1APCSMART(8)                       NUT Manual                       APCSMART(8)
2
3
4

NAME

6       apcsmart - Driver for American Power Conversion Smart Protocol UPS
7       equipment
8

SYNOPSIS

10       apcsmart -h
11
12       apcsmart -a 'UPS_NAME' [-x option=value ...]
13
14           Note
15           This man page only documents the hardware-specific features of the
16           apcsmart driver. For information about the core driver, see
17           nutupsdrv(8).
18

SUPPORTED HARDWARE

20       The apcsmart driver should recognize (or at the very least work with)
21       majority of Smart-UPS models - which includes Smart-UPS, Matrix-UPS and
22       Back-UPS lineups, among few other ones.
23
24       Currently we can roughly divide APC hardware into 3 groups (note that
25       the division isn't strict by any means, and the borders between those
26       are pretty fuzzy):
27
28       [very] "old" models
29           These models usually have old APC logo, white color and no
30           programmable eeprom; You won't find them listed anywhere on APC’s
31           site either. The support for those will be usually based on
32           driver's compatibility tables, or if the model (firmware) is not
33           listed in those - the driver will try to follow the very basic
34           subset of features, while still trying to remain useful. Despite
35           "smart" tagname, they often tend to behave in pretty dumb way (see
36           the section below about shutdown behaviour).
37
38           Example models:
39
40           ·   Smart-UPS 2000I
41
42           ·   Smart-UPS 900I
43
44       "new" models
45           These models usually come from late 1990s / pre-2009 times. They
46           are often referred as "3rd. gen". For the most part, they have
47           programmable eeprom, report supported commands and capabilites, and
48           should work just fine with the apcsmart driver.
49
50       "microlink" models
51           WARNING: these are not natively supported by apcsmart (or apcupsd
52           for that matter, if you’re wondering). Around 2007 APC (now APC
53           Schneider) decided to go back to its proprietry roots and all the
54           new models (SMT, SMX, SURTD) use completely different protocol and
55           cables. If you purchased a new APC ups, that uses cable with rj45
56           on the one end, and db-9 on the other - then you have such model.
57           Your only option to support it through NUT is to purchase "legacy
58           communications card" - part #AP9620 (google 'AP9620' for more
59           details). Or if that's not an option, rely on official software.
60
61       Another thing to remember is that Smart protocol is not USB protocol.
62       If you have ups with both USB and serial ports, then depending on how
63       you connect it, you will need either apcsmart or usbhid-ups driver.
64

CABLING

66       This driver expects to see a 940-0024C cable or a clone by default. You
67       can switch to the 940-0095B dual-mode cable support with the 'cable='
68       definition described below.
69
70       If your 940-0024C cable is broken or missing, use this diagram to build
71       a clone:
72
73       http://www.networkupstools.org/cables/940-0024C.jpg
74
75       You can specify alternate cable in ups.conf(5):
76
77       cable=940-0095B
78
79       Alternatively, you can also provide it on the command line using:
80
81       -x cable=940-0095B
82

