, see
11 nutupsdrv(8).
12
14 This driver supports CyberPower BC1200, PR2200 and many other similar
15 devices, both for the text and binary protocols. The driver will
16 autodetect which protocol is used.
17
18 If your Cyber Power Systems UPS has a USB port, you may wish to use the
19 usbhid-ups(8) driver. The snmp-ups(8) driver supports several network
20 cards via SNMP.
21
23 This driver supports the following optional settings in ups.conf(5):
24
25 protocol=[text,binary]
26 Override the default autodetection of the protocol.
27
28 manufacturer=value
29 If you don’t like the autodetected value, you can override this by
30 setting it here.
31
32 model=value
33 Like manufacturer above.
34
35 serial=value
36 Like manufacturer above.
37
38 ondelay=value
39 Time to wait before switching on the UPS (1 - 9999 minutes,
40 0=indefinite). Only available with the text protocol driver (see
41 Support Status).
42
43 offdelay=value
44 Time to wait before shutting down the UPS (6 - 600 seconds). Values
45 below 60 seconds will be truncated to 6 seconds intervals, values
46 above 60 seconds to 60 seconds intervals. Only available with the
47 text protocol driver (see Support Status).
48
50 Depending on the type of your UPS unit, some of the following variables
51 may be changed with upsrw(8). If the driver can’t read a variable from
52 the UPS, it will not be made available.
53
54 input.transfer.high
55 writable: high transfer voltage point in V
56
57 input.transfer.low
58 writable: low transfer voltage point in V
59
60 battery.charge.low
61 writable: remaining battery charge percentage for low battery
62 warning
63
64 output.voltage.nominal
65 writable: nominal output voltage in V
66
67 ups.start.battery
68 writable: allow cold start from battery
69
71 Depending on the type of your UPS unit, some of the following commands
72 may be available.
73
74 • test.battery.start.quick, test.battery.stop
75
76 • beeper.enable, beeper.disable, beeper.toggle
77
78 • shutdown.return, shutdown.reboot, shutdown.stayoff
79
80 On many devices, these commands are unreliable, so before using them
81 you must verify that these work as expected (see Shutdown Issues).
82
83 • shutdown.stop
84
86 Vendor support is absent for this driver, so if you need some features
87 that are currently not available, provide ample documentation on what
88 the driver should sent to the UPS in order to make this work. If more
89 information would be available on the binary protocol, it would
90 probably be possible to make ondelay and offdelay configurable. So far,
91 nobody has taken the time to investigate what we should tell the UPS to
92 make this work, and CyberPower isn’t willing to share this with us.
93
95 If the shutdown.return command on your UPS doesn’t seem to work,
96 chances are that your UPS is an older model. Try a couple of different
97 settings for offdelay. If no value in the range 6..600 works, your UPS
98 likely doesn’t support this. In order to get the expected behaviour, it
99 requires shutdown.stayoff (when on battery) and shutdown.reboot (when
100 on mains). The driver will automatically fallback to these commands if
101 shutdown.return fails, and tries to detect which one should be used
102 when called with the -k option (or through upsdrvctl shutdown).
103
104 This isn’t bullet-proof, however, and you should be prepared that the
105 power will either not be shutdown or that it doesn’t return when the
106 power comes back. All models supported by the binary protocol and many
107 supported through the text protocol are affected by this.
108
110 The CyberPower OP series don’t offer direct voltage, charge, frequency
111 and temperature readings. Instead, they will return a binary value that
112 needs conversion to the actual value.
113
114 The exact conversion needed is unknown at the time of this writing,
115 hence an estimation was made based om readings from actual devices.
116 This may (probably will) be off, possibly a lot. Unless you can tell us
117 the exact mapping between values from the UPS and actual readings,
118 don’t bother to complain. We’ve done the best we can based on the
119 limited information available. Remember, a UPS isn’t a measuring
120 instrument.
121
123 Arjen de Korte <arjen@de-korte.org>, Doug Reynolds <mav@wastegate.net>
124
126 The core driver:
127 nutupsdrv(8)
128
129 Other drivers:
130 usbhid-ups(8), snmp-ups(8)
131