6 netxml-ups - Driver for Eaton / MGE Network Management Card / Proxy
7 (XML/HTTP Protocol) equipment
8
10 This man page only documents the hardware-specific features of the
11 netxml-ups driver. For information about the core driver, see
12 nutupsdrv(8).
13
15 netxml-ups support all recent Eaton / MGE models which use a Network
16 Management Card or Proxy (MGE XML/HTTP protocol based). This applies to
17 both Eaton (previously MGE Office Protection Systems) and to MGE UPS
18 SYSTEMS. Supported card and proxy models are:
19
20 · NMC Minislot (Ref 66102, firmware EA or newer),
21
22 · SNMP/Web Minislot card (Ref 66244)
23
24 · NMC Transverse (Ref 66074),
25
26 · NMC & Modbus/JBus (Ref 66103),
27
28 · Network Management Proxy,
29
30 · ePDU Monitored (newer version).
31
32 Older models, such as SNMP card (Ref 66062 and Ref 66045), use the SNMP
33 protocol and should use the snmp-ups(8) driver with the "mibs=mge"
34 parameter.
35
37 This driver supports the following optional settings in the
38 ups.conf(5):
39
40 timeout=value
41 The timeout for connecting to and reading from the UPS. Defaults to
42 5 seconds. Don’t change this value unless you know exactly what
43 you’re doing.
44
45 This value must never be higher than half the MAXAGE value specified in
46 upsd.conf(5), otherwise you run the risk that upsd(8) declares the
47 driver stale while it is waiting for a connection to timeout.
48
49 login=value
50 Set the login value for authenticated mode. This feature also needs
51 the password argument, and allows value settings in the card. This
52 feature is not used yet.
53
54 password=value
55 Set the password value, needed with the login for authenticated
56 mode. This feature is not used yet.
57
59 The hostname of the UPS is specified with the "port" value in ups.conf,
60 i.e.:
61
62 [mgexml]
63 driver = netxml-ups
64 port = http://netxml-ups.example.com:80
65
66 Specifying the method to connect to the UPS (http, https) is mandatory.
67 If the port is equal to the default for the method specified (80 for
68 http, 443 for https) it may be omitted.
69
70 In order not to overload older NMCs by polling them too frequently, it
71 is recommended to increase the "pollinterval" (see nutupsdrv(8)) and
72 ups.conf(5)) to at least 5 seconds.
73
75 Don’t connect to the UPS through a proxy. Although it would be trivial
76 to add support for proxies, this is not recommended and don’t ask for
77 it. Not only because it will prevent the driver to make a persistent
78 connection to the UPS, but also it adds an additional failure mode. If
79 the proxy goes down (for whatever reason), the driver will no longer be
80 able to reach the UPS.
81
83 Arjen de Korte <adkorte-guest@alioth.debian.org>
84
86 The core driver:
87 nutupsdrv(8)
88
89 Internet resources:
90 The NUT (Network UPS Tools) home page: http://www.networkupstools.org/
91