EXPLANATION OF SHUTDOWN METHODS SUPPORTED BY APC UPSES

84       APC hardware supports a lot of shutdown methods, that themselves can
85       differ in behaviour quite a bit, depending on the model.
86
87       S (soft hibernate)
88           This is most basic command present in probably all APC models. It
89           will hibernate the UPS, and subsequently wake it up when the mains
90           supply returns.  The command doesn't work if UPS is running on
91           mains.
92
93           "old" models
94               The behaviour here is unfortunately pretty primitive - when the
95               power returns, the ups just wakes up. No grace periods, no min.
96               battery charge condition, etc. This is probably not what you
97               want.
98
99           "new" models
100               The behaviour here is as expected - the power is cut off after
101               the eeprom defined grace period. The ups will wake up when the
102               power returns, after the eeprom defined delay AND if the eeprom
103               defined min. battery charge level is met. The delay is counted
104               from the power's return.
105
106       CS (aka "force OB hack")
107           This is a trick to make UPS power down even if it's running on
108           mains. Immediately before issuing S, "simulate power failure" is
109           issued. The remaining behaviour is as in S case.
110
111           The name came from APC CS models, where such trick was used to
112           power down UPSes in consistent fashion using only S. It's better to
113           use @nnn command if your UPS supports it (and is not too old, see
114           below).
115
116       @nnn (hard hibernate)
117           This is basic command used to hibernate UPS regardless if it's
118           running on batteries or on mains. The option takes 3 digits
119           argument which can be used to specify additional wakeup delay (in 6
120           minute units).
121
122           "old" models
123               The behaviour is - unfortunately - similary primitive to S. The
124               ups unconditionally wakes up after nnn*6 minutes - it doesn't
125               care if the power returned !  If nnn = 000, then UPS will do
126               precisely nothing. On those models you're better specifying nnn
127               > 0, if you can estimate the kind of power problems that might
128               be happening in your environment. Another thing to consider
129               with "old" models - you might lose the connection with the ups,
130               until it wakes up (with S, the serial connection is kept
131               alive).
132
133           "new" models
134               All the usual variables defined in eeprom are respected (see
135               S). Additionally, if nnn > 0, the nnn*6 minutes are added to
136               eeprom defined delay. UPS will not power up if it's running on
137               batteries, contrary to what "old" models used to do - the
138               combined delay is counted from the moment of power return.
139
140           Supposedly there exist models that take 2 digits instead of 3. Just
141           in case, NUT also supports such variation. You have to provide
142           exactly 2 digits to trigger it (awd option, or argument to one of
143           the supported instant commands).
144
145       K (delayed poweroff)
146           This is permanent poweroff - the ups will not wake up
147           automatically. On newer units, it will respect applicable eeprom
148           variables.
149
150       Z (instant poweroff)
151           This is also permanent poweroff - the ups will not wake up
152           automatically. The poweroff is executed immediately.
153

SHUTDOWN CONTROL BY NUT

155       There're 3 options used to control shutdown behaviour.
156
157       sdtype=[0-5]
158           This option takes a single digit (0-5) as an argument. See below
159           for details.
160
161       advorder=no|[0-4]+
162           This option takes string of digits as an argument. Methods listed
163           are tried in turn until one of them succeedes. Note that the
164           meaning of digits is different from sdtype. See below for details.
165
166       awd=[0-9]{1,3}
167           This option lets you specify additional wakeup delay used by @. If
168           you provide exactly 2 digits, the driver will try 2 digits
169           variation (see previous section for more info). Otherwise standard
170           3 digits variation is used.  Note: the time unit is 6 minutes !
171
172       Keep in mind that sdtype and advorder are mutually exclusive. If
173       advorder is provided, sdtype is ignored. If advorder is set to 'no',
174       sdtype is used instead.
175
176       If nothing is provided, NUT will assume sdtype=0 - which is generally
177       fine for anything not too ancient or not too quirky.
178
179   SDTYPE
180       The values permitted are from 0 to 5. Only one can be specified.
181       Anything else will cause apcsmart to exit.
182
183       0
184           issue soft hibernate (S) if the ups is running on batteries,
185           otherwise issue hard hibernate (@)
186
187       1
188           issue soft hibernate (S) (if on batteries), and if it fails (or on
189           mains) - try hard hibernate (@)
190
191       2
192           issue instant poweroff (Z)
193
194       3
195           issue delayed poweroff (K)
196
197       4
198           issue "force OB hack" (CS)
199
200       5
201           issue hard hibernate (@)
202
203           Note
204           Hard hibernate's additional wakeup delay can be provided by awd.
205
206   ADVORDER
207       The argument is either a word 'no', or a string of 1 - 5 digits in [0 -
208       4] range. Each digit maps to the one of shutdown methods supported by
209       APC upses. Methods listed in this way are tried in order, until one of
210       them succedes.
211
212       If advorder is undefined or set to 'no', sdtype is used instead.
213
214       The mapping is as follows:
215
216
217       0   soft hibernate (S)
218
219       1   hard hibernate (@)
220
221       2   delayed poweroff (K)
222
223       3   instant poweroff (Z)
224
225       4   "force OB hack" (CS)
226
227
228           Note
229           Hard hibernate's additional wakeup delay can be provided by awd.
230

