1BESTUPS(8)                  Network UPS Tools (NUT)                 BESTUPS(8)
2
3
4

NAME

6       bestups - Driver for Best Power / SOLA (Phoenixtec protocol) UPS equip‐
7       ment
8

NOTE

10       This man page only documents  the  hardware‐specific  features  of  the
11       bestups  driver.   For  information  about the core driver, see nutups‐
12       drv(8).
13
14

SUPPORTED HARDWARE

16       bestups was designed to  monitor  Best  Power  UPS  hardware  like  the
17       Fortress,  Fortress Telecom, Axxium Rackmount and Patriot Pro.  It also
18       recognizes and supports SOLA units such as the 325, 520  and  620.   In
19       addition, the Best 610 is supported using the `ID' option.
20
21       Other  UPS hardware using the Phoenixtec protocol should also work, but
22       they will generate a warning since their  battery  information  is  not
23       known.
24
25       This driver does not support some older Best/SOLA units.
26
27

EXTRA ARGUMENTS

29       This   driver   supports   the   following  optional  settings  in  the
30       ups.conf(5):
31
32
33       nombattvolt=num
34
35              Override the nominal battery voltage which  is  normally  deter‐
36              mined  by  asking the hardware.  This is useful if your UPS con‐
37              stantly reports battery.charge values just below 100% even  when
38              it's completely charged.
39
40              If  you  have this problem, set this to whatever battery.voltage
41              reports when the UPS is known to be completely  charged  with  a
42              good battery.
43
44              The author's Best Fortress 750 uses nombattvolt=27.4.
45
46
47       ID=string
48
49              Set  the  Identification  response  string.  This should only be
50              used with hardware that supports the Phoenixtec protocol  status
51              inquiry  commands,  but  not  the  "ID"  command,  such  as  the
52              Best/SOLA    610.     Format    of    the    ID    string    is:
53              AAA,BBBB,CCC,DDD,EE.E,FF.F
54
55              AAA is the three-character identification for the UPS model.
56
57              BBBB  is  the output power in VA (volt amperes). B is an integer
58              number ranging from 0 to 9.
59
60              CCC is the Nominal Input Voltage. C is an integer number ranging
61              from 0 to 9. The unit is Volts AC.
62
63              DDD  is the Nominal Output Voltage. D is an integer number rang‐
64              ing from 0 to 9. The unit is Volts AC.
65
66              EE.E is the Battery Voltage that will  cause  the  UPS  to  shut
67              itself  off.   E  is an integer number ranging from 0 to 9. Then
68              unit is Volts DC and a decimal point is present.
69
70              FF.F or FFF.F is the Battery Voltage at full  charge.  F  is  an
71              integer number ranging from 0 to 9. Then unit is Volts DC. Typi‐
72              cally, for 700VA, 1KVA and 1.5KVA units, the format is FF.F. For
73              2KVA and 3KVA units, the format is FFF.F.
74
75              Example:   a   Best   610  1.5KVA  unit  would  use  the  string
76              "610,1500,120,120,10.0,48.0".
77
78

BUGS

80       The battery charge percentage value (in battery.charge) is derived from
81       the  voltage  data  that  the UPS returns, since the UPS doesn't return
82       that value directly.  On some hardware, the charge will remain at  100%
83       for  a long time and then drops quickly shortly before the battery runs
84       out.  You can confirm from the battery.voltage readings that this is  a
85       problem with the UPS and not this driver.
86
87       Similarly, the float from the charger in some models forces the battery
88       charge percentage back up to 100% immedately after the  UPS  goes  back
89       on‐line, so you can't tell when it is really recharged.
90
91       Finally,  some  models give one value for the battery's nominal voltage
92       and yet actually have a nominal  voltage  slightly  below  that.   This
93       leads  to  things  such  as  the perpetual 98.7% charge on the author's
94       Fortress 750, even when it's been charging for weeks.  You can use nom‐
95       battvolt= in ups.conf(8) to fix this.
96
97

AUTHOR

99       Russell Kroll, Jason White
100
101

SEE ALSO

103   The core driver:
104       nutupsdrv(8)
105
106
107   Internet resources:
108       The NUT (Network UPS Tools) home page: http://www.networkupstools.org/
109
110
111
112                                Wed Jul 28 2004                     BESTUPS(8)
Impressum