IGNORING LB STATE

232       APC units - even if they report LB mode - will not go into shutdown
233       automatically. This gives us even more control with reference to "when
234       to actually shutdown psu". Since version 2.6.2, NUT supports ignorelb
235       option in driver's section of ups.conf(5). When such option is in
236       effect, the core driver will ignore LB state as reported by specific
237       driver and start shutdown basing the decision only on two conditions:
238
239       battery.charge < battery.charge.low
240
241       OR
242
243       battery.runtime < battery.runtime.low
244
245       Of course - if any of the variables are not available, the appropriate
246       condition is not checked. If you want to explicitly disable one of the
247       conditions, simply override the right hand variable causing the
248       condition to always evaluate to false (you can even provide negative
249       numbers).
250
251       APC upses don't have battery.charge.low - you will have to define it if
252       you want to use such condition (prefix the variable with override. or
253       default.).
254
255       "New" units have battery.runtime.low, but depending on battery quality,
256       firmware version, calibration and ups load - this variable can be
257       underestimated quite a bit - especially right after going into OB
258       state. This in turn can cause LB to be asserted, which under normal
259       conditions will cause NUT to initiate the shutdown. You might want to
260       disable this condition entirely, when relying on ignorelb option (this
261       was actually the main motivation behind introduction of such feature).
262
263       Simple example:
264
265           [apc]
266               ignorelb
267               override.battery.charge.low = 15
268               override.battery.runtime.low = -1
269
270       This would cause apcsmart to go into shutdown only if detected battery
271       charge < 15%. Runtime condition is always false in this example.
272
273       You could ask - why bother ? Well, the reason is already hinted above.
274       APC units can be very picky about the batteries, and their firmware can
275       underestimate the remaining runtime (especially right after going into
276       OB state). ignorelb option and override.* let you remain in control of
277       the ups, not ups in control of you.
278
279       Furthermore, this allows to specify conditions similary to how it’s
280       done in apcupsd daemon, so it should be welcome by people used to that
281       software.
282

SUPPORTED INSTANT COMMANDS

284       The apcsmart driver exposes following instant commands:
285
286       shutdown.return
287           executes soft hibernate
288
289       shutdown.return cs
290           executes "force OB hack"
291
292       shutdown.return at:<nbr>
293           executes "hard hibernate" with <nbr>*6 minutes additional wakeup
294           delay (<nbr> format is the same as of awd option)
295
296       shutdown.stayoff
297           executes "delayed poweroff"
298
299       load.off
300           executes "instant poweroff"
301
302       All the above commands must be issued 2nd time to have any effect (no
303       less than 3 seconds, and no more than 15 seconds after the initial
304       call). Those commands are mostly useful for manual testing, when your
305       machine is not powered by the ups you're testing.
306
307       Other supported commands:
308
309       ·   load.on
310
311       ·   test.panel.start
312
313       ·   test.failure.start
314
315       ·   test.battery.start
316
317       ·   test.battery.stop
318
319       ·   bypass.start
320
321       ·   bypass.stop
322
323       ·   calibrate.start
324
325       ·   calibrate.stop
326

BUGS

328       Some older APC UPS models return bogus data in the status register
329       during a front panel test. This is usually detected and discarded, but
330       some other unexpected values have occasionally slipped through.
331
332       APC UPS models with both USB and serial ports require a power cycle
333       when switching from USB communication to serial, and perhaps vice
334       versa.
335

AUTHOR

337       Nigel Metheringham <Nigel.Metheringham@Intechnology.co.uk> (drawing
338       heavily on the original apcsmart driver by Russell Kroll). This driver
339       was called newapc for a time and was renamed in the 1.5 series. In
340       2.6.2 it was renamed to apcsmart-old, being superseded by updated
341       version with new features, which is maintained by Michal Soltys
342       <soltys@ziu.info>
343

SEE ALSO

345       nutupsdrv(8), ups.conf(5)
346
347   Internet resources:
348       The NUT (Network UPS Tools) home page: http://www.networkupstools.org/
349